    gfi breaker keeps jumping

    The GFI breaker has recently has been jumping lately. Whenever the heater kicks in a few minutes later the breaker jumps and one if the leads coming from the breaker gets hot and smokes a little. Here is a picture of the lead . I tested the breaker with a volt meter. 117 volts from each hot lead to ground and 234 from hot lead to hot lead so it appears to be working properly. I checked all the wiring for shorts and no luck. I also poked around the wiring looking for one the may be hot which was not the case. I even pulled the filter figuring that maybe the pump was working to hard. Any ideas for trouble shooting?

  2. Back To Top    #2
    Isaac-1's Avatar
    Join Date
    May 2010
    Location
    SW Louisiana
    Posts
    6,711

    Re: gfi breaker keeps jumping

    If the wire is getting hot enough to smoke then whatever is connected to it is drawing too many amps and the breaker is doing its job as a conventional breaker would and disconnects the load due to too high of amp draw. You likely need to get a professional service person there to check out the heater.
    Indoor 20x40 35,000 gallon vinyl pool with 1.5 HP 2 speed Jandy FloPro pump, Hayward EC75 Perflex DE filter, 11 4x12 Techno-Solis solar panels w/ Aquasolar controller, Aquabot Turbo T Robot Cleaner. Also LMI metering chlorine dispenser pump and HotSpring Jetsetter
    I use and endorse TFtestKits TF-100 from http://tftestkits.net
    ~Remember TFP counts on your donations to keep this site ad free~

  3. Back To Top    #3

    Join Date
    Jul 2014
    Location
    Hope Mills, NC
    Posts
    555

    Re: gfi breaker keeps jumping

    "Smoking" and "hot" are 2 terms you NEVER want associated with electricity. Unless you want to burn your house down and possibly kill your family...GET IT FIXED...RIGHT NOW.

    I am not kidding...that is really bad.
    16 x 32 17500 gallons
    Vinyl in-ground
    Hayward 250# Sand Filter
    1 HP Pump
    Hayward SWG

  4. Back To Top    #4

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: gfi breaker keeps jumping

    The real question is, where is this breaker located? It shouldn't have a bunch of things connected to it like the lights. Heater and such should be a dedicated breaker and it doesn't need to be GFCI. So where is this breaker at? Maybe a better picture of the entire inside of the box would help us identify the issue.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  5. Back To Top    #5

    TFP Guide

    Kiss4aFrog's Avatar
    Join Date
    May 2013
    Location
    Hudson, WI
    Posts
    2,602

    Re: gfi breaker keeps jumping

    That breaker looks to be damaged as the screw for the "Load Power" red wire seems to have been fatally overheated, it's moved off center and the metal beneath the screw seems discolored from heat. The plastic body of the breaker is likely also distorted and the breaker should be replaced.
    Apparently according to code it doesn't need to be a GFI breaker but it's always nice to have a little added protection.
    It sounds like you have a short in the heater and it's drawing way too many amps through the circuit. You know there is a problem so it's time to quit resetting the breaker as you are literally gambling each time you reset it that something severe doesn't occur.
    '70s IG Vinyl 32K gal, Lazy L, Hayward SuperPump 1.5hp 120V, S240 Sand Filter W/DE
    Solar Blanket, Well Water, Borax Added, TF-100 tester. ? too cold
    1979, 275gal Conway Emerald Spa P-100-2, ES-2 Spa Pack, bromine floater, indoor
    TF-100, Best test kit - TFTestkits.net
    Please help keep the lights on, become a TFP Supporter!

  6. Back To Top    #6

    Join Date
    Apr 2014
    Location
    Canada
    Posts
    18

    Re: gfi breaker keeps jumping

    Quote Originally Posted by ps0303 View Post
    The real question is, where is this breaker located? It shouldn't have a bunch of things connected to it like the lights. Heater and such should be a dedicated breaker and it doesn't need to be GFCI. So where is this breaker at? Maybe a better picture of the entire inside of the box would help us identify the issue.
    Here is the picture of the panel. Only the tub is connected to it.

    [IMG][/IMG]


    I haven't replaced the breaker yet as I wanted to do some quick amp reading as I now own an clamp meter and want to confirm the correct amp breaker first. On the side of the circuit panel it says 32 amp 240v 60hz (current gfci breaker is 50 amp). I only turned power on for a few seconds to be able to record some data.

    Results...

    Red and black wire on the load side of the breaker with the heater on:
    Pump on High:
    Red 32 amps
    Black 29.8 amps

    Pump on Low:
    Red 24.7 amps
    Black 23.3 amps

    Both leads at the heater: 21.8 on one side and 21.5 on the other

    At the pump:
    Low (red wire) speed 3.9 amps
    High (black wire) speed 9.5 amps

    Testing the heater with the power off using a multi meter I was getting around 11 amps.

    Can a conclusion be made from these results?

