    Raypak Gas Heater problem

    I have a 400,000 BTU Raypak digital heater with a 2hp pump , both going to a 220v Intermac manual timer (model# T104P201). 2 days ago, after turning on the gas heater at 0900, approx 2 hr later it stops firing (still 10 deg below set temp) and I see a "CLK" in the lcd window of the heater. Pump continues to run fine. About 1300 the CLK goes away, and the gas heater fires up and runs normally the rest of the day until the timer turns off the pump and heater approx 5 hr later. This has happened 2 days in a row.

    I do not see the "firemans sw" in the Intermac timer nor extra control wires although my timer model number corresponds to a heater cutoff-firemans sw type. The heater wires (3-bk, wh, gr)(120v) only go to common and one hot lead (120v), and I do not see any control wires other that the 3 leads (grd, common, and hot). Where as the pump is wired for 220v, so two red leads to 2 hot terminals plus 1 grd wire.

    The "CLK" according to my heater owners manual means heater cooldown or firemans sw activated. What could be causing the CLK intermittent. And why would it go away after 2 hr and not reappear the rest of the day

    Bottom question is what is causing this "cooldown cycle" or CLK
    Don SW Florida
    10,000 gal in ground concrete pool
    Pentair Cartridge filter, Pentair SWG, Pentair Intelliflow VS pump (11018)
    FAFCO solar panels w/Pentair SolarTouch controller
    using BBB for pool chemistry/Lamotte ColorQ tester for daily testing

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,887

    Re: Raypak Gas Heater problem

    Presumably, something is connected to the fireman switch terminals in the heater. You should be able to find out where those terminals are in the heater, open the heater up and find the terminals, and see if anything is connected to them.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3
    donaldm823's Avatar
    Join Date
    May 2007
    Location
    Cape Coral, FL
    Posts
    146

    Re: Raypak Gas Heater problem

    UPDATE
    Pool service came to checkout my Raypack heater. They confirmed there is no clock function wired to my Intermac timer, so the "CLK" error can only be a faulty wire connection (plug) in the heater or my heater main board is going bad. He pulled the connector several times to clean off any high resistance contact and reinstalled x5 and then walked away. The alternative was to replace the main board ($450) or do a wait and see if the "CLK" reappears or if his "fix" worked. He also said that sun temp beating on the front f the heater control panel should have no effect on the circuit and there is no cooling fan.

    So will check tomorrow as supposed to be full sun. I only got the "CLK" in the morning when full sun shining on the heater. It does make sense to spend the $450 on the off chance the problem was simply the jumper wire had a high resistance contack on the multiplug

    Putting this on the board just in case there is someone else out there that has gotten this "CLK" error on their Raypack heater LCD OR has experienced a failed main board.

    UPDATE+++++UPDATE
    full sun yesterday (5/31) and yes got the "CLK" and no flame. It cleared itself in the afternoon after the sun went behind the house leaving the Raypak in the shade. So, ordered a new PC control board as the only that makes sense is a temp sensitive chip on the PC board. Found a cheap source for the OEM part for $259 so figured it was cheaper to easter egg than keep paying troubleshooting hourly rates!!!

    UPDATE+++UPDATE New PC Board installed// CLF fault corrected
    Received the RAypak kit from poolsupplyworld.com. Great kit and easy install with instructions providing lots of photo steps. 3 screws and 5 board plugs!. All fixed-heater fired up normally after PC board replaced. SO the CLK error/msg was really a PC board issue that did not identlify ittself as a board failure.
    Item Name – PC BOARD, RP2100 CURRENT - 010253F
    Quantity Ordered – 1
    SKU Number – 010253F
    Item Price – $259.95
    Total Price – $259.
    Don SW Florida
    10,000 gal in ground concrete pool
    Pentair Cartridge filter, Pentair SWG, Pentair Intelliflow VS pump (11018)
    FAFCO solar panels w/Pentair SolarTouch controller
    using BBB for pool chemistry/Lamotte ColorQ tester for daily testing

  4. Back To Top    #4

    Re: Raypak Gas Heater problem

    Hi I am currently looking into this heater...how old was it before it failed and was it not warrantied?
    IG freeform gunite w/attached spa. Purex Triton FNS Plus 60 filter with matching multiport backwash valve. Century 1.5HP motor. Purex Minimax Plus 400 gas heater.

  5. Back To Top    #5
    donaldm823's Avatar
    Join Date
    May 2007
    Location
    Cape Coral, FL
    Posts
    146

    Re: Raypak Gas Heater problem

    The RAypak heater in question was new April 2006. My PB says the Raypaks can last 10 years or longer if pool chemistry maintained. I fo one would still recommend Raypaks and the parts arre avaialble
    Don SW Florida
    10,000 gal in ground concrete pool
    Pentair Cartridge filter, Pentair SWG, Pentair Intelliflow VS pump (11018)
    FAFCO solar panels w/Pentair SolarTouch controller
    using BBB for pool chemistry/Lamotte ColorQ tester for daily testing

  6. Back To Top    #6
    Guest

    Re: Raypak Gas Heater problem

    RayPak is owned by Rheem now. Great heaters!

  7. Back To Top    #7

    Join Date
    Apr 2014
    Location
    San Diego, CA
    Posts
    18

    Re: Raypak Gas Heater problem

    Quote Originally Posted by donaldm823 View Post
    The RAypak heater in question was new April 2006. My PB says the Raypaks can last 10 years or longer if pool chemistry maintained. I fo one would still recommend Raypaks and the parts arre avaialble
    I have the RayPak 2100 and it came with the house 11 years ago.....and was probably 5 years old when we got it. So 16 years I guess, but now it has lost its spark. No ignition and it says SPK 22.
    AG plaster pool about 20k gallons kidney shaped, Nautilus FNS filter DE (runs at 22psi), Raypak RP2100 gas heater for spa, magnetek pool/spa motor 2hp, magnetek waterfall pump 1/2 hp and Hayward Pool Vac.

  8. Back To Top    #8

    In the Industry
    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    2,769

    Re: Raypak Gas Heater problem

    Please start a new thread for this.
    Paul
    http://www.gastekservices.com

    A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you.