    Strange electrical problem - Fuse blowing

    I recently added an Intermatic T101 mechanical timer, and now about once a week the 20A fuse that is in the circuit blows out. Before adding the timer I never blew a fuse. I tested with an ammeter, with the pump on it draws 10.6A pre-timer and 10.4A on the pump side of the timer. I have a Hayward 1HP PowerFlo II pump.

    currently the electrical is set up like

    house box > fuse/switch box in garage > GFCI outlet > timer > pump

    The timer is hard wired in with 10ga wire connected to the load side of the GFCI outlet.

    I'm totally stumped as to why this is happening since I have tested all of the connections and everything is set up correctly. Any ideas? Should I move the timer to be before the fuse box and GFCI?
    10,600 Gallon 12x32x4 Above Ground
    Hayward Veri-Flo sand filter
    Hayward 1hp pump

    Taylor k-2006

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    21,774

    Re: Strange electrical problem - Fuse blowing

    Is the fuse that's blowing on the timer itself or elsewhere?

    It appears to be wired correctly.

    From your description it sounds like the timer has to be the problem, but we'll know more once we know exactly what is failing.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3

    Join Date
    Apr 2008
    Location
    UhhhHiya
    Posts
    26

    Re: Strange electrical problem - Fuse blowing

    There is no fuse on the timer itself. It is this thing wired in with the conduit...
    10,600 Gallon 12x32x4 Above Ground
    Hayward Veri-Flo sand filter
    Hayward 1hp pump

    Taylor k-2006

  4. Back To Top    #4
    TizMe's Avatar
    Join Date
    Aug 2007
    Location
    Covington, Georgia
    Posts
    920

    Re: Strange electrical problem - Fuse blowing

    In the picture of the switch thingy it says 15amps max but your saying it blew a 20amp fuse ? Is there anything plugged into the GFCI outlet drawing power?

    We had an electrician come to the house and run a line to our storage shed with 60 amps available to us for the pool. Then off that he ran a line to the pool for the filter to run on I think 20amps (would have to double check that)
    but he said it would be more than ample for what we needed up there.
    Les
    Don't have a pool right now. Just sharing what I have learned over the years!
    Helpful Links:
    Pool School,Pool Calculator,Cl/CYA Shock Chart,TF Test Kit
    Doing BBB and loving it!

  5. Back To Top    #5

    Join Date
    Apr 2008
    Location
    UhhhHiya
    Posts
    26

    Re: Strange electrical problem - Fuse blowing

    The one that I have is 20A. It's also interesting to note that I have never tripped the breaker in the house for this circuit.

    Nothing else is plugged into the GFCI. While I would like a new 60A circuit run to the garage, I doubt that would fix my current (HA!) problem.

    I am going to take apart the fuse box tomorrow and check the current at that point..
    10,600 Gallon 12x32x4 Above Ground
    Hayward Veri-Flo sand filter
    Hayward 1hp pump

    Taylor k-2006

  6. Back To Top    #6

    Join Date
    Jun 2007
    Location
    New Jersey
    Posts
    651

    Re: Strange electrical problem - Fuse blowing

    Are you using slo-blo or regular fuses? A time delay fuse of 20 amps is appropriate for a 1.5 hp 110 VAC circuit assuming the wiring (12ga. or better) is sized appropriately. You are using a switch/fuse combo sized for 15 amp, but the risk of failure there is probably the switch, not the fuse part. Still, if I've got a 1.5 hp motor on a 15 amp switch that needs a 20 amp fuse, I would review the whole circuit for load size capability.
    Current: 28,000G 18'x36' I/G AnthonySylvan Plaster; Waterway 60 sq.ft. DE Filter; 1.0hp x 1.65 SF Two-Speed (B2982) WhisperFlo; 2004-Present
    Previous: 40,000G 20'x40' I/G Koven unlined WWII salvage 5/8" marine steel; Lomart Stainless Sand Filter; 3/4hp Hayward SuperPump; 1946-2003 (managed by me from about 1964)
    Ancient Taylor K-2000, upgraded with Taylor CH, TA, and FAS-DPD, and TFT CYA tests.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •