GFCI tripping

Jun 3, 2013
78
Have a Swim Spa and the GFCI trips immediately. Went one by one and disconnected components. Culprit is the heater but I replaced this element April of 2023 and never had issues. Tested continuity-GOOD, Testing Resistance-NORMAL RANGE. No corrosion on posts etc. Any other ideas why the heater is tripping the GFI?
Thanks,
 
Did you test continuity to ground?

Turn off the breaker to the spa and test resistance (ohms) from the terminal to ground.

Do not do anything you are not 100% sure you can do safely.
 
Did you test continuity to ground?

Turn off the breaker to the spa and test resistance (ohms) from the terminal to ground.

Do not do anything you are not 100% sure you can do safely.
Just tested from the heater posts to the ground. NO Continuity. If I test the ground to the outside of the heater tube, there is continuity. When testing resistance to ground, the numbers start at 8 and keep climbing to 30+
 
Last edited:
Just tested from the heater posts to the ground. NO Continuity. If I test the ground to the outside of the heater tube, there is continuity. When testing resistance to ground, the numbers start at 8 and keep climbing to 30+
The tube will have continuity to ground.

If the gfci only trips when the heater is connected, it probably means that the element is bad.

You can remove the element to look for damage like a crack in the insulation.
 
A regular ohmmeter will be limited to a certain range of ohms that it can actually measure.

If the resistance is above a specific amount, you will get O.L which means Over Limit or Open Line.

Did the meter show O.L?

A megometer can test resistance levels that are much higher than a regular ohmmeter can do.

In any case, the easiest thing to do is replace the element.
 

Enjoying this content?

Support TFP with a donation.

Give Support
Maybe a bad element, but that should only trip during call for heat.

Maybe a stuck relay.

Maybe the element is always getting power due to a stuck relay?

Possibly a stuck relay and a bad element.

Does the element get power when no call for heat?
 
Maybe a bad element, but that should only trip during call for heat.

Maybe a stuck relay.

Maybe the element is always getting power due to a stuck relay?

Possibly a stuck relay and a bad element.

Does the element get power when no call for heat?
thats a really good point. Any idea how to ID the relay for This unit? Its a Balboa VSS.
 