    Re: Stray Voltage

    I am having the same exact issues. Basic facts. In ground pool, saltwater , vinyl liner, only metal is pool lights and rebar in concrete deck. I am reading 500 millivolts from water to earth as ground. I get a serious tingle and sometimes a shock when my feet are wet on the concrete and finger in pool. Take feet off concrete and it's nothing. Power company disconnected completely including their neutral, along with catv and phone. Still feel tingle, still read 500 millivolts. All power to my home disconnected including my own neutral, still exists. Old owner had same issue and chose to ignore it. I'm told the pool is properly bonded, but who knows. Can anyone please help

  2. Back To Top    #2
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Stray Voltage

    Well clearly the pool is not properly bonded or you would not feel anything.

    Of course then there is still the problem of the source which may not even be on your property.

    You need 2 failures to experience what you are feeling.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  3. Back To Top    #3

    Join Date
    Sep 2014
    Location
    New York
    Posts
    3

    Re: More Stray Voltage.

    Agreed. My thought however is not to find the stray voltage but to create an equipotential plane. How can I get my deck to be the same potential as the water and will that work? I'm not an electrician by any means, but wouldn't that have to work?

  4. Back To Top    #4
    MBG75's Avatar
    Join Date
    Jun 2013
    Location
    Long Island
    Posts
    184

    Re: Stray Voltage

    Are there any handrails or ladders?

    You could run a temporary bond wire into the water and see if the voltage goes away.
    25k IG vinyl SWG Haywood 4830de 1.5hp TF-100

  5. Back To Top    #5

    Join Date
    Sep 2014
    Location
    New York
    Posts
    3

    Re: More Stray Voltage.

    We plan to do that this weekend.