If anything, excessive flow will cause mechanical erosion of the copper.
Copper pipe is usually limited to 6 or 8 feet per second.
The heat exchanger has 6 tubes but it is a double pass system, so it is 4 and 2 or 3 and 3.
The tubes look like about 1/2" or 3/4" diameter pipe.
So, you probably do not want more than about 40 gpm max going through the heat exchanger.
The heater has an internal bypass, so not all of the water goes through the heat exchanger anyway.
The Pool & Hot Tub Alliance advances the common interests of the industry by providing education, industry leadership, legislative and regulatory advocacy, standards development, research and market growth to increase our members' professionalism, knowledge and profitability.
issuu.com
This Standard provides recommended minimum guidelines for the design, equipment, operation, and installation of new construction and renovation of public pools for builders, installers, and pool opera
issuu.com
issuu.com
The ANSI/APSP/ICC-11 2019 American National Standard for Water Quality in Public Pools and Spas provides recommended minimum guidelines for the specifications for recreational water quality parameters in public pools and spas. An Appendix A includes explanatory sections about the values for the...
issuu.com
Once inside the heater some of the water is by-passed.
Heaters are designed to operate at a predetermined flow rate, normally not exceeding 100 GPM. Any excess flow is diverted to the outlet side of the heater.
The bypass valve is a spring loaded valve that opens when the pressure indicates that there is too much flow.
The water now enters the heat exchanger.
The heat exchanger is a series of copper finned tubes that absorb the heat from the combustion chamber and transfer it to the water.
After passing through the heat exchanger, the water exits the heater and returns to the pool or spa. (Figure 3)
Water flow and pressure loss <i>(psi/ft)</i> due to friction in copper tubes ASTM B88 Types K, L and M.