I have just hooked up my two hayward color logics to the intermatic 300 watt transformer and the second they flash on the gfi trips. Even when I disconnect the lights it still trips.
I read what is below on a different thread. Is it sake to just use a regular breaker?
Quote Originally Posted by ozark01 View Post
I was just reading 680.23 (8) and it looks like I don't need a GFCI breaker if the transformer is listed and the secondary is 15 volts or less. Is this the case?
Yes, that is what 680.23(A)(8) says.
I read what is below on a different thread. Is it sake to just use a regular breaker?
Quote Originally Posted by ozark01 View Post
I was just reading 680.23 (8) and it looks like I don't need a GFCI breaker if the transformer is listed and the secondary is 15 volts or less. Is this the case?
Yes, that is what 680.23(A)(8) says.