I can't get my spa to heat up above "lukewarm" -- maybe 88 degrees. I have a Pentair MasterTemp 250 heater, ~4 years old, worked fine for years. Now, it reads ~15 degrees hotter on the inflow water temp than the water actually is. For example, when I turn it on, and the spa water temp is actually ~60 degrees, the Pentair LCD screen says 75 degrees. It then proceeds to fire normally and heat the water up to the spa temp setting of 100 deg (or the 104 max), but the actual water temp reached and stabilized is ~85-~88 degrees and it won't get any hotter.
I thought it was a bad thermocouple/thermister (part 42001-0053S) -- but I replaced it with a new one, testing the resistance on both, and both are in spec and read the Ohms for a temperature that 15 degrees lower than what the LCD screen shows (used this table: File:10K thermistor chart.png - Further Reading )
The Control board show no errors. Anyone have any ideas on what is going on or how to fix? Thanks
I thought it was a bad thermocouple/thermister (part 42001-0053S) -- but I replaced it with a new one, testing the resistance on both, and both are in spec and read the Ohms for a temperature that 15 degrees lower than what the LCD screen shows (used this table: File:10K thermistor chart.png - Further Reading )
The Control board show no errors. Anyone have any ideas on what is going on or how to fix? Thanks