  7. Back To Top    #7

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: gfi breaker keeps jumping

    Need more info. What is your entire setup? Do you have a pool, spa, one pump or two. So that's the only panel you have feeding ALL of your equipment?

    Please give us some more info.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  8. Back To Top    #8

    Join Date
    Apr 2014
    Location
    Canada
    Posts
    18

    Re: gfi breaker keeps jumping

    It's a hot tub. Two pumps. One is a circ pump and the other is a high low speed pump which runs during heating, filtration cycle and to work the jets. As for the panel there is a direct line of 6-3 wire from the panel inside to a panel outside the house as seen in the picture. The panel outside has the gfci and only the hot tub is connected to it.

  9. Back To Top    #9

    Join Date
    Apr 2014
    Location
    Canada
    Posts
    18

    Re: gfi breaker keeps jumping

    It's a hot tub. Two pumps. One is a circ pump and the other is a high low speed pump which runs during heating, filtration cycle and to work the jets. As for the panel there is a direct line of 6-3 wire from the panel inside to a panel outside the house as seen in the picture. The panel outside has the gfci and only the hot tub is connected to it.

  10. Back To Top    #10

    Join Date
    Jul 2014
    Location
    Hope Mills, NC
    Posts
    555

    Re: gfi breaker keeps jumping

    At least your fire will be confined to the box...
    16 x 32 17500 gallons
    Vinyl in-ground
    Hayward 250# Sand Filter
    1 HP Pump
    Hayward SWG

  11. Back To Top    #11
    n240sxguy's Avatar
    Join Date
    May 2014
    Location
    Benton, KY
    Posts
    1,800

    Re: gfi breaker keeps jumping

    My stab in the dark at this is maybe that lug was over torqued and damaged the electrical connection inside the breaker. After heat cycling so many times it has finally worn down enough that there is only a small connection between the lug and the inside of the breaker, and it isn't capable of handling that kind of current. It gets super hot which eventually trips the thermal circuit. It could also just be at the end of its life. Breakers do wear out. I just replaced the main breaker in my subpanel that feeds my garage, an A/C, and the pool. It was getting hot and tripping. No other breaker was remotely warm, but that one was super hot. Replaced it, and now everything works as it should. I vote replace the breaker ASAP.
    30K gallon IG vinyl. 1.5HP 2-speed Waterway Mustang pump. 600 lb sand filter. Polaris 280. Circupool SI-60+. TF-100

  12. Back To Top    #12

    Join Date
    Apr 2014
    Location
    Canada
    Posts
    18

    Re: gfi breaker keeps jumping

    I do agree with replacing the breaker asap. I haven't yet as I would like to make sure I have the right amperage breaker based on the data that I previously posted since they are expensive. I am currently using 50 amp.

  13. Back To Top    #13
    Mod Squad tim5055's Avatar
    Join Date
    May 2014
    Location
    Columbia, SC
    Posts
    8,494

    Re: gfi breaker keeps jumping

    Quote Originally Posted by bandito View Post
    I do agree with replacing the breaker asap. I haven't yet as I would like to make sure I have the right amperage breaker based on the data that I previously posted since they are expensive. I am currently using 50 amp.
    Breakers are really sized for the wire, not the load. Now, in a perfect world the wire is sized to the load.

    You can put a smaller breaker in there as it would afford greater protection to the wire, but only put a larger breaker in if the wire is properly sized for the rating of the breaker.

    You can't just put in a larger breaker if you calculate you have a larger load because the wire is weak link and will fail before the breaker trips.
    TFP Moderator 39 X 18 23,000(ish) freeform gunite; built 2007ish; Pentair Triton II TR100 600lb Sand filter; 2 HP Pentair pump with 2.2 HP AO Smith single speed motor; 2 skimmers, 1 main drain, 4 returns w/waterfall, Stenner 45MHP2 3GPD running@ 60% - 15 gal Tank; heated by the sun CYA 200+ when I started - 50 now. Dolphin Supreme M5 Pool Cleaner. Hot Springs SX Spa, 285 gallon

  14. Back To Top    #14
    n240sxguy's Avatar
    Join Date
    May 2014
    Location
    Benton, KY
    Posts
    1,800

    Re: gfi breaker keeps jumping

    Yep. Size the breaker for the wire. Also, get a price on a breaker from a couple electrical supply houses. They have the potential to be a whole lot cheaper. I used to order from North American breaker to fill orders for customers. Maybe call them and see if anyone in the area has an account with them. All but square d homeline were cheaper from them. Lowes had some special contract with square d to get super pricing.
    30K gallon IG vinyl. 1.5HP 2-speed Waterway Mustang pump. 600 lb sand filter. Polaris 280. Circupool SI-60+. TF-100

  15. Back To Top    #15

    Re: gfi breaker keeps jumping

    I'm assuming your 11 amp reading with power off was 11 ohms?
    That is correct for a 5kW heater. More importantly I would test ohms from each leg of heater to ground.

