    Intermatic timer replacement

    I am going to have to change out my intermatic timer pump timer soon. I have one hooked up to the pump and one to the booster pump for the cleaner. I do not care to have the booster pump on a timer that works as I only run it when I am around. So can I just switch out the pump timer and leave the other one as is? It seems to be a pretty quick swap. Is there anything special I need to know about it besides cut off the power to it when changing it? Is it something hard to do? It looks like basically swapping out a manual thermostat to a digital, just follow the wires. It is the one with a yellow face. Also if I did not want the pump to come on at my specified times, is there a way to do that?

    Thanks.
    13,000 Plaster IG Pool approx
    Hayward C5030 Cart Filter
    Emerson 1081 EB653 1.0 HP 1.40 S.F. 3450 RPM
    Pool Calculator, Pool School, TF Test Kits

  2. Back To Top    #2

    Join Date
    Mar 2010
    Location
    Spring, TX
    Posts
    1,082

    Re: Intermatic timer replacement

    13,000 Plaster IG Pool approx
    Hayward C5030 Cart Filter
    Emerson 1081 EB653 1.0 HP 1.40 S.F. 3450 RPM
    Pool Calculator, Pool School, TF Test Kits

  3. Back To Top    #3
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    21,778

    Re: Intermatic timer replacement

    Which timer do you have? Anyway, it should be a simple changeout.

    There should be a manual switch on the timer to turn it on manually and you can just remove the pins to keep it from coming on.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  4. Back To Top    #4

    Join Date
    Mar 2010
    Location
    Spring, TX
    Posts
    1,082

    Re: Intermatic timer replacement

    This is not mine, but I have the same one. Mine actually has two of these in one box. MIne also has a black swith to the right of the time, but I think this is for a heater. Since I do not have a heater, do I need a timer with this switch. I think it is called a fireman switch and it is black and to the right.
    Attached Images Attached Images
    13,000 Plaster IG Pool approx
    Hayward C5030 Cart Filter
    Emerson 1081 EB653 1.0 HP 1.40 S.F. 3450 RPM
    Pool Calculator, Pool School, TF Test Kits

  5. Back To Top    #5
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    21,778

    Re: Intermatic timer replacement

    If you'll look to the bottom right of the time dial you'll see a small handle. That's the manual switch. There are arrows below it to indicate the on/off positions.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  6. Back To Top    #6

    Join Date
    Mar 2010
    Location
    Spring, TX
    Posts
    1,082

    Re: Intermatic timer replacement

    Quote Originally Posted by Bama Rambler
    If you'll look to the bottom right of the time dial you'll see a small handle. That's the manual switch. There are arrows below it to indicate the on/off positions.
    So when the timer works, do you leave it in the on spot and it comes on and off when it should? If you turn it off, it will not come on with the timer settings?
    13,000 Plaster IG Pool approx
    Hayward C5030 Cart Filter
    Emerson 1081 EB653 1.0 HP 1.40 S.F. 3450 RPM
    Pool Calculator, Pool School, TF Test Kits

  7. Back To Top    #7
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    21,778

    Re: Intermatic timer replacement

    Yes that's correct.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  8. Back To Top    #8

    Join Date
    Mar 2010
    Location
    Spring, TX
    Posts
    1,082

    Re: Intermatic timer replacement

    I have seen these for sale at the pool store, can you buy them anywhere else? Such as lowes, home depot, etc?
    13,000 Plaster IG Pool approx
    Hayward C5030 Cart Filter
    Emerson 1081 EB653 1.0 HP 1.40 S.F. 3450 RPM
    Pool Calculator, Pool School, TF Test Kits

  9. Back To Top    #9

    Join Date
    Jun 2007
    Location
    New Jersey
    Posts
    651

    Re: Intermatic timer replacement

    Quote Originally Posted by mynewpool
    I have seen these for sale at the pool store, can you buy them anywhere else? Such as lowes, home depot, etc?
    I always get those at my electric supply house. Many, if not most, are Intermatic dealers and can get you any model, extra trippers, a motor or just the mechanism without the case for repairs, etc. The difference between a timer and a thermostat is ten times the voltage (24V vs. 240V). 240V can kill you. 24V can't. So be very careful.

