I installed a new EcoStar VSP pump this yesterday and the Goldline controls are not starting the pump. I followed the instructions connecting #7 on pump to #2 on PCB and #8 on pump to #3 on PCB. When you press the Filter button on the Goldline controls, you can hear the relay engage but the filter doesn't start. All other aspects of the controls work properly (valve rotating between pool & spa, lights, etc..).
I used the configuration menu to indicate a variable speed pump, set the pump output % and set the timers. Still nothing when the filter button is replaced. I connected the Hayward control panel (provided with pump) and the pump operates perfectly. Primes, turns on, off, runs at desired speed. Given the pump is working fine, I'm fairly sure I have a communication issue between the Goldline and the new pump.
I do have a message displayed "Check System Pool Bridge Comm" which I haven't figured out yet. Any guidance or help would be appreciated.
SP3200SR / SP3400VSP
Main SW 2.87
Display SW r2.00 S:40
RF Base Software r1.2 ID:5931
I used the configuration menu to indicate a variable speed pump, set the pump output % and set the timers. Still nothing when the filter button is replaced. I connected the Hayward control panel (provided with pump) and the pump operates perfectly. Primes, turns on, off, runs at desired speed. Given the pump is working fine, I'm fairly sure I have a communication issue between the Goldline and the new pump.