    Basic Electric Hookups for AGP

    I am looking for info on basic electric hookups for AGP. I will be having an electrician do the work, but I want to be able to do some basic planning before I meet with the electrician. I will have a 2 speed pump. The manual states it needs a 15 amp circuit, but does not state whether the pump needs its own circuit. I will have a Goldline control unit for a valve on the solar panels. I also want to have some outlets around the pool deck and adjacent patio. My initial thought is I would have a 20 amp circuit for the pump (in case I need to upgrade in future) and a separate 15 amp circuit for lights and outlets around the pool and adjacent patio. I need a pump timer also. I believe I need a subpanel at the pool location with power cut-offs, which I assume will be breakers in the subpanel.

    Is there any where on this site or any other sources you can point me to that have general info on how a pool and related accessories get wired?

    (PS, I like the larger font on the draft message box - easier to read - less typoss)
    27' AGP with 6' deep end (AquaLeader); 3/4 hp, 2 speed pump (Pentair); 22" sand filter (Pentair Sand Dollar); 2 4x20 Solar Bear panels with Goldline control valve

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,887

    Re: Basic Electric Hookups for AGP

    It is very nice to get a sub-panel installed and run individual circuits from there, though there are other ways to do it. Intermatic makes some timers that come in an enclosure that includes a sub-panel.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3
    frustratedpoolmom's Avatar
    Join Date
    May 2007
    Location
    SWSuburban Chicago, IL
    Posts
    11,963

    Re: Basic Electric Hookups for AGP

    We were told that our 2hp pump needed its own dedicated circuit. And so it does. 8)
    Helpful links: Pool School; CYA/Chlorine Chart
    24' round AG pool, 52" high, Raypak heater; Waterway 2 spd Pump;
    150 Sq ft. Clearwater Cartridge Filter; Former and DISSATISFIED "Pool Frog" owner
    http://www.PerfectlyClearPoolService.com

  4. Back To Top    #4

    Join Date
    Jun 2007
    Location
    SF Bay Area
    Posts
    441

    Re: Basic Electric Hookups for AGP

    frustratedpoolmom,

    We were told that our 2hp pump needed its own dedicated circuit. And so it does.
    A 2 HP inground pump only draws around 10-11 amps at 240 Volts (230 Volts and 220 Volts are the same thing). A typical pool sub-panel is usually fed with a minimum #10 gauge wire which is rated for 30 Amps. This type of system would have absolutely no problem (assuming normal voltage at the main panel and no abnormally long wire runs) running a 2 HP filter pump, in addition to a cleaner booster pump and pool lights.

    The only time that a 2 HP pool pump might need a dedicated circuit is if it was being fed at 120 Volts. And a pump this large really should be run at 240 Volts ; not because it is any more efficient at 240 Volts than at 120 Volts, but rather because a pump run at 240 Volts will use less of the limited current capacity (ampacity) of the wire than the same size pump run at 120 Volts.

    Titanium
    24,000 gallon inground freeform pool/spa circa 1983 (113 ft perimeter, 625 sq ft) with 350 gallon attached spill-over spa
    2007 2 HP, three-phase Hayward TriStar pump which is powered by an Ikeric VS-200 variable speed drive system
    1983 Laars XE Pool/Spa Heater Type ES 400,000 BTU, 1998 Hayward Super Star-Clear C-4000 cartridge filter (400 sq ft, 4 separate cartridges)
    1998 Polaris 380 pressure-side cleaner w/ 3/4 HP booster pump
    One skimmer :( and one PoolSkim :), One Supervision Galaxy LED pool lamp, Second story solar panels
    Hayward/GoldLine AquaLogic PS4 (replaced 1983 vintage dual circuit Intermatic timer)

  5. Back To Top    #5
    frustratedpoolmom's Avatar
    Join Date
    May 2007
    Location
    SWSuburban Chicago, IL
    Posts
    11,963

    Re: Basic Electric Hookups for AGP

    Quote Originally Posted by Titanium
    frustratedpoolmom,

    We were told that our 2hp pump needed its own dedicated circuit. And so it does.
    A 2 HP inground pump only draws around 10-11 amps at 240 Volts (230 Volts and 220 Volts are the same thing). A typical pool sub-panel is usually fed with a minimum #10 gauge wire which is rated for 30 Amps. This type of system would have absolutely no problem (assuming normal voltage at the main panel and no abnormally long wire runs) running a 2 HP filter pump, in addition to a cleaner booster pump and pool lights.