    I'm guessing your meter error was responsible for the unequal heater amp readings 21.8 vs 21.5.

    Did you test the line side voltage in the panel vs the load side voltage on the breaker?

    Question I have is, what's the couple amp difference in L1 vs L2 red/black? Is the difference showing up on the neutral line amp reading as well?
    What is drawing that many amps?
    Hopefully not the transformer or control board which is likely 120v. Maybe an ozonator?

    BTW, NM-B wire is not rated for outdoor use, or wet locations.
    24k gallon inground vinyl liner pool, 8'-3' depth, 2 skimmers, 3 returns, basic 5 chem kit.
    Hayward: DE-60 filter, Superpump VS, AquaRite salt chlorinator w/T-Cell 15, TigerShark QC robot. Jacuzzi hot tub ~350gal. Air blower type, w/8 jets.

  16. Back To Top    #16

    Join Date
    Apr 2014
    Location
    Canada
    Posts
    18

    Re: gfi breaker keeps jumping

    I replaced the breaker with a 40 amp as specified in the manual and after 6 hours runs perfect. No wires are getting hot. I had put the original breaker in during the winter and I think it cracked a bit when I tighten the screw.

  17. Back To Top    #17

    TFP Guide

    Kiss4aFrog's Avatar
    Join Date
    May 2013
    Location
    Hudson, WI
    Posts
    2,602

    Re: gfi breaker keeps jumping

    Glad you're up and running again

    Quote Originally Posted by tim5055 View Post
    Breakers are really sized for the wire, not the load. Now, in a perfect world the wire is sized to the load.

    You can put a smaller breaker in there as it would afford greater protection to the wire, but only put a larger breaker in if the wire is properly sized for the rating of the breaker.

    You can't just put in a larger breaker if you calculate you have a larger load because the wire is weak link and will fail before the breaker trips.
    In my world the circuit breaker is never chosen or sized according to the wire. Someone posted something like this once before. You choose a circuit breaker depending on the load on the line and only the load. Same with the wire, the wire size is chosen depending on the load on the circuit and the distance of the run. In a perfect world the person making the buying decision picks a circuit breaker close to what's recommended for the load and goes a size bigger than what's recommended on the wire.

    There is no benefit in going bigger on the circuit breaker as it only allows the device to pull more amps than it should. That extra amperage is usually being turned into heat and with enough of it you get smoke and then fire. If you put in a bigger circuit breaker because the wire can handle more amps due to it being over sized for the load you simply put the electrical device at risk of massive failure including smoke, fire and explosion as it's not being protected at the proper level.
    '70s IG Vinyl 32K gal, Lazy L, Hayward SuperPump 1.5hp 120V, S240 Sand Filter W/DE
    Solar Blanket, Well Water, Borax Added, TF-100 tester. ? too cold
    1979, 275gal Conway Emerald Spa P-100-2, ES-2 Spa Pack, bromine floater, indoor
    TF-100, Best test kit - TFTestkits.net
    Please help keep the lights on, become a TFP Supporter!

  18. Back To Top    #18

    Join Date
    Apr 2014
    Location
    Canada
    Posts
    18

    Re: gfi breaker keeps jumping

    Well said! I also may have broken the original breaker when installing it in the freezing cold.

  19. Back To Top    #19
    Mod Squad tim5055's Avatar
    Join Date
    May 2014
    Location
    Columbia, SC
    Posts
    8,494

    Re: gfi breaker keeps jumping

    Quote Originally Posted by kiss4afrog View Post
    In my world the circuit breaker is never chosen or sized according to the wire. Someone posted something like this once before. You choose a circuit breaker depending on the load on the line and only the load. Same with the wire, the wire size is chosen depending on the load on the circuit and the distance of the run. In a perfect world the person making the buying decision picks a circuit breaker close to what's recommended for the load and goes a size bigger than what's recommended on the wire.

    There is no benefit in going bigger on the circuit breaker as it only allows the device to pull more amps than it should. That extra amperage is usually being turned into heat and with enough of it you get smoke and then fire. If you put in a bigger circuit breaker because the wire can handle more amps due to it being over sized for the load you simply put the electrical device at risk of massive failure including smoke, fire and explosion as it's not being protected at the proper level.
    I actually think we are saying the same thing. What I should have said is that in repair/remodeling where you have an existing wire the breaker is sized to the existing wire.

    But when it comes down to it as you said the breaker protects the wire from overheating.
    TFP Moderator 39 X 18 23,000(ish) freeform gunite; built 2007ish; Pentair Triton II TR100 600lb Sand filter; 2 HP Pentair pump with 2.2 HP AO Smith single speed motor; 2 skimmers, 1 main drain, 4 returns w/waterfall, Stenner 45MHP2 3GPD running@ 60% - 15 gal Tank; heated by the sun CYA 200+ when I started - 50 now. Dolphin Supreme M5 Pool Cleaner. Hot Springs SX Spa, 285 gallon