Trouble shoot: Pump trips breaker ONLY the first time it runs each day ( Omnilogic )

citznfish

Active member
Sep 17, 2007
35
805 area code
Hello,

I am having a strange problem and I am hoping I can get some advice.

pool is only 4 years okd. Pool equipment is running through Hayward OmniLogic and the pumps have their own 20amp breakers, one for each.

Every morning the pool pump kicks on, I can hear the relay click. The filter pump doesn't start, there is a hum, and then the breaker trips (I can watch the breaker trip each morning). In Omnilogic, the program still shows the pump running but then the flowsensor error appears because in reality the pump never started. I can turn the pump off in the software, walk over to the breaker and reset it, then start the pump again in Omnilogic and it works flawlessly, until it has to start again the next morning. What could cause this? ( no water is leaking back into the pool when the pump is off)

Here is what I tried:
  • Switching the 20amp breaker for a known working one - no change in condition.
  • Checking all the wires in the Omnilogic service box.

Thoughts:
  • I don't think it can be a bad relay since it will immediately start up after I reset the breaker.
  • I don't think it can be a bad pump since the pump runs correctly the second time I try to start it via Omnilogic, after resetting the breaker

I am stumped and would love some insight.

Thank you,
CF

attachment.php
 

Attachments

  • poolissues.jpg
    poolissues.jpg
    58.8 KB · Views: 63

JamesW

TFP Expert
Mar 2, 2011
25,894
Maybe the capacitor or a sticking shaft.

If the shaft turns freely, try replacing the capacitor.

What pump do you have?
 

ajw22

Gold Supporter
TFP Guide
Jul 21, 2013
26,454
Northern NJ
Pool Size
35000
Surface
Plaster
Chlorine
Salt Water Generator
SWG Type
Pentair Intellichlor IC-60
My guess would be a weak start capacitor.
 

tstex

Silver Supporter
Aug 28, 2012
1,903
Houston, TX
Maybe the capacitor or a sticking shaft.

If the shaft turns freely, try replacing the capacitor.

What pump do you have?

Yes, what type of pumps do you have? That would be a great addition to your signature.

What this sounds like is problem w the controller and something is causing the start up from the controller to short-out the connections to the pump.

When did this start happening? Do you have surge protectors in your house or pool panel, esp if you have a VSP.

Since you do not list where you live, what has the weather been like? If L-Vegas NV or San Diego, then no lightening, but the Midwest, S & SW is a different
 

citznfish

Active member
Sep 17, 2007
35
805 area code
Maybe the capacitor or a sticking shaft.

If the shaft turns freely, try replacing the capacitor.

What pump do you have?




Yes, what type of pumps do you have? That would be a great addition to your signature.

What this sounds like is problem w the controller and something is causing the start up from the controller to short-out the connections to the pump.

When did this start happening? Do you have surge protectors in your house or pool panel, esp if you have a VSP.

Since you do not list where you live, what has the weather been like? If L-Vegas NV or San Diego, then no lightening, but the Midwest, S & SW is a different


I live in SoCal so the weather has been nice. The issue started about 2weeks ago. Here is my VSP information:
attachment.php
 

Attachments

  • 20181215_092721.jpg
    20181215_092721.jpg
    87.9 KB · Views: 51

JamesW

TFP Expert
Mar 2, 2011
25,894
It's a two speed pump. Try a new capacitor.

It's under the bump on top.

Note: Your pump is a SP32202EE Hayward TriStar 2 hp two-speed pump.
 

tstex

Silver Supporter
Aug 28, 2012
1,903
Houston, TX
It's a two speed pump. Try a new capacitor.

It's under the bump on top.

Note: Your pump is a SP32202EE Hayward TriStar 2 hp two-speed pump.

Thanks James - how old is this pump? It's certainly not lightening or storm related in SoCal.
 

JamesW

TFP Expert
Mar 2, 2011
25,894
As of August 2006 a common date code format for all motors is being used. It consists of seven alpha-numeric characters. The first three characters represent the day of the year based on the Julian calendar, the next two the year, and the last two the plant code. For example, 123064M, would mean the 123rd day of 2006 (May 3, 2006) in Regal’s Juarez IGMEX4 plant.
Users and distributors may visit our website centuryelectricmotor.com to access our ‘date code converter,” as well as applicable warranty forms.

https://www.centuryelectricmotor.com/WarrantyServices.aspx

Motor serial number 03114J2 was made January 31 2014.

The pump also has a serial number to indicate when it was made.

Starting May 1, 2010 and Forward

The first two numbers (21) are common to all ID tags.

The 3rd - 4th number is the plant
of manufacture.
10 = Canada. 11 = Pomona, CA.
12 = Clemmons, NC.
13 = Nashville, TN

The 5th -6th number will be the year & the 7th - 8th is the month.

The pump was probably made within a few months after the motor and installed within about 8 months typically.

So, I would suspect that the pump was probably installed mid to late 2014 or early 2015.
 

tstex

Silver Supporter
Aug 28, 2012
1,903
Houston, TX
fairly new 2-speed in the scheme of things...might call Hayward and join the warranty bandwagon...I believe a capacitor install is worth the try...
 

citznfish

Active member
Sep 17, 2007
35
805 area code
Thank you all for your help, I'll try a new capacitor.

fairly new 2-speed in the scheme of things...might call Hayward and join the warranty bandwagon...I believe a capacitor install is worth the try...

There is a warrant issue for these pumps? I wasn't aware. So this seems to be a common issue?
 

Enjoying this content?

Support TFP with a donation.

Give Support

JamesW

TFP Expert
Mar 2, 2011
25,894
I think that it's probably just a bad capacitor. It's an easy fix. Capacitors are generally considered "consumable" and not a warranty item.

The pump is out of warranty. The issue is not an issue specific to Hayward.
 

citznfish

Active member
Sep 17, 2007
35
805 area code
I think that it's probably just a bad capacitor. It's an easy fix. Capacitors are generally considered "consumable" and not a warranty item.

The pump is out of warranty. The issue is not an issue specific to Hayward.

Thanks for the clarification. Ordering the cap now
 