- Sep 11, 2021
- 9
- Pool Size
- 17000
- Chlorine
- Salt Water Generator
- SWG Type
- Hayward Aqua Rite (T-15)
I installed a GVA-24 valve actuator to control a waterfall. It is plugged into an Omnihub. With power to the Omnihub, there does not appear to be any power to the actuator. Moving the switch to On1 or On 2 does nothing. I opened up the actuator and tested for 24VAC between black and red/white and got 0. Did this with the actuator manual switch in the OFF and On1 position.
Also tested the pins on the Omnihub connector and got 0. Assuming I should see 24VAC there but not sure.
Any thoughts on what to try next? The Omnihub and GVA-24 are both new but I suppose one or the other could be defective out of the box. Hopefully, I'm just doing something dumb that can be easily corrected.
Also tested the pins on the Omnihub connector and got 0. Assuming I should see 24VAC there but not sure.
Any thoughts on what to try next? The Omnihub and GVA-24 are both new but I suppose one or the other could be defective out of the box. Hopefully, I'm just doing something dumb that can be easily corrected.