Pentair Superflo VS will only run in service mode

BRob49

New member
Jul 20, 2022
1
San Diego
Hello - I recently upgrade my control panel to the Intellicenter Control System with Screen Logic. Now the only way I can get my filter pump (Superflo VS) to run is when I put the system in service mode and then manually run it from the pump panel. My (2) older single speed pumps (WhisperFlo) work just fine through the panel. Is it a set up issue within screen logic?? Thanks in advance!
 
Rob,

Do you have your SuperFlo VS connected to the RS-485 port in the IntelliCenter? What does the pump's display show when the IntelliCenter is in AUTO?

How old is your pump, only the ones made in the last couple of years have RS-485 control. Show us a pic of the S/N label.

For a pump to run from the IntelliCenter several things have to happen.

1. The pump must be controlled by the automation
2. A circuit that needs the pump to run must be on.
3. A pump speed must be assigned to that circuit.

Thanks,

Jim R.
 