    I don't really understand why you are swapping it out. Is it broken? You can change just the motor or just the timer mechanism (including motor) and reuse your existing case. If you remove the trippers, it has no timing function and you can use just the manual switch. The fireman switch might have another use other than a heater. For instance, it might only allow the auxiliary pump to run only when the main pump is in operation. It is a separate module and can be moved to a new timer or a new mechanism if so required. In any case, I would try to trace its wires to see what it is intended to do.

    If you are uncomfortable with any of this, call an electrician.
    Current: 28,000G 18'x36' I/G AnthonySylvan Plaster; Waterway 60 sq.ft. DE Filter; 1.0hp x 1.65 SF Two-Speed (B2982) WhisperFlo; 2004-Present
    Previous: 40,000G 20'x40' I/G Koven unlined WWII salvage 5/8" marine steel; Lomart Stainless Sand Filter; 3/4hp Hayward SuperPump; 1946-2003 (managed by me from about 1964)
    Ancient Taylor K-2000, upgraded with Taylor CH, TA, and FAS-DPD, and TFT CYA tests.

  10. Back To Top    #10

    Join Date
    Mar 2010
    Location
    Spring, TX
    Posts
    1,082

    Re: Intermatic timer replacement

    Quote Originally Posted by Durk
    Quote Originally Posted by mynewpool
    I have seen these for sale at the pool store, can you buy them anywhere else? Such as lowes, home depot, etc?
    I always get those at my electric supply house. Many, if not most, are Intermatic dealers and can get you any model, extra trippers, a motor or just the mechanism without the case for repairs, etc. The difference between a timer and a thermostat is ten times the voltage (24V vs. 240V). 240V can kill you. 24V can't. So be very careful.

    I don't really understand why you are swapping it out. Is it broken? You can change just the motor or just the timer mechanism (including motor) and reuse your existing case. If you remove the trippers, it has no timing function and you can use just the manual switch. The fireman switch might have another use other than a heater. For instance, it might only allow the auxiliary pump to run only when the main pump is in operation. It is a separate module and can be moved to a new timer or a new mechanism if so required. In any case, I would try to trace its wires to see what it is intended to do.

    If you are uncomfortable with any of this, call an electrician.
    I am not sure if you would call it broken, as it works as a manual switch, but the timer aspect does not work. I thought it would be easier to just pull it out and switch in a new one. I have changed out manual to digital thermostats, so it seems to be a simlilar deal. The fireman switch has two black wires coming off of them and they are both capped off, so I see now use for that. The booster pump is hooked up with the main pump. If the main pump is not on, neither will the booster pump. It seems the booster pump was jumped off of the main pump. So we shall see.
    13,000 Plaster IG Pool approx
    Hayward C5030 Cart Filter
    Emerson 1081 EB653 1.0 HP 1.40 S.F. 3450 RPM
    Pool Calculator, Pool School, TF Test Kits

  11. Back To Top    #11

    Join Date
    Jun 2007
    Location
    New Jersey
    Posts
    651

    Re: Intermatic timer replacement

    Quote Originally Posted by mynewpool
    I am not sure if you would call it broken, as it works as a manual switch, but the timer aspect does not work. I thought it would be easier to just pull it out and switch in a new one. I have changed out manual to digital thermostats, so it seems to be a simlilar deal. The fireman switch has two black wires coming off of them and they are both capped off, so I see now use for that. The booster pump is hooked up with the main pump. If the main pump is not on, neither will the booster pump. It seems the booster pump was jumped off of the main pump. So we shall see.
    So you probably just need a new clock motor. Look through the hole in the gray plate just right of top center. If the motor is running you can see the gears turning. You can just pull the mechanism forward (after disconnecting electric supply at panel), unscrew the motor (3 or 4 screws), unscrew the motor wires from the supply line screws, and replace. Much cheaper than a new timer and actually easier to do.

