mx702
|
Post subject: Tinned copper?  Posted: November 26th, 2011, 10:36 pm |
Joined: August 2nd, 2010, 3:56 pm Posts: 157 Location: MA
|
|
Would the use of tinned copper for pool/spa wiring be considered code compliant? I am having trouble finding any info regarding this in the NEC.
_________________ Completed: June 2011 18' X 38' IG Vinyl, 3' - 8' depth ~ 24K gallons 2 skimmers, 2 wall suctions, 3 returns, 1.5" piping Hayward Equipment: 1HP Tri-star 2-speed, Aqua-Plus SWG, Star-Clearâ„¢ Plus 175 sqft cartridge filter, Colorlogic 4.0 LED The Pool Cleaner 4X(suction) 2011 Jacuzzi J-280 Hot tub
|
|
|
|
 |
|
JasonLion
|
Post subject: Re: Tinned copper?  Posted: November 26th, 2011, 10:56 pm |
| Site Admin |
 |
 |
Joined: May 7th, 2007, 3:03 pm Posts: 23821 Location: Silver Spring, MD
|
|
It depends what you are doing with it. Tinned copper is not suitable for bonding, but can be used in several other places.
_________________ 19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot TFP Admin. Creator of The Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School
|
|
|
|
 |
|
mx702
|
Post subject: Re: Tinned copper?  Posted: November 26th, 2011, 11:22 pm |
Joined: August 2nd, 2010, 3:56 pm Posts: 157 Location: MA
|
|
Jason,
I intend on using it to power my portable hot-tub. Three #6 insulated and stranded wires. 2 hots and a ground.
_________________ Completed: June 2011 18' X 38' IG Vinyl, 3' - 8' depth ~ 24K gallons 2 skimmers, 2 wall suctions, 3 returns, 1.5" piping Hayward Equipment: 1HP Tri-star 2-speed, Aqua-Plus SWG, Star-Clearâ„¢ Plus 175 sqft cartridge filter, Colorlogic 4.0 LED The Pool Cleaner 4X(suction) 2011 Jacuzzi J-280 Hot tub
|
|
|
|
 |
|
mx702
|
Post subject: Re: Tinned copper?  Posted: November 29th, 2011, 6:45 am |
Joined: August 2nd, 2010, 3:56 pm Posts: 157 Location: MA
|
_________________ Completed: June 2011 18' X 38' IG Vinyl, 3' - 8' depth ~ 24K gallons 2 skimmers, 2 wall suctions, 3 returns, 1.5" piping Hayward Equipment: 1HP Tri-star 2-speed, Aqua-Plus SWG, Star-Clearâ„¢ Plus 175 sqft cartridge filter, Colorlogic 4.0 LED The Pool Cleaner 4X(suction) 2011 Jacuzzi J-280 Hot tub
|
|
|
|
 |
|
X-PertPool
|
Post subject: Re: Tinned copper?  Posted: December 1st, 2011, 10:15 am |
| In the Industry |
 |
Joined: June 12th, 2009, 10:35 pm Posts: 888 Location: Exeter, PA
|
|
Here is a snippet from the wiring that came with my spa. Basically as long as your not using aluminum wire you should be okay. Naturally if you want to be super sure just ask the guy at the electrical store (not home depot/lowes). From what I can tell though the wire you are talking about is better than just plain copper wire anyways.
240 Volt Electrical Installation GFCI and Wiring Requirements The power supplied to the spa must be on a dedicated GFCI protected circuit as required by ANSI/NFPA 70 with no other appliances or lights sharing the power. Use copper wire with THHN insulation. Do not use aluminum wire. Use the table on the next page to determine your GFCI and wiring requirements. Wire runs over 85 feet must increase wire gauge to the next lower number. For example: A normal 50 amp GFCI with four #8 AWG Copper wires run over 85 feet would require you to go to four #6 AWG copper wires.
_________________ -Kevin X-Pert Pool Service http://www.x-pertpool.com ----------------------------------- 22,000 gal / 16' x 32' / Vinyl liner pool Hayward s244t (300lbs.) with GlassPak Media [freebie] / Pentair SuperFlo 1 hp [freebie]
|
|
|
|
 |
|
PoolGuyNJ
|
Post subject: Re: Tinned copper?  Posted: December 1st, 2011, 10:30 am |
| Special Contributor |
 |
Joined: May 20th, 2007, 4:29 pm Posts: 3053 Location: South Central NJ
|
|
Also expect to need a common lead. Lights and other accessories on tubs are rarely 240V.
Scott
_________________ Owner of - PoolGuyNJ LLC Expert Pool and Spa Repairs, Renovations, and Augmentation. Helping people decide what is the right gear for meeting their needs. Expectations Set, Expectations Met, No Surprises.
|
|
|
|
 |
|
bk406
|
Post subject: Re: Tinned copper?  Posted: December 1st, 2011, 11:40 am |
Joined: December 3rd, 2009, 11:28 am Posts: 2423 Location: Central Massachusetts
|
PoolGuyNJ wrote: Also expect to need a common lead. That would be a neutral. Mx, how far is your tub from the panel? What are you going to run on your tub? Pump? Lights? heater? The power needs and distance will dictate what you need to run for wiring. Are you running the power from an exising subpanel outdoors? From Inside? More detail will help here.
