Raypak RP2100 digtal pool heater

Sep 26, 2014
8
toledo ohio
I'm working on a raypak Rp2100 digtal unit with a pilot.it's sparks pilot comes on you here the gas valve open but has no gas coming out of the test tap. i have already replaced the gas valve still the same thing, but when the flame shows on the front panel you only see one of the flames flashing.
 
Is this natural or LP? Did you confirm that you have a pilot light before the gas valve main opens/clicks? Have you tested the gas pressure coming into the unit?
 
OK. What gas valve did you install on the unit? With no gas pressure on the manifold side of the valve can mean either the gas valve is locking up or not enough pressure. 7"WC should be enough incoming.
 
OK so you got a direct replacement valve. What is the gas pressure on the manifold side? There is a test spot on the valve that you can hook into. Curious to know what that reading is since you have 7" coming into the valve, what is the valve passing thru it. How does the inside of the heater look? Burners look OK?
 