    Bond wire connection to pump motor..where is it?

    I have a bond wire coming out of the concrete floor in the pool pump room next to the return pvc pipe.

    It's not attached to the pump motor.

    Does anyone know where on the motor I should attach the bond wire?
    16x32 IG Vinyl, 13,000 Gals. Hayward S-244T sand filter, SP2810X15 pump
    (1.5 HP motor) Raypak PR266AEN (266k btu) gas heater. TF-100 Test Kit.
    Dolphin E10 Cleaning Robot.

  2. Back To Top    #2
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Bond wire connection to pump motor..where is it?

    There should be a lug on the outside of the motor case to attach the bond wire.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  3. Back To Top    #3

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Bond wire connection to pump motor..where is it?

    Some motors do not have them. Check to see if it is a double insulated motor. It should say it on the data plate. If it is, then it does not get bonded.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  4. Back To Top    #4
    borjis's Avatar
    Join Date
    Aug 2014
    Location
    Pacific NW
    Posts
    2,058

    Re: Bond wire connection to pump motor..where is it?

    If I don't see a bond wire lug and or it's double insulated, then does that mean there is no potential shock risk?
    16x32 IG Vinyl, 13,000 Gals. Hayward S-244T sand filter, SP2810X15 pump
    (1.5 HP motor) Raypak PR266AEN (266k btu) gas heater. TF-100 Test Kit.
    Dolphin E10 Cleaning Robot.

  5. Back To Top    #5

    Re: Bond wire connection to pump motor..where is it?

    The SuperPump usually has a bonding lug on the motor. Can you post a picture?

  6. Back To Top    #6

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Bond wire connection to pump motor..where is it?

    Quote Originally Posted by borjis View Post
    If I don't see a bond wire lug and or it's double insulated, then does that mean there is no potential shock risk?
    It is not that simple.

    Bonding is the act of connecting all metal items around the pool and the ground it is built on/in together to bring them all into the same electrical potential. This reduces/eliminates shock potential from differing voltage gradients. This has nothing to do with the electrical supply system to the pool equipment.

    Grounding is a completely different science from bonding. Grounding is the act of bringing any fault voltage back to the source that the electricity was derived from. A properly connected ground wire back to the panel box and ultimately back to the center tap on the street transformer is what will clear a fault (trip the breaker) and protect you from a shock. Unfortunately, this may be a slow process or not happen at all if the Amp draw is not high enough to trip the breaker. This is where GFCI protection comes into play. This is what will ultimately protect you as the trip threshold for a GFCI is purposely set to be below the threshold determined to cause death.

    A double insulated motor under normal circumstances will not carry a voltage potential on the case, thus not needing to be bonded
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  7. Back To Top    #7
    Mod Squad JohnT's Avatar
    Join Date
    Apr 2007
    Location
    SW Indiana
    Posts
    9,089

    Re: Bond wire connection to pump motor..where is it?

    Typically on a Superpump, the bonding lug is on the motor flange that is on the top left as you look at the pump from the wet end. Closest to the R in Hayward. This flange is a little bigger than the rest and has two holes in it. The smaller hole is the one the bonding lug mounts in.
    TFP Moderator
    20K Gallon 20X36 Vinyl Inground
    Hayward S244T Sand Filter with 1HP Whisperflo Pump. Liquidator C-201 and Solar Heat

  8. Back To Top    #8
    borjis's Avatar
    Join Date
    Aug 2014
    Location
    Pacific NW
    Posts
    2,058

    Re: Bond wire connection to pump motor..where is it?

    Found it. It was at 12 o'clock on the pump motor, near where it mounts to the pump housing.

    copper square thing with a grub screw.

    I cleaned that inside and out as well as the bonding wire to a shiny copper finish
    then attached it to the bonding lug.

    thanks!
    16x32 IG Vinyl, 13,000 Gals. Hayward S-244T sand filter, SP2810X15 pump
    (1.5 HP motor) Raypak PR266AEN (266k btu) gas heater. TF-100 Test Kit.