    Generators

    Any electricians on here? I'm considering buying a generator for power outages and am not sure how I would run my pool pump. There is no "plug" as it's hardwired into the breaker box. How could I hook up a generator in this case?

    Donnie
    8500 Gallon Fiberglass IG / Sta-Rite pump,cartridge filter & heater / PoolPilot Dig 220-36 SWG / Testing w/K2006

  2. Back To Top    #2

    Join Date
    Mar 2007
    Location
    Coastalish 'down easter'
    Posts
    4,160

    Re: Generators

    Donnie, while I'm certainly NOT an electrician, my boss had a generator installed on his house a few years ago. His is a propane beast, large enough to run the vital functions of his house, and it's run into the main breaker box with some sort of sensor that knows to kick on the generator if there's no power (he tests it by killing the main feed to the box). If you're talking about a gas generator that you need to 'pull start', I'm sure there's a way to - I just don't know how to do it (of course you'd have to keep the propane tank full or stock up on gas before any possible power outages in freezing temps )
    Luv& Luk
    -Ted

    Having done construction and service for 4 pool companies in 4 states starting in 1988, what I know about pools could fill a couple of books - what I don't know could fill a couple of libraries :-D

    POOL SCHOOL, TF Testkits, Jason's Pool Calculator, CYA vs. cl chart, (Just a few DARNED handy links!)

  3. Back To Top    #3
    DONNIE's Avatar
    Join Date
    Mar 2007
    Location
    OKLAHOMA
    Posts
    122

    Re: Generators

    I've priced the whole house generators and while I'd love to have one I can't justify the price vs use. I'm thinking about a $700, 8000 watt, gas, pull start emergency generator. Something to run the pump, furnace, a tv and a few lights.

    Donnie
    8500 Gallon Fiberglass IG / Sta-Rite pump,cartridge filter & heater / PoolPilot Dig 220-36 SWG / Testing w/K2006

  4. Back To Top    #4
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,887

    Re: Generators

    To use a generator with a hard wired pool pump you will need some minor electrical work done. You would have a transfer switch installed, which allows you to move selected circuits from utility power to the generator and back as needed. The generator also needs to be rated to handle the load from the pump, which usually means a fairly large generator.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  5. Back To Top    #5
    Molson's Avatar
    Join Date
    Apr 2008
    Location
    Midland, Ontario
    Posts
    479

    Re: Generators

    When I had my electrical fire at my house in 2008, I had 2 generators running for a month. 1 to power the fridge/freezer, the other for the pool. I had the electrician wire it for 110 with a simple plug on the end, which I plugged in the generator. I ran it during the day, I believe it was a 3000 watt gen. Ran it perfectly. (and my pond too)
    40 x 16 IG Vinyl. Goldline SWG
    160 Sq Ft Roof mounted solar array
    2014 Hydropool Serenity 5000 Hot Tub
    The Pool School- A great place to start
    Jason's Pool calculator

  6. Back To Top    #6
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    21,778

    Re: Generators

    The proper way to do it is with an distributed load automatic transfer switch. The best way to do it is buy a generator with enough capacity to run your whole house and add about 30 seconds of UPS power to run it while the genny starts up.

    A down and dirty way to do it would be to buy a manual transfer switch and a power distribution center (breaker panel) and move the critical circuits to the switched panel. Then when the power goes out you just go throw the switch and start the genny and you're off and running.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  7. Back To Top    #7

    Join Date
    Nov 2009
    Location
    Indialantic, FL
    Posts
    323

    Re: Generators

    And the way to kill (literally) your electric company linemen is to run it into the main panel, "back-feeding", while not providing a means to disconnect from the main service.
    Geometric 16X36', 16K gal, shotcrete, exposed aggregate plaster, acrylic coated concrete deck/cantilever coping;
    Pentair equipment suite (EasyTouch w/wireless, 2 Intellibrites, Intelliflo VS-3050, C&C 200 Filter, IC-40 SWG);
    Heliocol solar panels, Rocky's Roller, Blue Diamond robot

  8. Back To Top    #8
    Brentr's Avatar
    Join Date
    Oct 2009
    Location
    Jacksonville, FL
    Posts
    874

    Re: Generators

    Quote Originally Posted by lee32903
    And the way to kill (literally) your electric company linemen is to run it into the main panel, "back-feeding", while not providing a means to disconnect from the main service.
    Always disconnect your main breaker when running a generator back feeding I have an emergency generator with one plug in at the main breaker in the garage and I plan to put one at the pool sub panel. When you have a power outage you first need to disconnect the main breaker, then you fire up your generator and backfeed the things that are essential. I got our generator from Home Depot. It is a 7KW and runs everything except the AC units. I have a small window AC unit for this purpose. Hope this helps
    5,775 gal, IG free form, Beach Series Antigua by Marbletite Pebble finish, 2 swim out benches, Sheer Descent, IG Fountain, Dolphin / Mermaid Statues, StaRite Dura- Glas 1.5hp pump, Hayward Pro Series Sand Filter replaced with Hayward Pro-grid DE4820, Aqua Rite SWG with T-Cell 15, Polaris 360, Pentair 300w Light upgraded to Pentair IntelliBrite (OMG what a huge difference) , Heat Siphon Heat Pump DX 5.0 109,000 btu, Pool Cage, 1800sq ft Tremron Estate Pavers, solar cover, TF-100 test kit, Pentair Deck Jet, Apollo Magnetic Stirrer (Makes testing a breeze), Aquatherm Ecosun Solar Panels 192 sq ft with GL-235 Controller,Margarita Concoction Machine,
    Pics of our Spool ( Social Pool) being built Solar install Outdoor kitchen upgrade

