    Too many amps on one breaker?

    I'm in the middle of installing an Intermatic PE635 automation system. The instructions call for the spa blower to be connected to the breaker for the main pool pump. This is necessary because of the way Intermatic does the wiring for their control system. In the past, the blower was on a separate breaker, but that is no longer an option if I want to use the automation to control the blower. I'd like to hook the following up to the main pump breaker:

    1) Spa blower - as stated above, I have no choice if I want the blower controlled by the automation system. Amp draw: 4 amps
    2) Main pool pump - Amp draw: 11.5 amps
    3) Stenner Pump - don't I also want this connected to the main pump breaker as I don't want the Stenner to operate if the pump is not running?? Amp draw: 1.7 amps
    4) Raypak RP2100 heater - this was hooked up to the pump breaker originally. I'm assuming it should be connected to the main pool pump breaker also as you don't want the heater to run if the pool pump is not running. This is a propane gas heater and I'm assuming the amp draw is small, but I can't find the amp draw for this device. This information is not contained in the instruction manual and I have not been able to find it on line.

    My main pump breaker is 20 amp and with this setup I'll have 17.2 amps plus whatever the heater is. Is this too much on that breaker?

    If it is too much, any suggestions on what I move to another breaker? I'm thinking my only option would be the Stenner, but that does not remove very much amp draw?

    Suggestions?
    30,000 plaster in-ground pool with spa; 2.5HP single speed Centurion pump; Raypak RP2100 propane heater; Polaris 280 with pump, waterfall with separate pump, Triton II commercial sand filter; TF-100 test kit w/ SpeedStir

  2. Back To Top    #2
    Divin Dave's Avatar
    Join Date
    Oct 2013
    Location
    Longview, Texas
    Posts
    4,926

    Re: Too many amps on one breaker?

    Hi, hopefully one of the more experiened electrical guys will chime in. I dont know if all of those items on a breaker like you explain is the thing to do or not without actually seeing all of it.

    But, in the event it is ok, why cant you just install a bit larger breaker in place of the 20?
    Divin Dave,
    IG Vinyl, 15' x 30', 3 1/2' - 6' deep, Oval, ~15K gal, Intelliclor IC40, Intelliflo VS pump, Clean and Clear 420 Filter, auto-fill-disabled, Retrofit LED Color Light, Dolphin Nautilus Robot, TF100 Test Kit, Taylor K1766 Salt Test Kit, Tftestkit Pressure Gauge.
    www.tftestkits.net Experience- it's what's learned just after you needed it most !!

  3. Back To Top    #3

    Join Date
    Nov 2013
    Location
    Fort Worth, TX
    Posts
    112

    Re: Too many amps on one breaker?

    Quote Originally Posted by Divin Dave View Post
    Hi, hopefully one of the more experiened electrical guys will chime in. I dont know if all of those items on a breaker like you explain is the thing to do or not without actually seeing all of it.

    But, in the event it is ok, why cant you just install a bit larger breaker in place of the 20?
    I thought of that, but I'd have to go to a 30AMP breaker and all the wiring is 12 gauge which I don't believe is large enough to carry that current? Also, my breaker box is limited to 80AMP and I'm there now. I do have one 20AMP breaker that only has a waterfall/fountain on it.
    30,000 plaster in-ground pool with spa; 2.5HP single speed Centurion pump; Raypak RP2100 propane heater; Polaris 280 with pump, waterfall with separate pump, Triton II commercial sand filter; TF-100 test kit w/ SpeedStir

  4. Back To Top    #4
    Richard320's Avatar
    Join Date
    Jan 2010
    Location
    San Dimas, CA (LA County)
    Posts
    18,768

    Re: Too many amps on one breaker?

    Have you considered using the controller to just power relays, leaving the actual loads on their respective circuits?
    16K freeform gunite with spa; Pentair 4000 DE filter; Century Whisperflow 1 HP; Pentair Minimax heater.
    Troublefree does not mean Maintenancefree. It's like brushing your teeth: You can spend a couple minutes a day and pennies a week or go to the dentist once a year and spend several thousand dollars.
    A pool is like a pet - you have to feed it every day, even the days you don't want to play with it!