    Yes, if the fireman switch is capped off, you don't need it. You had not included that detail.
    Current: 28,000G 18'x36' I/G AnthonySylvan Plaster; Waterway 60 sq.ft. DE Filter; 1.0hp x 1.65 SF Two-Speed (B2982) WhisperFlo; 2004-Present
    Previous: 40,000G 20'x40' I/G Koven unlined WWII salvage 5/8" marine steel; Lomart Stainless Sand Filter; 3/4hp Hayward SuperPump; 1946-2003 (managed by me from about 1964)
    Ancient Taylor K-2000, upgraded with Taylor CH, TA, and FAS-DPD, and TFT CYA tests.

  12. Back To Top    #12

    Join Date
    Mar 2010
    Location
    Spring, TX
    Posts
    1,082

    Re: Intermatic timer replacement

    Quote Originally Posted by Durk
    Quote Originally Posted by mynewpool
    I am not sure if you would call it broken, as it works as a manual switch, but the timer aspect does not work. I thought it would be easier to just pull it out and switch in a new one. I have changed out manual to digital thermostats, so it seems to be a simlilar deal. The fireman switch has two black wires coming off of them and they are both capped off, so I see now use for that. The booster pump is hooked up with the main pump. If the main pump is not on, neither will the booster pump. It seems the booster pump was jumped off of the main pump. So we shall see.
    So you probably just need a new clock motor. Look through the hole in the gray plate just right of top center. If the motor is running you can see the gears turning. You can just pull the mechanism forward (after disconnecting electric supply at panel), unscrew the motor (3 or 4 screws), unscrew the motor wires from the supply line screws, and replace. Much cheaper than a new timer and actually easier to do.

    Yes, if the fireman switch is capped off, you don't need it. You had not included that detail.
    Yea they are not turning as that was pointed out to me during pool school. Where can I pick up these pool motors? Will I need to change the gears or anything?
    13,000 Plaster IG Pool approx
    Hayward C5030 Cart Filter
    Emerson 1081 EB653 1.0 HP 1.40 S.F. 3450 RPM
    Pool Calculator, Pool School, TF Test Kits

  13. Back To Top    #13

    Join Date
    Jun 2007
    Location
    New Jersey
    Posts
    651

    Re: Intermatic timer replacement

    From the Intermatic website:

    There are 5 locations within 10 miles of 77389.

    Now viewing page 1 out of 1 pages.
    6 milesConroe Lighting & Supply
    1144 Rayford Road #5
    Spring, TX 77386
    (281) 296-7777
    7 milesElliott Electric
    201 South Persimmon Street
    Tomball, TX 77375
    () -
    8 milesCity Electrical Sy
    16749-F North Freeway
    Houston, TX 77090
    (281) 580-5200
    8 milesJohnstone Supply
    15631 Blue Ash #160
    Houston, TX 77090
    (281) 872-5200
    8 milesLloyd Graves Elec Sy Co
    21604 North I-45 Freeway
    Spring, TX 77373
    Best approach is to take out the old clock motor and bring it with you to one of these places. (all Intermatic distributors--don't waste time at Home Depot as they won't have it.) Just remember what screws the two motor wires were on. [They go on the incoming supply Line screws.] The motor has the pinion gear on it, and when you screw it in place, it will mesh with the clockwork on the timer. Really quite easy--just be safe. The motor is in an aluminum can about the size of a roll of tape held to the back of the gray plate by 2 or 3 screws. The plate is held in the case by a spring clip on either side. Spray some WD40 on all the gears while you are in there.
    Current: 28,000G 18'x36' I/G AnthonySylvan Plaster; Waterway 60 sq.ft. DE Filter; 1.0hp x 1.65 SF Two-Speed (B2982) WhisperFlo; 2004-Present
    Previous: 40,000G 20'x40' I/G Koven unlined WWII salvage 5/8" marine steel; Lomart Stainless Sand Filter; 3/4hp Hayward SuperPump; 1946-2003 (managed by me from about 1964)