I have a Tristar VS (SP3200VSP) pump and Aqua-Plus control system. Since VSP model according to manual can't be connected via data cable, I'm trying to enable relay controls.
So current wiring is as follow.
230V supply connected directly to breaker as amendment to manual suggests.
Filter Relay connected to Port 1 of the pump's Digital input .
Aux-1 to Port 2
Aux-2 to Port 3
Com of the Digital Input connected to Com of the RS485 and +12V goes to all relays.
Pump's Dip Switches are 1,2 ON, 3,4,5 OFF.
So exactly as manual suggests.
Speeds configured and Pump set to Relay Control.
When I'm trying to set Aqua-Plus to Variable Speed Pump I get "VSP Comm Error" and only other settings I have are 1 and 2 speed, that does not seem to be correct settings for my case.
Any suggestions what I've missed?
Also, is it possible to completely disconnect pumps control panel and connect via data cable to automation system?
Thanks in advance.
So current wiring is as follow.
230V supply connected directly to breaker as amendment to manual suggests.
Filter Relay connected to Port 1 of the pump's Digital input .
Aux-1 to Port 2
Aux-2 to Port 3
Com of the Digital Input connected to Com of the RS485 and +12V goes to all relays.
Pump's Dip Switches are 1,2 ON, 3,4,5 OFF.
So exactly as manual suggests.
Speeds configured and Pump set to Relay Control.
When I'm trying to set Aqua-Plus to Variable Speed Pump I get "VSP Comm Error" and only other settings I have are 1 and 2 speed, that does not seem to be correct settings for my case.
Any suggestions what I've missed?
Also, is it possible to completely disconnect pumps control panel and connect via data cable to automation system?
Thanks in advance.