  5. Back To Top    #5
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Too many amps on one breaker?

    Raypak heaters tend to be very low current draw. I suspect that everything will just work on one breaker.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  6. Back To Top    #6

    Join Date
    Jan 2013
    Location
    Friendswood, TX
    Posts
    320

    Re: Too many amps on one breaker?

    Breakers are only supposed to be loaded to 80% of the listed rating I believe.

    Not knowing what type of wire they used (assuming UF-B) it is rated at 20 amps.

    You can't increase the breaker above 20 without pulling new wires.
    ~Paul
    19x40 IG including 10' BE, 18,000 gal, plaster, 48 SF DE, 1.5HP pump, AquaPure SWCG, Ozonejoe 30MR, Rockwaterfall, LED light, TF-100 Fill date 11/21/2014
    My ODK Build | My Pool Build | If You're From Texas Vote Here

  7. Back To Top    #7

    Join Date
    Nov 2013
    Location
    Fort Worth, TX
    Posts
    112

    Re: Too many amps on one breaker?

    Quote Originally Posted by Richard320 View Post
    Have you considered using the controller to just power relays, leaving the actual loads on their respective circuits?
    Richard,

    Thanks for your suggestion. I have a vague understanding of what you are talking about. Can you elaborate? What type of relay would I need? I assume I would need to either put the relay/relays in another box or install them somewhere in my existing box?

    Thanks!
    30,000 plaster in-ground pool with spa; 2.5HP single speed Centurion pump; Raypak RP2100 propane heater; Polaris 280 with pump, waterfall with separate pump, Triton II commercial sand filter; TF-100 test kit w/ SpeedStir

  8. Back To Top    #8
    Richard320's Avatar
    Join Date
    Jan 2010
    Location
    San Dimas, CA (LA County)
    Posts
    18,768

    Re: Too many amps on one breaker?

    Quote Originally Posted by Billrector View Post
    Richard,

    Thanks for your suggestion. I have a vague understanding of what you are talking about. Can you elaborate? What type of relay would I need? I assume I would need to either put the relay/relays in another box or install them somewhere in my existing box?

    Thanks!
    Actually, I can't. My electrical expertise is pretty well confined to DC automotive circuits. But I do know there are relays for industrial use, which is how a normal lightswitch can turn on hundreds of fluorescent lights. I think google or a certified electrician would be your best bet with specifics.
    16K freeform gunite with spa; Pentair 4000 DE filter; Century Whisperflow 1 HP; Pentair Minimax heater.
    Troublefree does not mean Maintenancefree. It's like brushing your teeth: You can spend a couple minutes a day and pennies a week or go to the dentist once a year and spend several thousand dollars.
    A pool is like a pet - you have to feed it every day, even the days you don't want to play with it!

  9. Back To Top    #9

    Re: Too many amps on one breaker?

    There has to be a way to put them on separate breakers.... What if the spa blower goes bad? Itll shut everything down. Same goes for the heater. same goes for the stenner... The pool heater should have a pressure switch to shut itself down when the pump turns off, although having your automation system tell it to shut down and let the pump run for a few to help cool it down is the ideal situation and let the pressure switch be the backup.

  10. Back To Top    #10
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Too many amps on one breaker?

    The Intermatic PE635 has five switches in three groups: the first pair of switches must share a circuit, the second pair of switches must share a circuit (allowed to be different from the one used by the first pair), and the final switch can have it's own circuit. The final switch can be setup as low voltage or line voltage. The first four are all line voltage.

    Unless you have some other equipment you haven't mentioned there shouldn't be any problem having the blower on it's own circuit breaker.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  11. Back To Top    #11

    Join Date
    Nov 2013
    Location
    Fort Worth, TX
    Posts
    112

    Re: Too many amps on one breaker?

    Quote Originally Posted by JasonLion View Post
    The Intermatic PE635 has five switches in three groups: the first pair of switches must share a circuit, the second pair of switches must share a circuit (allowed to be different from the one used by the first pair), and the final switch can have it's own circuit. The final switch can be setup as low voltage or line voltage. The first four are all line voltage.

