    pool light and CGFI issue

    last year my pool light went out and I did not replace it (I have another pool light in the pool on other end and then a spa light). I did not replace it because never really swam at night.

    This year when I tried to turn on the lights all were not working. I checked the CGFI and the red test button pops every time I reset it and turn on the light switch. My question is would a dead bulb cause this to fault or could it be more serious? I was thinking of switching out the light bulb and replace gasket myself but beyond that I would need to call for help. I guess I'll find out when I replace the bulb but I was wondering if this is likely the cause now for the CGFI to trip. Thanks - Tom

  2. Back To Top    #2
    borjis's Avatar
    Join Date
    Aug 2014
    Location
    Pacific NW
    Posts
    2,058

    Re: pool light and CGFI issue

    Could be a number of things.

    I just went through this myself but it was a case of poorly done / improper wiring.

    to get started:

    do you have the light on a GFI breaker or is it a plugin GFI receptacle the light is fed from?
    16x32 IG Vinyl, 13,000 Gals. Hayward S-244T sand filter, SP2810X15 pump
    (1.5 HP motor) Raypak PR266AEN (266k btu) gas heater. TF-100 Test Kit.
    Dolphin E10 Cleaning Robot.

  3. Back To Top    #3

    Re: pool light and CGFI issue

    the CGFI breaker is on an outlet next to my control box that offers two 110V plugs. When I push the red button in and turn on the light on from the control box the red button pops out.

  4. Back To Top    #4
    borjis's Avatar
    Join Date
    Aug 2014
    Location
    Pacific NW
    Posts
    2,058

    Re: pool light and CGFI issue

    Three things come to mind:

    1. corrosion on the wiring

    2. bad gfci breaker - replace with a new one...return it if it too pops.

    3. moisture in the wiring from the pool to the junction box

    Not sure it would be the dead bulb causing but could be...maybe replace that first and a new gasket to start.

    with the niche pulled out on deck, maybe pull the bulb off, inspect the socket for moisture and if dry, try testing the gfci.
    16x32 IG Vinyl, 13,000 Gals. Hayward S-244T sand filter, SP2810X15 pump
    (1.5 HP motor) Raypak PR266AEN (266k btu) gas heater. TF-100 Test Kit.
    Dolphin E10 Cleaning Robot.

  5. Back To Top    #5

    Re: pool light and CGFI issue

    thanks for the ideas. I should mention that I plugged a hair dryer in the outlet and got it to work. Not sure if that means anything.

  6. Back To Top    #6
    borjis's Avatar
    Join Date
    Aug 2014
    Location
    Pacific NW
    Posts
    2,058

    Re: pool light and CGFI issue

    probably ignore #2 then.
    16x32 IG Vinyl, 13,000 Gals. Hayward S-244T sand filter, SP2810X15 pump
    (1.5 HP motor) Raypak PR266AEN (266k btu) gas heater. TF-100 Test Kit.
    Dolphin E10 Cleaning Robot.

  7. Back To Top    #7

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: pool light and CGFI issue

    Plain and simple, you have a voltage leak. Do you know what type of wire was used from the GFCI down to the deck box where the light is connected? (thwn, UF, NMb, etc). A burned out light bulb will not cause this.. Is there water in the light assembly on any of the lights? The wire in the conduit from the light to the deck box is rated wire for wet locations so I doubt the problem exists there.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  8. Back To Top    #8

    Join Date
    Jul 2014
    Location
    Peoria, IL
    Posts
    389

    pool light and CGFI issue

    I would start by checking each of your 3 lights to make sure that there is not water in them.

    From there you need to eliminate (disconnect) them from the circuit one at a time until the gfci breaker does not trip when switch is turned on. You have them isolated your bad wiring run/fixture.


    30x20 vinyl IG, Hayward SD60 with Pentair Dynamo 340219 2HP pump, Compupool CPSC24 SWG, Hayward H200FDN heater. APC automatic pool cover.