I know this question is better suited for an electrician's forum but I'm not a member to any of those, and it is regarding my pool light job I will be undertaking.
It is my understanding that you cannot run Romex in conduit; but you can run THHN wire in conduit. It is also my understanding that Romex is THHN wire just wrapped in the heavy jacket. I happen to have some 12/3 Romex laying around. Can I remove the individual wires from the heavy jacket and run the individual wires in conduit and stay within code? I only need a 2 or 3 foot run.

Thanks..
 
The conduit inside or outside?

For outside you need to use THWN or dual rated THHN/THWN wire in conduit.
 
  • Like
Reactions: proavia
Typically romex is solid wire. You would use stranded wire in conduit.
 
The home centers will sell you any length you need. Use the correct wire. If there was ever a problem, or worse, your insurance company will look for any way not to pay the claim....
 