    heater 60 amp panel?

    Question for ya. I have a 60 amp sub panel at the pool shed that is running off of a 100 amp sub panel under my porch. There are no other circuits on the 100 amp panel just the 60 amp circuit. It's just there in case I ever decide on installing a hot tub. How many amps can I run off the 60 amp sub panel?
    So basically i have 150 main to 100 sub to 60 sub at pool shed. I was curious if a pool heat pump can run off the 60 sub panel w my pump and chlorinator?
    18x44 double Roman vinyl pool, Hayward superpump, Hayward DE Filter,
    Aqua Rite T15 SWG, Taylor k 2006 test kit

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,750

    Re: heater 60 amp panel?

    Theoretically you can run 60 amps through that panel. The wire is sized to handle 60 amps, so you can't exceed that without upgrading the wire and breaker.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3

    Join Date
    Nov 2015
    Location
    Boston, MA
    Posts
    142

    Re: heater 60 amp panel?

    Okay thank you
    18x44 double Roman vinyl pool, Hayward superpump, Hayward DE Filter,
    Aqua Rite T15 SWG, Taylor k 2006 test kit

  4. Back To Top    #4
    setsailsoon's Avatar
    Join Date
    Oct 2015
    Location
    Stuart/FL
    Posts
    493

    Re: heater 60 amp panel?

    Dave's correct but the only caveat I'd add is this assumes the wire size was chosen so that it conforms to NEC requirements. This is a safe assumption almost all of the time. However, I've found sometimes the sub panel is added after the original build that had a building department inspection or was added by a "handy man" and the supply wire was too small. There are usually other signs like sloppy wire installation, wire is exposed not in conduit, or sloppy mounting of the sub panel. If you suspect this it's easy to look up the wire size and check.

    I hope this helps.

    Chris
    -Chris-
    2013 In-ground plaster/pebble, screen enclosed, 12000 gal w/ Jandy 2 speed 1 HP pump, Jandy CS 200 cartridge filter, 800 gal spa w/ 1.5 HP booster pump, Solar heater, 2 LED lights in pool 1 light in spa, TF-100 test kit, The PoolCleaner Next Generation, Jandy RS-12 Automation system with iAqualink 2.0 control, Separate Hayward/Goldline Solar control

  5. Back To Top    #5
    CJadamec's Avatar
    Join Date
    Apr 2016
    Location
    Quaker Hill, CT
    Posts
    2,192

    Re: heater 60 amp panel?

    It's not just the wire size that matters you need to know how long the wire is as well as what gauge it is. If you are going to add a heat pump it is heavy continuous draw equipment. You don't want to be borderline with your wire size and a heat pump. Make sure you take into account the wiring to both panels when you figure your voltage drop.
    Chuck-
    15x30 AG, Pentair Superflo VS, 19" sand filter, TF-100 test kit
    Aqua Comfort ACT750 heat pump / 6x20 ground mount solar panel / DIY automation

    Photos of 2016 Build, Inside Your Breaker Panel, Free Copy of 2017 NEC code
    TFP is AD Free and is funded solely by member support click here to help

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •