    Teledyne Laars Lite won't stay lit

    I have an older laars lite pool heater with the hot surface ignition. The heater will ignite for a few seconds and then turn off. It will do this about 3 times then stop. I have checked all the sensors and get the proper 24 volts in the right places. The thermister also reads correctly.

    With all the trouble shooting it is either the gas valve or the controller itself. The gas valve is a r0317100 and the controller is a r0317500. What I get on the brown wire coming from the valve output of the controller to the mv1 input on the gas valve is 24 volts for about 7 seconds after the ignitor gets hot then it goes to 0 volts. When the mv1 on the valve is getting the 24 volts gas is being released and the burners fire up until mv1 goes to 0 volts.

    Reading the jandy troubleshooting guide for the laars lite2, which has pretty much the same components it says the mv1 should only have 24 volts on it for the 7 seconds at start up. This seems incorrect to me as wouldn't the gas valve need 24 volts constantly to keep the solonoids open? So I am unsure if the controller is messed up or is it the valve? I cannot find any info on the operation voltages for these wires.

    Thanks for any help anyone can provide

  2. Back To Top    #2

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Teledyne Laars Lite won't stay lit

    Sounds to me like the ignitor isn't sensing flame or if your unit has a separate flame sensor, it is not working.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  3. Back To Top    #3

    Join Date
    Aug 2014
    Location
    toronto/ontario
    Posts
    2

    Re: Teledyne Laars Lite won't stay lit

    No flame sensor on this model. How can I tell if the ignitor is sensing flame? Is the controller sensing ohm changes in the ignitor?

  4. Back To Top    #4

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Teledyne Laars Lite won't stay lit

    So the ignitor is the flame sensor. then I've never gotten into actually trying to determine if the ignitor is sending back a signal or not. It would stand to reason it would be looking for some ohm change, probably a steady reading as the flame is keeping the ignitor hot. I just usually swap out the sensor and see what happens. It's just easier for me to do that. If I swap that and it still won't stay lit, then I would suspect the control module.

    There are only a few items I part swap like this in the field.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,