- Jul 2, 2023
- 110
- Pool Size
- 14500
- Surface
- Plaster
- Chlorine
- Salt Water Generator
- SWG Type
- Jandy Aquapure 1400
At 2750 RPM, in Pool Heat Mode, heater bypass closed, Spaool Makeup off the spa:Check the heater inlet temperature and compare it to the outlet temperature to see what the temperature rise is.
The SWG temperature is the heater outlet temperature.
The Temperature rise is Outlet - Inlet = Temp. Rise, which should be 16.8 degrees or less.
You can use this formula to estimate the flow based on the temperature rise.
Y = temperature rise.
X = flow in gpm.
Y = 672/X
X = 672/Y.
For example a flow of 40 gpm should be a temperature rise of 16.8 degrees.
A temperature rise of 11.2 degrees should be about 60 GPM.
As you can see, flow below 40 gpm results in a big temperature rise.
If the water temperature is 86 degrees and water boils at 212°F, then a temp rise of 126 degrees will result in boiling of the water and the heater will probably explode or be seriously permanently damaged.
A flow of 5.3 GPM or less will likely cause the water to boil and seriously damage the heater.
plot Y = 672/X, y from 6 to 60 - Wolfram|Alpha
Wolfram|Alpha brings expert-level knowledge and capabilities to the broadest possible range of people—spanning all professions and education levels.www.wolframalpha.com
plot Y = 672/X, y from 6 to 150 - Wolfram|Alpha
Wolfram|Alpha brings expert-level knowledge and capabilities to the broadest possible range of people—spanning all professions and education levels.www.wolframalpha.com
Inlet temperature 77 degrees
Outlet temperature into pool 88 degrees
Thanks.
Jim