    Air in pump when heating on?

    Hi,

    After winter and without the heater on, just running the pump, I found a lot of air bubbling out of my returns in the pool and weak flow. I thought I must have a leak on the suction side. Whilst investigating, I started to bleed the air using the valve on top of the filter. After several hours doing this, the air bubble seen in the pump cover disappeared, as did the bubbling at the returns and the flow returned to normal.
    Today, the water was at 70 f and the pump running for a second hour. I switched the boiler on and returned less than an hour later to see a big bubble in my pump cover, but no bubbling from returns in the pool.
    The heating circuit isn't on the suction side, so...?
    This is the second time it's happened this season. Can you get an intermittent leak on suction side? Just seems odd both times it happened when I switched heating on after just running pump daily up until then.
    Any help gratefully received. Here's a pic of the plant room attached to the cabin housing the hydrotherapy pool.

    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.

  2. Back To Top    #2
    Mod Squad pooldv's Avatar
    Join Date
    Aug 2012
    Location
    DFW, TX
    Posts
    24,974

    Re: Air in pump when heating on?

    It is not unusual to have some air build up when you first start up equipment. If the air dissipates and doesn't return then everything is fine. If it returns daily or gets worse then it is time to track down a leak.

    More here, Pool School - Suction Side Air Leaks
    TFP Moderator
    If TFP helped you or saved you money - Become a TFP Supporter! <--Click here
    2012 build and pics, 20k gal gunite, black onyx pebblesheen, OK flagstone, IntellifoVS, cart filter w/Pleatco, IC40 SWG, Solartouch, 5 12'x4' solar panels, HP50HA heat pump, 8mil solar cover, borates, TF-100 test kit, SONOS, Doheny's Discovery Robot, hot tub on bleach

  3. Back To Top    #3
    Mattsway's Avatar
    Join Date
    Apr 2017
    Location
    Sussex UK
    Posts
    30

    Re: Air in pump when heating on?

    Ok, I've checked again and small bubbles are again coming from the returns, so a suction side leak. There were definitely none before, so it's intermittent. Perhaps the leak occurs when hot water expands joints in the suction pipework?

    Just had a gander at your pool build, pooldv - N-I-C-E!
    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.

  4. Back To Top    #4
    Mattsway's Avatar
    Join Date
    Apr 2017
    Location
    Sussex UK
    Posts
    30

    Re: Air in pump when heating on?

    I closed the red valve on the main drain feed to the pump whilst it was running, thinking I was thereby isolating the skimmer line. Instantly, the water in the pump basket went below the inlet pipe, so I turned off the pump. Does this confirm that the air is being sucked through the skimmer line, or just that I shouldn't have turned off the main?
    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.

  5. Back To Top    #5
    Mattsway's Avatar
    Join Date
    Apr 2017
    Location
    Sussex UK
    Posts
    30

    Re: Air in pump when heating on?

    Just looked again at my setup and with good flow to the pool (despite the pump only priming to just above the inlet pipe) the water in the skimmer is not flowing over the top of the floating Weir. The weir moves up and down freely with a light touch, but my understanding is that the pump should suck it down a little to establish a flow. Is this further indication of a suction leak on the skimmer line? Shutting off the skimmer doesn't affect the pressure reading on the filter. I think I'll leave the skimmer inlet valve shut and try bleeding the air out of the filter again with just the main drain open, although this seems to take hours. (Is there any reason a bleed valve on the pump lid wouldn't work?) If all the air bleeds out of the pump and stays out, I'll know it's the skimmer line.
    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.

  6. Back To Top    #6

    In the Industry

    duraleigh's Avatar
    Join Date
    Apr 2007
    Location
    Sebring, Florida
    Posts
    30,961

    Re: Air in pump when heating on?

    the water in the skimmer is not flowing over the top of the floating Weir.
    is it sucking air into the skimmer since the water is not flowing? Then the pool water is not high enough.
    Dave S.
    42k vinyl and concrete pool, 1.5hp pump, 140gpm filter
    TFTestkits , PoolMath , Pool School

  7. Back To Top    #7
    Mattsway's Avatar
    Join Date
    Apr 2017
    Location
    Sussex UK
    Posts
    30

    Re: Air in pump when heating on?

    Water not flowing over Weir despite good flow into pool, as above;



    - - - Updated - - -

    Water level ok?

    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.

  8. Back To Top    #8
    Mattsway's Avatar
    Join Date
    Apr 2017
    Location
    Sussex UK
    Posts
    30

    Re: Air in pump when heating on?

    I bled the air out as before, but this time, with the skimmer line shut off, none has returned which is not such a problem, given the pool is in a cabin with only my son, myself and my wife ever using it. Better flow just on main drain anyway.
    I could slowly turn on the skimmer and check for air, just to confirm, but I've had enough of bleeding the air out through the filter for now. In fact, because it takes so many uses of the bleeder valve to expel all the air, little by little, it is now leaking a drop a second. Is there an o ring to replace/lube or can I wrap PTFE tape on the thread?

    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.

  9. Back To Top    #9
    Mattsway's Avatar
    Join Date
    Apr 2017
    Location
    Sussex UK
    Posts
    30

    Re: Air in pump when heating on?

    No air in system for an hour before turning heater on. Nothing for first hour of it being switched on, but three hours later, a 2 inch bubble in pump cover. I guess the heat (91 f) has opened up a leak in the main drain? Time to peel the vinyl splashback off and lift the ply cabinet lid to get at the skimmer and main drain pipework. Ho hum!
    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.

  10. Back To Top    #10
    Mattsway's Avatar
    Join Date
    Apr 2017
    Location
    Sussex UK
    Posts
    30

    Re: Air in pump when heating on?

    Silicone lube arrived today, so I used it on the o rings on the pump lid and basket drain valve, the air valve on the filter, the union onto the front of the pump and unions to main and skimmer valves. The lube instantly worked to allow the leaking air valve to seal, but no immediate prime on the pump, so although I'll carry on bleeding the air out as before, I expect it to return little by little.
    In doing this job, I realised the cut outs in the cabin wall, bringing the 2 suction pipes in have been cut to the size of the pipe, giving no room for the expansion and contraction of the timber (please see photo above) I reckon the joints I can't yet get at have been compromised by this seasonal movement. We'll see when the builders come to visit.
    In ground hydrotherapy pool in wooden cabin. Oil heater for water temp 89f. Poly Bloc construction using high temp liner. 9'9" square x 3'8" deep, 2700 gallons. Hayward MaxFlo XL pump, model SP2310XE161 0.97hp. Waterco Multicyclone 12 Plus Centrifugal Filter, guage reads 16psi. Certikin Skimmer with floating collar Weir. Spectrum UV light, Calorex 33 dehumidifier and 2 radiators in cabin. Taylor K2006C test kit.