    The only time that a 2 HP pool pump might need a dedicated circuit is if it was being fed at 120 Volts. And a pump this large really should be run at 240 Volts ; not because it is any more efficient at 240 Volts than at 120 Volts, but rather because a pump run at 240 Volts will use less of the limited current capacity (ampacity) of the wire than the same size pump run at 120 Volts.

    Titanium
    That's facsinating. I was completely lost after "A 2hp pump only draws".... Are you an electrician? Can you come over and ground/bond my pool? Just confirmed last night that its not.
    Helpful links: Pool School; CYA/Chlorine Chart
    24' round AG pool, 52" high, Raypak heater; Waterway 2 spd Pump;
    150 Sq ft. Clearwater Cartridge Filter; Former and DISSATISFIED "Pool Frog" owner
    http://www.PerfectlyClearPoolService.com

  6. Back To Top    #6
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,887

    Re: Basic Electric Hookups for AGP

    We don't tend to go into any more detail on how to setup electrical stuff than bobnamy already has because the code gets rather convoluted. For example there is no such thing as a "dedicated" circuit in the code, but various rules in the code often result in what you or I would call a dedicated circuit. You almost always need a professional electrician to figure out all the details, which often revolve around critical safety issues and are important to get right.

    You nearly always want to place a sub-panel in the general pool area and run a minimum of two breakers/circuits from there, one for the pump and one for a utility outlet. It is very nice to have enough capacity for additional circuits beyond that, as there are always more things that you think of adding later, more lights, more outlets. Underwater lights also need their own breaker. The cost of putting in wire suitable for a 100 amp sub-panel is not much more than the cost of wiring a sub-panel in the first place, and having the extra capacity almost always comes in handy at some point.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  7. Back To Top    #7

    Join Date
    Jul 2007
    Location
    New Hudson, MI
    Posts
    48

    Re: Basic Electric Hookups for AGP

    Check out this site if you want to educate yourself a bit before meeting with the electrician:
    http://www.selfhelpandmore.com/home-wiring-usa/

    Note that this link applies to the 2002 version of the code. In 2005, the NEC significantly changed its requirements for pool bonding, both above ground and in-ground. Most everything else related to a pool though remained unchanged. You might want to contact your electrical inspector while in the planning stages to get his/her thoughts on how the pool bonding will be inspected. The 2005 NEC has much more stringent bonding requirements than most AG pools have employed. As time goes on, these rules will become both better understood, and therefore enforced more uniformly.

    I agree with Jason - after all the rules are applied, you generally are forced into a dedicated circuit for your pump motor. My memory says this is more or less explicit in the pool rules of the NEC. And your electrician may suggest that you oversize your wiring to reduce voltage drop to the pump if you have a long run of wire. Trust him to provide good advice on that, or specifically ask him to calculate your resistance voltage drop for you as a percentage. Keep in mind that this percentage is essentially the percentage of electricity you are paying for that is used for heating your wires rather than powering your pump motor (i.e., it's wasted electrical power).

    And while subpanels are nice, going bigger will cost more, so you shouldn't leave yourself too much extra room if you can't afford it.

    I would suggest you consider going with only 20A circuits, even for general purpose/outlet circuits. You essentially get another third of a circuit with the cost difference being quite small.

    The most cost effective way of wiring a modest AG pool with a 120V pump motor, in my opinion, is to run 2 20A circuits from your main breaker panel into a new box located near the main breaker panel. This box will hold two non-outlet GFI devices which will protect both circuits downstream of that point. Run one of these circuits to your pump motor using 12 or 10 AWG from the GFI output to the motor access point (twist lock receptacle??). Your timer can plug into this receptacle, then your pump motor into that timer. The other circuit provides general purpose service to the pool vicinity, and can in fact go to multiple outlets if you'd like that convenience. Alternatively, you can buy more expensive GFI breakers and eliminate the GFI devices and the stand-alone box near your main breaker panel. GFI breakers are typically pricey, but perhaps they've come down in price over the years???

    The link above is good reading, if you're so inclined, and a brief chat with your inspector during the planning stage cannot hurt either.

    Good luck!
    Scott

    27'x52" AG Vogue Impact, Waterway Cyclone 200 cartridge filter, Waterway pump w/2 HP 2-sp motor, 8mil solar cover, Raypak 206 nat gas heater, Pool Rover Jr.

  8. Back To Top    #8

    Join Date
    May 2008
    Location
    rock springs, wi
    Posts
    45

    Re: Basic Electric Hookups for AGP

    Thanks ssabin, that is exactly what I was looking for.