    What Should the Bonding wire be tied to? Inspection?

    We are having a pool put in and the builder is pathetic. It has full automation, automatic cover, pool/spa, water fall and deck jets. Once filled (5 weeks ago) the builder's electrician could not come out to hook up the pumps to circulate. After a week and a half I insisted and the electrician came and quickly got the pumps going but did not finish the automation or lights and haven't seen him since. I have been cleaning things up and getting things going myself. I know that there was a bonding wire that ran to the re-bar, lights and all places required and it passed inspection before the gunite. As I was working at the equipment pad I did not see the bonding wire hooked to anything or going into the Pentair EasyTouch control panel. I then noticed it just hanging loose off to the side of the pad (actually through the fence and into my neighbors roses - he has beautiful roses). My question is, what all should the bonding wire be tied to and how? Is that a big deal, should I be concerned? It seems that with my prior pool it ran directly to all pumps and into the control box. We also have pentair intellibrite lights that have not been connected to the breaker yet. Inside the J-box for those I see a lug for, what looks like, a bonding wire but no bonding wire. Is that (those tied to the bonding wire) done at the box or should it be bonded at the j-box as well. Also, is there generally a final electrical inspection or just the one before the gunite? I'm a bit concerned that in a hurry the electrician did not do things correctly or to code and there may be some safety concerns. Thanks!
    21,000 gal, in ground gunite/plaster, sand filter, rectangular pool with automatic cover, raised 8' round spa, 2' wall opposite spa with 2 sheer decent falls, 8 deck jets, 2 Pentair VS speed pumps (1 for pool/spa, 1 for falls and deck jets), one 2 hp for 6 spa jets, almost completed (been 3 months, was supposed to be 5 weeks).

  2. Back To Top    #2
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: What Should the Bonding wire be tied to? Inspection?

    It should be connected to all the pieces of equipment that have power at the pad (motors, automation panel, heater, etc). I am not sure if the J-box for the lights need to be bonded or not, certainly would not hurt.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  3. Back To Top    #3

    Join Date
    Mar 2014
    Location
    Albq. NM, United States
    Posts
    38

    Re: What Should the Bonding wire be tied to? Inspection?

    Thanks, that's sort of what I remembered with my old pool. I will make sure that get's done.
    21,000 gal, in ground gunite/plaster, sand filter, rectangular pool with automatic cover, raised 8' round spa, 2' wall opposite spa with 2 sheer decent falls, 8 deck jets, 2 Pentair VS speed pumps (1 for pool/spa, 1 for falls and deck jets), one 2 hp for 6 spa jets, almost completed (been 3 months, was supposed to be 5 weeks).