hi guys, long time lurker, first time posting. Few questions on pump head and flow. i believe my pool is a bit over powered and want to swap impellers to slow the water flow, reduce the pressure/head overall and quiet the pump. when the motor gives up ill be looking into a VS but for now im tinkering with what i have.
thank you for sharing the pool pump spreadsheet! really great asset!
I have taken pressure readings right at the pump housing on the drain ports. Are these numbers enough to get an accurate GPM with out having to consider the specifics of the inline equipment and pipe runs/turns etc? i basically zeroed out the inputs on the psivac2gpm tab for pipe length/multiport etc.
Pool mode:
11 inhg- pump suction side
28 psi- pump pressure side
20 psi- filter gauge
77ft head
calculated plumbing curve 0.01067
spa mode:
14inhg- pump suction side
31psi- pump pressure side
25.5 psi- filter gauge
87ft head
calculated plumbing curve 0.04080
if i swap the impellers to a smaller hp unit from the sp3215ee or even sp3210ee, will the total plumbing curve remain the same?
is there anyway to calculate the % decrease in pressure/head/flow with these impellers?
not sure how much pump i really need with the spa/heater combo.
suction side is three separate intakes at 2inch each merging to one 2inch pipe in front of the pump. two skimmers and one floor drain
return side is three separate pipes at 2inch each, one feeds 5, 3/4inch eyeballs into the pool the other feeds 6, 3/4 inch eyeballs into the spa, last one feeds water fountain coming out of the spa but valve is nearly closed 99% of the time.
thank you for sharing the pool pump spreadsheet! really great asset!
I have taken pressure readings right at the pump housing on the drain ports. Are these numbers enough to get an accurate GPM with out having to consider the specifics of the inline equipment and pipe runs/turns etc? i basically zeroed out the inputs on the psivac2gpm tab for pipe length/multiport etc.
Pool mode:
11 inhg- pump suction side
28 psi- pump pressure side
20 psi- filter gauge
77ft head
calculated plumbing curve 0.01067
spa mode:
14inhg- pump suction side
31psi- pump pressure side
25.5 psi- filter gauge
87ft head
calculated plumbing curve 0.04080
if i swap the impellers to a smaller hp unit from the sp3215ee or even sp3210ee, will the total plumbing curve remain the same?
is there anyway to calculate the % decrease in pressure/head/flow with these impellers?
not sure how much pump i really need with the spa/heater combo.
suction side is three separate intakes at 2inch each merging to one 2inch pipe in front of the pump. two skimmers and one floor drain
return side is three separate pipes at 2inch each, one feeds 5, 3/4inch eyeballs into the pool the other feeds 6, 3/4 inch eyeballs into the spa, last one feeds water fountain coming out of the spa but valve is nearly closed 99% of the time.