  9. Back To Top    #9
    New2Me's Avatar
    Join Date
    Jun 2008
    Location
    SW Indiana
    Posts
    322

    Re: Generators

    Most minimum codes require something like this - http://www.interlockkit.com/ if you are going to use a generator. It's a whole lot easier then moving circuits to a new panel.
    22 x 40 IG vinyl lined, 23,570 gal.
    1 hp. Pac-Fab Challenger pump 300# sand filter
    Intex 8110 SWG, Hayward CL220 offline feeder
    Hayward 250K Btu gas heater
    Aquabots

  10. Back To Top    #10
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    21,778

    Re: Generators

    I didn't know that existed but it's a wonderful idea. It's a bit expensive for what it is, but a good idea.

    The reason for installing a secondary switched panel for critical loads is because a lot of people don't want to buy a large enough generator to run the whole house so they have to remember to turn off the non essential breakers, which of course they don't.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  11. Back To Top    #11
    Brentr's Avatar
    Join Date
    Oct 2009
    Location
    Jacksonville, FL
    Posts
    874

    Re: Generators

    Quote Originally Posted by Bama Rambler
    I didn't know that existed but it's a wonderful idea. It's a bit expensive for what it is, but a good idea.

    The reason for installing a secondary switched panel for critical loads is because a lot of people don't want to buy a large enough generator to run the whole house so they have to remember to turn off the non essential breakers, which of course they don't.
    Good advice We lived on boats for 5-6 yrs and know the importance of power sharing. I do not recommend backfeeding unless your are very disciplined and fully understand what your are doing However most people who tinker with RVs and Large boats are familiar with this
    5,775 gal, IG free form, Beach Series Antigua by Marbletite Pebble finish, 2 swim out benches, Sheer Descent, IG Fountain, Dolphin / Mermaid Statues, StaRite Dura- Glas 1.5hp pump, Hayward Pro Series Sand Filter replaced with Hayward Pro-grid DE4820, Aqua Rite SWG with T-Cell 15, Polaris 360, Pentair 300w Light upgraded to Pentair IntelliBrite (OMG what a huge difference) , Heat Siphon Heat Pump DX 5.0 109,000 btu, Pool Cage, 1800sq ft Tremron Estate Pavers, solar cover, TF-100 test kit, Pentair Deck Jet, Apollo Magnetic Stirrer (Makes testing a breeze), Aquatherm Ecosun Solar Panels 192 sq ft with GL-235 Controller,Margarita Concoction Machine,
    Pics of our Spool ( Social Pool) being built Solar install Outdoor kitchen upgrade

  12. Back To Top    #12
    New2Me's Avatar
    Join Date
    Jun 2008
    Location
    SW Indiana
    Posts
    322

    Re: Generators

    There was a very bad ice storm (termed a Perfect Storm by the TV talking weather-heads) that hit the Western Kentucky area one year ago. Power was out in some areas for weeks. Temperatures were below freezing for weeks.
    Generators, extension cords and male plugs dis-appeared from local stores, as people got desperate for heat.
    Luckily, I know of no reports of any electrocutions!
    Unfortunately, I do recall reports of Carbon Monoxide Poisoning, and fire, from running and fueling, generators and heaters inside of houses and garages.
    IF you are going to use a generator, be careful!!!
    22 x 40 IG vinyl lined, 23,570 gal.
    1 hp. Pac-Fab Challenger pump 300# sand filter
    Intex 8110 SWG, Hayward CL220 offline feeder
    Hayward 250K Btu gas heater
    Aquabots

  13. Back To Top    #13
    Brentr's Avatar
    Join Date
    Oct 2009
    Location
    Jacksonville, FL
    Posts
    874

    Re: Generators

    Also please install Carbon Monoxide Detectors The digital ones are $25.00 at WalMart. This is a must in my opinion
    5,775 gal, IG free form, Beach Series Antigua by Marbletite Pebble finish, 2 swim out benches, Sheer Descent, IG Fountain, Dolphin / Mermaid Statues, StaRite Dura- Glas 1.5hp pump, Hayward Pro Series Sand Filter replaced with Hayward Pro-grid DE4820, Aqua Rite SWG with T-Cell 15, Polaris 360, Pentair 300w Light upgraded to Pentair IntelliBrite (OMG what a huge difference) , Heat Siphon Heat Pump DX 5.0 109,000 btu, Pool Cage, 1800sq ft Tremron Estate Pavers, solar cover, TF-100 test kit, Pentair Deck Jet, Apollo Magnetic Stirrer (Makes testing a breeze), Aquatherm Ecosun Solar Panels 192 sq ft with GL-235 Controller,Margarita Concoction Machine,
    Pics of our Spool ( Social Pool) being built Solar install Outdoor kitchen upgrade