    Waterfall Suction Piping Location

    Does anyone have any suggestions on the best place to put my waterfall suction pipe? Right now I have it located just to the left of the waterfall. However, someone on this forum kindly pointed out that I should move it closer to the pump pad, and I agree. Now I'm just trying to figure out the best place.

    I'm thinking about putting it on the left or right side of the bench on the deep end (far right side), or would that be too close to the skimmer/returns? Or maybe between the light and the slide? Any reasons for picking one spot over another?

    I will have a dedicated Intellipro VS pump for the waterfall. The loop will NOT run through the filter or SWG. Suction pipe is 2.5". Return is 2". Thanks for any suggestions!


  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Waterfall Suction Piping Location

    You want it close to the equipment pad, and in an area where people are the least likely to interact with it.

    Remember that the waterfall suction needs to be dual (or long slot), same as the main drain.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3
    Matchless1's Avatar
    Join Date
    Jul 2014
    Location
    Baton Rouge, LA
    Posts
    254

    Re: Waterfall Suction Piping Location

    Quote Originally Posted by JasonLion View Post
    Remember that the waterfall suction needs to be dual (or long slot), same as the main drain.
    Could please explain a bit more what you mean by "dual (or long slot), same as the main drain"?

  4. Back To Top    #4
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Waterfall Suction Piping Location

    Main drains and wall suction ports always need to be designed to prevent entrapment. Entrapment is when the pump suction traps a person against the suction port. There are various ways to design the system to prevent this, but the nearly universal choice is to place two drains connected together at least three feet apart. The next most common solution is to use a slot that is more than three feet long. There are several other approaches allowed, but they quickly get more expensive and less practical.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  5. Back To Top    #5
    Matchless1's Avatar
    Join Date
    Jul 2014
    Location
    Baton Rouge, LA
    Posts
    254

    Re: Waterfall Suction Piping Location

    Ok, that makes perfect sense. Thanks for pointing that out. In that case, I suppose it makes the most sense to put it between the light and the slide (out of the way and plenty of room for 3 feet of separation). Does this look about right? Any issues with Return #2 being right there?



  6. Back To Top    #6
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Waterfall Suction Piping Location

    Looks good.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School