Bonding rebar of any concrete within 3' of the water is very much required by the national code. Conceivably your local area changed the rules, but I very much doubt it.
Not in my local ones. I was in the orange store the other day and saw an orange vest advise a person that regular romex would be fine underground in conduit.They make clamps that bolts the bare bond wire to the rebar. Any one in the electrical depts of the home improvement stores will know what u need.
Your inspector should also.
My IG fiberglass pool w concrete reinforced deck by my city cpde required bonding and inspection prior to pouring. It all depends where u live
Sent from my SPH-L720 using Tapatalk
.....NEC codes are national and cities are supposed to enforce them....
I'm sure he knows what will be approved by the local inspector, but that is not the same as what the code actually says. The code clearly states that permitter surfaces within 3' of the pool must be bonded, regardless of pool type or construction. That is doubly true if they contain rebar, since a separate provision requires that all metal parts over 4" within 5' of the water must be bonded. So he is just dead wrong about that part, even if he knows how to get the local inspector to pass it. And completely apart from what the code says, unbounded concrete close to the water is just plain dangerous, as concrete conducts fairly well (it's not metal, but way more conductive than most dirt) and people are known to get shocks that way, as mentioned above.my electrician came out today to give me a bid on running power to our pool that is being built. He recommended #6 wire ran around the pool connected to all 8 of the metal supports for our pool and specifically said #8, while NEC code, is in his opinion not big enough. He said if the other supports were metal and not resin he would connect them all, not just at 4 points like I originally planned. Then a run to the lug on the pump, a water bond through the skimmer, and all tied to a ground rod driven 3 feet in near the pump station. He said bonding the rebar in the slab is not necessary on an AGP, even if buried, nor is it required by NEC. He stated that by the NEC, concrete / gunite ingrounds must have the concrete deck bonded as well due to the rebar in the pool itself and the fact that the pool deck and inground pool itself are often connected and are essentially one piece.
With a vinyl liner pool, it is not necessary unless there is rebared concrete under the liner or there is a metal or otherwise conductive ladder or step attached to both the pool and concrete deck combining the two. With our AGP we have no such conductive ladder or step. Ours is resin. He has been a licensed electrician for over 30 years and is recommended by our city code enforcement. I have used him on several other jobs and I trust his knowledge of his field. He also does many pools.
I'm sure he knows what will be approved by the local inspector, but that is not the same as what the code actually says. The code clearly states that permitter surfaces within 3' of the pool must be bonded, regardless of pool type or construction. That is doubly true if they contain rebar, since a separate provision requires that all metal parts over 4" within 5' of the water must be bonded. So he is just dead wrong about that part, even if he knows how to get the local inspector to pass it. And completely apart from what the code says, unbounded concrete close to the water is just plain dangerous, as concrete conducts fairly well (it's not metal, but way more conductive than most dirt) and people are known to get shocks that way, as mentioned above.
Yes, certainly dangerous. You can get a deadly shock from the concrete while touching both the concrete and the water unless the concrete is bonded. That is not to say that you will, but you could. And while deadly shocks are very very rare, annoying shocks are fairly common.
crazy. where does all this stray voltage come from...
crazy. where does all this stray voltage come from...
Now im baffled on all this.
My pool was bonded as follows.
1. #8 bare copper continuously around the pool about 15" out.
2. #8 bare copper attached to metal panel with copper connector 4 places on each side spaced equally and 2 on each end.
3. Wire attached to pool walls connects to the continuous loop.
4. Metal ladder is in brass cups (I think brass or copper, dont remember which). Cups are attached to bond loop and set in concrete.
5. Light niche outside connection attached to bond loop.
6. dry box above ground where light connects attached to bond loop.
7. Bond loop attached to pump and I think control panel box on outside.
8. Bond loop attached to zinc anode.
Bond is NOT attached to any rebar. I have no rebar in the concrete. I have a very thin layer of concrete with pavers overtop. Inspector had no issue with this. Is it because the ladder is in brass cups and the brass cups are attached to the bond loop? Inspector was quite happy I used the metal cups rather than the plastic.