So I'm gearing up to finish this pool install I started last fall. The pool and equipment pad are in, now to install the electrical and equipment.
I'm doing the work myself and just wanted to get feeback on if anything I'm doing is not to Ontario code. I've already applied for my ESA inspection as well.
Some background:
Main service is 200A. The panel is full so the previous owners ran a secondary 125 service to a small 4 port Square D panel. Good thing is they did it legit with 2/3 wire from the main panel.
What I'm looking to do is replacing the Square D sub panel with some other panel (Siemens?) with 125A main and a spot for a 60A sub service. The 60A sub will be run 110 ft with 6/3 NMWU wire through 1.25" PVC conduit buried 3 ft deep. This line will be run to the equipment pad and connected to a Hayward Omnilogic that will control the usual equipment (heater, pump, ect..) along with other things like Cabana/landscape lighting, receptacles in the cabana, ect.
I'm sure I could be okay with only running 40A out but I'd like 60 for future growth. Never know.
Any feedback would be helpful. Again, I live in Ontario so i'm looking on feedback on the Ontario code. Thanks!
I'm doing the work myself and just wanted to get feeback on if anything I'm doing is not to Ontario code. I've already applied for my ESA inspection as well.
Some background:
Main service is 200A. The panel is full so the previous owners ran a secondary 125 service to a small 4 port Square D panel. Good thing is they did it legit with 2/3 wire from the main panel.
What I'm looking to do is replacing the Square D sub panel with some other panel (Siemens?) with 125A main and a spot for a 60A sub service. The 60A sub will be run 110 ft with 6/3 NMWU wire through 1.25" PVC conduit buried 3 ft deep. This line will be run to the equipment pad and connected to a Hayward Omnilogic that will control the usual equipment (heater, pump, ect..) along with other things like Cabana/landscape lighting, receptacles in the cabana, ect.
I'm sure I could be okay with only running 40A out but I'd like 60 for future growth. Never know.
Any feedback would be helpful. Again, I live in Ontario so i'm looking on feedback on the Ontario code. Thanks!