The wiring connector contains 6 wires. The red wire connects to relay: 1 terminal: line 1 and relay: 2 terminal line 1, the green wire connects to relay 1 load 1, the yellow wire connects to relay 2 terminal load 1. The orange, brown and black wires won't be used.
It's not hard, we can walk you through it if you post pictures of your relays, or you could get someone to help wire it.
Your pump should be continuously powered. The pump has its own on board timers. You can set the timers in the pump, or you can activate external only mode.
If you have a SWG, you should run the pump from the automation so that the system will know whether or not to turn on the SWG (the flow switch will mostly work for this purpose, but it’s better to let the system control the pump).
“To activate External Control Only mode:
1. Stop the pump by pressing the Start/Stop button.
2. Activate External Control Only mode by pressing and holding the Start/Stop button for 3 seconds.
3. If successful the LED next to Ext. Control Only will illuminate. See Figure 6.
4. The Start/Stop button must be pressed again to allow the pump to run.”
To recap:
1) Get the wiring kit.
2) Take the pump power off of the relay and power directly from the breaker in the automation box.
3) Connect the wiring kit to the plug on the side of the motor.
4) Connect the wires from the wiring kit into the relays as described.
5) Activate External Control Only mode
6) Go to configuration in the AquaLogic and set as a two speed pump.
7) Set the timers for the pump speeds as you like.
8) Set speed 1 and 2 rpm as you like. Set from pump control panel.
9) Done