    Is proper ground wiring for pool light switch?

    Does using a wire nut to splice grounds in a pvc jbox with a run of the mill single pole switch an acceptable exception to the no splice code for pool light ground connections in 680.23(F)(2)(b)?

    See image below for an example of what I am describing where the top image shows doing so with wire nut in switch jbox and the lower image shows a configuration that home run the ground to the panel then back to the switch.

    So is the easiest way a home run to the panel then wire a separate ground to the switch jbox? If the answer is no the wire nut and splice, why would a timer or "snap switch" be different than a wire nut inside the single pole switch jbox?

    The lines are 12AWG THHN/THWN in 1" gray pvc conduit. I can provide more detail about the rest of the configuration but usually when I type too much no one looks at them


    Location: Western PA
    Attached Images Attached Images
    18x36 IG Steel Wall Vinyl 25K gallon 3.5-8ft, Hayward 4820 DE Filter, Hayward 1HP Super Pump, Hayward 250K BTU NG heater, Zodiac Baracuda MX8 Cleaner, 4 jets (steps/deep), 1 return
    30 mins North of Pittsburgh Pennsylvania

  2. Back To Top    #2

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Is proper ground wiring for pool light switch?

    Wire nuts in an approved junction box are fine. The no splice is for the run of wire from the deck box down to the light. Actually, the no splice rule is in effect for any wire outside of an approved junction box
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  3. Back To Top    #3

    In the Industry

    Join Date
    Mar 2011
    Posts
    441

    Re: Is proper ground wiring for pool light switch?

    That is not true the code clearly says..


    2) Equipment Grounding. The branch-circuit conductors to an underwater luminaire shall contain an insulated copper equipment grounding conductor. The equipment grounding conductor shall not be smaller than 12 AWG and it shall be without splice, except as permitted in (a) or (b). Figure 680-16 un680-16 680-23F2 01.cdr
    (a) If more than one underwater luminaire is supplied by the same branch circuit, the equipment grounding conductor shall be permitted to terminate to a listed pool junction box that meets the requirements of 680.24(A).
    (b) The equipment grounding conductor shall be permitted to terminate to the grounding terminal of a listed pool transformer that meets the requirements of 680.23(A)(2).

    Can you do it and get away with it, yes, 99% of the installations likely do this.
    20X40 30,000 gallon gunite pool

  4. Back To Top    #4

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Is proper ground wiring for pool light switch?

    I stand corrected, The connections need to be under a termination screw in the deck box. Don't recall ever seeing any done this way, but I don't work on may of these either. I will have to keep an eye out for this.

    I really need to stop goofing off while in meetings at work
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  5. Back To Top    #5
    Mod Squad pooldv's Avatar
    Join Date
    Aug 2012
    Location
    DFW, TX
    Posts
    23,999

    Re: Is proper ground wiring for pool light switch?

    Really? I don't want to. Work is overrated!
    TFP Moderator
    If TFP helped you or saved you money - Become a TFP Supporter! <--Click here
    2012 build and pics, 20k gal gunite, black onyx pebblesheen, OK flagstone, IntellifoVS, cart filter w/Pleatco, IC40 SWG, Solartouch, 5 12'x4' solar panels, HP50HA heat pump, 8mil solar cover, borates, TF-100 test kit, SONOS, Doheny's Discovery Robot, hot tub on bleach

  6. Back To Top    #6

    Re: Is proper ground wiring for pool light switch?

    Thank you all for the replies. I am starting to think that the 99% doing it wrong but getting away with it is correct since I've asked this question numerous times in different forums over the years and keep getting no 100% agreement. Thanks again. What I amp contemplating if I need to contact my contractor to repull the ground or not.
    18x36 IG Steel Wall Vinyl 25K gallon 3.5-8ft, Hayward 4820 DE Filter, Hayward 1HP Super Pump, Hayward 250K BTU NG heater, Zodiac Baracuda MX8 Cleaner, 4 jets (steps/deep), 1 return
    30 mins North of Pittsburgh Pennsylvania

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •