Wire Size
I suggest #10 wire at the minimum.
< 3% voltage drop at 14 amp draw from the motor.
#12 would give you a VD of around 5%
There is variables:
True RMS voltage, Actual amp draw from the motor nameplate and true length
Just my two cents.
If you pulled #12 would it work. Short answer yes.
If you pulled #10 would it work. Yes and be more efficient for the motor and possible the motor may last longer.
I suggest #10 wire at the minimum.
< 3% voltage drop at 14 amp draw from the motor.
#12 would give you a VD of around 5%
There is variables:
True RMS voltage, Actual amp draw from the motor nameplate and true length
Just my two cents.
If you pulled #12 would it work. Short answer yes.
If you pulled #10 would it work. Yes and be more efficient for the motor and possible the motor may last longer.