Good day, been working in industrial automation for the last decade and regularly work with 480v to 110v stuff. I understand all about the bonding the electrical. My question is that i see a lot of people running a trench from the house to a 4x4 and plugging the pool into a disconnect with GFCI there. I have consulted the NEC and I cant determine if can just wire the motor directly thru the trench with underground rated conduit to a disconnect and GFCI outlet I already have on my house. with out having an unsightly 4x4 in the yard.

Thoughts?

Thanks
 

ajw22

Gold Supporter
TFP Guide
Jul 21, 2013
29,066
Northern NJ
Pool Size
35000
Surface
Plaster
Chlorine
Salt Water Generator
SWG Type
Pentair Intellichlor IC-60
I have consulted the NEC and I cant determine if can just wire the motor directly thru the trench with underground rated conduit to a disconnect and GFCI outlet I already have on my house. with out having an unsightly 4x4 in the yard.

Thoughts?

See 680.21(A)(3) - Pool motors shall be permitted to employ cord and plug connections. The flexible cord shall not exceed 3 feet in length.

You can trench to connect the motor directly to a GFCI CB in the house.

However connecting to a GFCI outlet in the house would give you a cord over 3' and not conform to 680.21(A)(3)
 
  • Like
Reactions: Mdragger88

Mentat

New member
Mar 12, 2021
3
Mtusker1234
See 680.21(A)(3) - Pool motors shall be permitted to employ cord and plug connections. The flexible cord shall not exceed 3 feet in length.

You can trench to connect the motor directly to a GFCI CB in the house.

However connecting to a GFCI outlet in the house would give you a cord over 3' and not conform to 680.21(A)(3)
what if the breaker has built in GFCI?
 

Mentat

New member
Mar 12, 2021
3
Mtusker1234
Never mind i can trench directly to breaker if so desired, only need to worry about the plug if I intended to use an actual plug. right? and it cant be over 3 ft. gotcha
 

ajw22

Gold Supporter
TFP Guide
Jul 21, 2013
29,066
Northern NJ
Pool Size
35000
Surface
Plaster
Chlorine
Salt Water Generator
SWG Type
Pentair Intellichlor IC-60
Note that 680.22 requires at least one 15A or 20A, 125V receptacle must be located not less than 6 ft and not more than 20 ft from the inside wall of a permanently installed pool. This receptacle must be located not more than 6½ ft above the floor, platform, or grade level serving the permanently installed pool.

So NEC requires you to put some electrical service near the pool.
 

magiteck

Gold Supporter
May 20, 2020
580
Neenah, Wisconsin
Pool Size
13600
Surface
Vinyl
Chlorine
Liquid Chlorine
In addition to the pump itself, I was required to have a separate 120v “accessory” outlet within something like 20 feet of the pool.

If you direct wire the pump, just make sure you’ve got any other requirements like this accounted for.

In my case I had nothing, so I just installed both the pump outlet and accessory outlet on a 4x6 post.
 
  • Like
Reactions: Mdragger88

Mdragger88

Bronze Supporter
Jun 1, 2018
3,138
Hernando, Ms
Pool Size
26000
Surface
Vinyl
Chlorine
Salt Water Generator
SWG Type
Intex Krystal Clear
The idea is that you need a disconnecting means within reach of the pool equipment for safety reasons - a gfci breaker inside your house (while a good addition) would not fully serve this purpose. If u are concerned about looks use the opportunity to build a small shelter or wall for your pool equipment pad since the equipment will already be visible in the yard. There are lots of threads here of examples.
 