I will try this today and see if flow rate improves at all. Will post results shortly.You can do it with the pump running. Mandatory to open valve 8 all the way first. It shouldn’t technically matter the sequence of the other 2, but closing 9 first will stop flow through the heater before closing the outlet side. You won’t put un-necssary pressure on the heat exchanger vs closing 10 first which would allow pressurized water to get trapped in the heat exchanger. Always close and open the valves slowly.
Reverse the sequence when opening. Open 10, then 9, then tweak 8. Although depending on what happens to flow with the heater bypassed, valve positions may need to be tweaked to get the desired flow rate.
I adjusted valves as you said. Unfortunately, there was no increase in the flow rate with Valve 8 fully open and 9 and 10 closed, so I returned the valves to their original positions. Sounds like I can pretty much rule out any valves and lack of by pass for heater as the source of the low flow rate reading. That leaves me with the following potential issues causing the low reading at the flow meter:You can do it with the pump running. Mandatory to open valve 8 all the way first. It shouldn’t technically matter the sequence of the other 2, but closing 9 first will stop flow through the heater before closing the outlet side. You won’t put un-necssary pressure on the heat exchanger vs closing 10 first which would allow pressurized water to get trapped in the heat exchanger. Always close and open the valves slowly.
Reverse the sequence when opening. Open 10, then 9, then tweak 8. Although depending on what happens to flow with the heater bypassed, valve positions may need to be tweaked to get the desired flow rate.
Yep. I tapped on that gauge with the pump off and it dropped to 0. Was just stuck.That one is around 20 psi so I think it has an issue. Try tapping the dial with the pump off to see if the needle moves.
The concern I have is what does that actually mean? Is it hydraulically inefficient because it should be 4”, 6”, 8” in diameter?….. or because it has too many restrictive fittings….or because anything? They have not defined the actual root cause, which leaves you with a potential fix that could mean re-plumbing everything depending on the knowledge/expertise of the diagnostician….Call me pessimistic but their diagnosis/proposed solution leaves me feeling a bit queasy.Hydraulically Inefficent Plumbing (Remedy: Replace sections of plumbing that may be restricting flow.) (Recommended by pool company.)
The suction side reading has changed slightly (see below). How does this change the calculation of "head loss"? How do you calculate total head in feet from those two gauge readings? What gpm do these two measurements indicate now? Not sure if it matters, but remember... that suction side gauge does not go to zero when the pump is off because the gauge is about 2' above water level (see third pic below).The original pump PSI and suction in-hg you posted were 30 PSI and 9" HG respectively. This would indicate a total head loss of close to 80' of head. From the pump curve, flow rate is right at 180 GPM (DMJ curve). There may be an issue with your flow meter.
![]()
What has changed on the suction side? For the suction level to change, some valve or other thing has changed.The suction side reading has changed slightly (see below). How does this change the calculation of "head loss"?
Return Head Loss (ft) = Pressure (PSI) * 2.31 = 30 * 2.31 = 69.3'How do you calculate total head in feet from those two gauge readings? What gpm do these two measurements indicate now?
That is ok and due to the height of the gauge over water level. The pressure side reacts in the same way but in the opposite direction so counters the suction side and nets to zero.Not sure if it matters, but remember... that suction side gauge does not go to zero when the pump is off because the gauge is about 2' above water level (see third pic below).
It is usually stamped on the side of the impeller. Also, sometimes a clog in the impeller inlet or vane can also change the pump's head curve so it would have a different flow rate than what the pressure and suction would indicate. So while they have it apart and you confirm the part#, check the internal vanes for any clogs.We meet with the PC on June 3rd to discuss their proposed solution(s). All the information that you have all provided will be very helpful in that discussion. At this point it sounds like figuring out the discrepancy in the flow rate between the flow meter and what is indicated by those readings at the pump is key before anything else is done. I will definitely have them pull apart the pump and check the impeller. Since we did have that impeller replaced in the past two years, it's possible that the wrong size impeller was installed. How can I get the part number for the original impeller on our pump?
That is the correct one but make sure it was actually installed and clean of debris.Pentair Sta-Rite D Series Medium Head Impeller, 5 HP - C5-247 - INYOPools.com
C5-247 - IMPELLER, 5HP (C5-247)www.inyopools.com
Is this the right impeller for that Pentair Sta-Rite DMJ3-172 pump?
The only valves I have adjusted are those ones for the heater bypass, Valves 9 and 10 are completely open again, but Valve 8 may not be in the exact same position. Should I tweak that valve to see if I can get a slightly lower reading on that suction gauge... back to where it was?What has changed on the suction side? For the suction level to change, some valve or other thing has changed.
It didn't really change things much so I don't think that is the real issue. Confirm the impeller part# and condition.The only valves I have adjusted are those ones for the heater bypass, Valves 9 and 10 are completely open again, but Valve 8 may not be in the exact same position. Should I tweak that valve to see if I can get a slightly lower reading on that suction gauge... back to where it was?