Hi,
I'm using a Pentair SolarTouch controller with my IntelloFlo VSF pump. I notice that my controller falls back to solar hold after just a few minutes, because it picks up a sudden drop in "solar temp" (roof temp).
As a result, my valve opens and closes multiple times over the span of a few minutes, my pump spends most of the time in solar hold (ext4) with the valve closed, and I'm using a fraction of my roof solar capacity.
Some details:
My initial hypothesis was: cold pool water goes up to the roof and cools down the sensor too much. Hence I changed the Diff to start (increased to 4C) and Diff to stop times (decreased to 1C).
I started monitoring the Solar/roof temp on the controller. Typical sequence:
Could this be a faulty sensor or a bad contact? (since the measured 15C is even lower than my pool temp this seems like an anomaly)
My temp sensor on the roof is at the top/cold side of the first panel, this seems counter intuitive to me. Shouldn't it be at the bottom/hot side of the panels?
I would welcome any suggestions (including corrections to my understanding of how the system works)
Side question: what's the point of solar hold for 5 minutes, especially if there is no separate solar booster pump to prime?
I'm using a Pentair SolarTouch controller with my IntelloFlo VSF pump. I notice that my controller falls back to solar hold after just a few minutes, because it picks up a sudden drop in "solar temp" (roof temp).
As a result, my valve opens and closes multiple times over the span of a few minutes, my pump spends most of the time in solar hold (ext4) with the valve closed, and I'm using a fraction of my roof solar capacity.
Some details:
- pool
- current temp: 18C
- solar touch settings:
- target temp: 31C
- diff to start: 4C (=22C)
- diff to stop: 1C (= 19C)
My initial hypothesis was: cold pool water goes up to the roof and cools down the sensor too much. Hence I changed the Diff to start (increased to 4C) and Diff to stop times (decreased to 1C).
I started monitoring the Solar/roof temp on the controller. Typical sequence:
- start roof temp: 25C
- starting solartouch with Solar Heating Enabled
- start solar hold (since 25 > 31-4)
- 5 min hold (pump in ext 4, solar valve closed, expected)
- solar heating enabled (pump in ext2, solar valve enabled, expected)
- roof solar temp drops a few degrees (21-22C still above Diff to stop, expected)
- after a few minutes roof solar temp drops suddenly to 15C for a few seconds, triggering solar hold (for 5 minutes)
- repeat
Could this be a faulty sensor or a bad contact? (since the measured 15C is even lower than my pool temp this seems like an anomaly)
My temp sensor on the roof is at the top/cold side of the first panel, this seems counter intuitive to me. Shouldn't it be at the bottom/hot side of the panels?
I would welcome any suggestions (including corrections to my understanding of how the system works)
Side question: what's the point of solar hold for 5 minutes, especially if there is no separate solar booster pump to prime?