Prologic PLPS4 or PLPS8

According to the manual, The connection at the main house panel should be to a 240VAC circuit breaker rated at 100A maximum.

I am going to have an existing 40A breaker main house connections that feed PLPS8 main powers. Can someone confirm my 40A breaker would be fine?
 
It would be best if you could keep the same project in one thread. Otherwise we go nuts and get lost.

Can you install a PLPS8 control center on a 40 Amp 240 breaker? Yes. Will it work for you? I don't know. With 4 pumps you need to do some math and also take into account the other loads.
 