Hi Guys, Newby Here. This is my problem. I have a Jandy Model #LXI25N that the access door blow open during a bad wind and rainstorm. the pool pump was on so when I went outside to shut the pump down I noticed the PIB board had shorted out. This was last fall and I have waited until now to repair the damage. when I assessed the damage I also found the PDB board was destroyed also. I ordered both parts and installed them. With my downloaded troubleshooting Guide I checked my voltage all the way to the Black wire (L) on the PDB.... 110 volts. Everything is good but still no fan and (CHECK IGN CONTROL) error is still coming up. I am testing with the pump on and heater request on. I pulled the fan motor and it looks brand new. No visible signs or smell of damage. (Heater is less than 2 years old very clean inside, and little usage)
Here is what have i have tried so far. As my post indicates...almost everything including voltage to and from transformer, air pressure switch, water pressure switch, high limits ETC, but these are all startup stages that come after FAN START right? I have also pulled the wires going to the igniter and it tested 72.4 ohms. Also I safely discharged the capacitor on the motor and on the ohm meter it spiked up high and slowly went to “o” how do I bench test the motor? 5 wires are confusing. I do know the system is 220 volts ac
Here is what have i have tried so far. As my post indicates...almost everything including voltage to and from transformer, air pressure switch, water pressure switch, high limits ETC, but these are all startup stages that come after FAN START right? I have also pulled the wires going to the igniter and it tested 72.4 ohms. Also I safely discharged the capacitor on the motor and on the ohm meter it spiked up high and slowly went to “o” how do I bench test the motor? 5 wires are confusing. I do know the system is 220 volts ac