_________________ 14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.
|
|
|
|
 |
|
mx702
|
Post subject: Re: Tinned copper?  Posted: December 1st, 2011, 6:30 pm |
Joined: August 2nd, 2010, 3:56 pm Posts: 157 Location: MA
|
PoolGuyNJ wrote: Also expect to need a common lead. Lights and other accessories on tubs are rarely 240V.
The tub is a Jacuzzi J-280 and there is no neutral required. bk406 wrote: Mx, how far is your tub from the panel? What are you going to run on your tub? Pump? Lights? heater? The power needs and distance will dictate what you need to run for wiring. Are you running the power from an exising subpanel outdoors? From Inside? More detail will help here. The run of wire from my 100A SWG/sub-panel to the tub is approximately 25 feet. Both are located outdoors. The tub is a totally self contained unit comprised of 3 pumps, heater and LED lighting. According to the owner's manual the max current draw with all the equipment running is 45A. The tub will protected by a 60 amp GFCI breaker I placed in the sub-panel. I ran 1" NM conduit through which to pull the wires.
_________________ Completed: June 2011 18' X 38' IG Vinyl, 3' - 8' depth ~ 24K gallons 2 skimmers, 2 wall suctions, 3 returns, 1.5" piping Hayward Equipment: 1HP Tri-star 2-speed, Aqua-Plus SWG, Star-Clearâ„¢ Plus 175 sqft cartridge filter, Colorlogic 4.0 LED The Pool Cleaner 4X(suction) 2011 Jacuzzi J-280 Hot tub
|
|
|
|
 |
|
bk406
|
Post subject: Re: Tinned copper?  Posted: December 1st, 2011, 7:29 pm |
Joined: December 3rd, 2009, 11:28 am Posts: 2423 Location: Central Massachusetts
|
|
Ok, you can use #6 stranded copper wire. Not sure why you want the tinned copper, its not needed.
Just go down to HD and get some black, red, and green #6. It'll be on roles back in the wiring section. Somebody will measure it off and cut it for you. Get several more feet than the 25 so you have enough to hook into the sub panel and at the tub.
Hopefully it wont be too stiff to pull through 1" conduit. For #6, you really want a bit bigger raceway, but you should get by with it.
_________________ 14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.
|
|
|
|
 |
|
mx702
|
Post subject: Re: Tinned copper?  Posted: December 1st, 2011, 8:42 pm |
Joined: August 2nd, 2010, 3:56 pm Posts: 157 Location: MA
|
bk406 wrote: Ok, you can use #6 stranded copper wire. Not sure why you want the tinned copper, its not needed. It's a cost saving exercise. There are several huge spools of large wire left over from construction of the power plant I work at. It's industrial, heavily insulated tray cable. I removed the the multiple layers of sheathing and extracted the wires. I just needed reassurance that it was allowed by code. Thanks. 
_________________ Completed: June 2011 18' X 38' IG Vinyl, 3' - 8' depth ~ 24K gallons 2 skimmers, 2 wall suctions, 3 returns, 1.5" piping Hayward Equipment: 1HP Tri-star 2-speed, Aqua-Plus SWG, Star-Clearâ„¢ Plus 175 sqft cartridge filter, Colorlogic 4.0 LED The Pool Cleaner 4X(suction) 2011 Jacuzzi J-280 Hot tub
|
|
|
|
 |
|
bk406
|
Post subject: Re: Tinned copper?  Posted: December 1st, 2011, 9:10 pm |
Joined: December 3rd, 2009, 11:28 am Posts: 2423 Location: Central Massachusetts
|
|
Well, I'm not sure what you have. Wire you stripped sheath off of may or may not be the right stuff. I DO know that #6 THHN/THWN stranded copper rated at 90 degrees C IS up to code. The ground wire needs to be insulted.
_________________ 14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.
|
|
|
|
 |
|
mx702
|
Post subject: Re: Tinned copper?  Posted: December 2nd, 2011, 7:54 pm |
Joined: August 2nd, 2010, 3:56 pm Posts: 157 Location: MA
|
|
The wires appear to have a PVC insulator encased in a nylon jacket.
_________________ Completed: June 2011 18' X 38' IG Vinyl, 3' - 8' depth ~ 24K gallons 2 skimmers, 2 wall suctions, 3 returns, 1.5" piping Hayward Equipment: 1HP Tri-star 2-speed, Aqua-Plus SWG, Star-Clearâ„¢ Plus 175 sqft cartridge filter, Colorlogic 4.0 LED The Pool Cleaner 4X(suction) 2011 Jacuzzi J-280 Hot tub
|
|
|
|
 |
|
|
 |
|
 |
|