    Unless you have some other equipment you haven't mentioned there shouldn't be any problem having the blower on it's own circuit breaker.
    Hi Jason,

    Thanks for your comment. Regarding the 5 circuits in the Intermatic PE635, I have the system configured as follows:

    1) Single speed pool pump
    2) Spa blower
    3) Polaris 280 booster pump
    4) P4043 valve actuator to control 2 valves
    5) Heater - low voltage to control heater thermometer remotely

    In addition, I have the following equipment that currently I can't control with the PE635:
    1) Stenner pump - I plan to add another timer in my open box (P7103ME I'm thinking) and power it with 120V with one leg from Circuit one of the PE635
    2) Waterfall - I have a separate pump running a waterfall that currently is controlled by a wall switch and it looks like it will have to stay that way!
    3) My pool and spa lights will also stay on wall switches unless I can figure out how to automate them using the Z-wave.

    Based on the above, I don't see how I can move the blower off of a shared circuit with the main pump, the Stenner pump, and the heater?

    Appreciate everyone's help!
    30,000 plaster in-ground pool with spa; 2.5HP single speed Centurion pump; Raypak RP2100 propane heater; Polaris 280 with pump, waterfall with separate pump, Triton II commercial sand filter; TF-100 test kit w/ SpeedStir

  12. Back To Top    #12
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Too many amps on one breaker?

    Indeed, quite a bit more equipment. If you want to control all of that remotely you need something fancier than the PE635.

    Assuming the Stenner is 120 volts and the pump is 240 volts, you don't want to put the Stenner on one leg of the pump circuit. If you have a GFI breaker, which is required by recent versions of the electrical code, having the Stenner on one leg will trip the breaker any time the Stenner comes on. If they both operated at the same voltage there wouldn't be a problem.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  13. Back To Top    #13
    dumbcluck's Avatar
    Join Date
    Aug 2013
    Location
    long beach
    Posts
    670

    Re: Too many amps on one breaker?

    a breaker supplies constant power.
    it is the automation that controls when it gets or doesn't get power.
    no need to share if amps are too high. 16 is really max for a 20a circuit.
    heater usually needs flow to turn on so wouldn't turn on without pump normally. why not put heater and blower on same circuit? they will probably be coming on together anyway but only if pump is running I would guess.
    these things could all easily be controlled with proper relay setup.
    Jason is right, you cant steal one leg from a 220v circuit for 120v power. you need a separate circuit and also a neutral.
    any photos of your current setup would help.
    -Jimbo- My pool was full of dirt and trees. Now it's full of water and children!
    20k gallon inground pool, 18" raised spa 7' round, 8 jets, 3" spa plumbing. Pentair intelliflo 3hp vsp, Easy touch 4 w/ ic 40, CCP 420 cartridge filter, Raypak 407a w/ cupro nickel, Screen logic 2, Pentair intelliph, spa side remote, Pentair 5g color lights pool and spa, TF-100 test kit with speed stir and Dolphin Oasis Z5

  14. Back To Top    #14

    Join Date
    Nov 2013
    Location
    Fort Worth, TX
    Posts
    112

    Re: Too many amps on one breaker?

    Here is a picture of my current project as well as a schematic.
    Attachment 34039

    IMG_0748.jpg

    I've given this some more thought and am wondering if the following will work:

    All equipment per schematic. Add a 240V relay which will be triggered by the pool pump switch and a 120V 7-day timer to run the Stenner pump (also 120V). This would enable the Stenner to run when both the timer and pool pump are active.

    Replace the existing toggle switches for the pool and spa lights with Z-wave switches so that I can control them from the Intermatic remote. These are 120V which should be easy to find, but I'm not sure about having them in an outdoor weatherproof enclosure like they are in now and what that will do to the Z-wave signal?

    If I can find one, replace the toggle switch to run the waterfall. This has to be 240V and again would be in a weatherproof box....again, signal issues?

    If I can do all this, I will be able to automate ALL of my equipment!!! That would be awesome!

    Comments and suggestions welcome!

    Like the schematic shows with
    30,000 plaster in-ground pool with spa; 2.5HP single speed Centurion pump; Raypak RP2100 propane heater; Polaris 280 with pump, waterfall with separate pump, Triton II commercial sand filter; TF-100 test kit w/ SpeedStir

  15. Back To Top    #15
    dumbcluck's Avatar
    Join Date
    Aug 2013
    Location
    long beach
    Posts
    670

    Re: Too many amps on one breaker?

    Its hard to see on my phone but it looks like you want to share legs from different circuits. No. You cannot borrow power from another source to make up your own 220. This will cause major problems.
    If I'm seeing it wrong sorry.