OK so our pool has been up for a week or so. I since found this site and will be adopting the TFPC methods. I as many new pool owners , it seems, have purchased the "package" from whatever pool store. My pump, filter, sanitizer (which I am not going to use) all seem to have a common problem. I don't find hardly ANY information on the manufacture websites for these items. I will use my pump and filter as the example:

Manufacture Hayward
Model SWIMPRO VOYAGER
2HP 2 Speed Pump

I was trying to find info for the flow ratings and head loss charts. There are not ANY SWIMPRO Voyager Pumps that match what I have on their site??? The motor does not even match the part number in the manual. Is this common? I have my doubts as to weather or not it is truly a 2 HP pump I would bet it is an inflated number. I will post a pic of the motor plate.
 
The pump itself looks like the matrix pumps but none of those specs are even close.

Here is the motor nameplate if anyone can decipher it.

2amezury.jpg
 
That is a 2.25 HP on the label, but the Service Factor is listed as SPL, which means it is less than 1 (probably 0.9). So ... it is a 2 SFHP pump

You could also have a 2HP with 1.0 SF or 1.5HP with 1.33 SF and they would be identical ... except for the marketing games they are playing with the numbers.
 
That is a 2.25 HP on the label, but the Service Factor is listed as SPL, which means it is less than 1 (probably 0.9). So ... it is a 2 SFHP pump

You could also have a 2HP with 1.0 SF or 1.5HP with 1.33 SF and they would be identical ... except for the marketing games they are playing with the numbers.

Actually that's what I initially thought as well 2.25 HP but it actually says 2-.25 SPL
 
I would be more looking at the amp rating. Looks like you need something that will handle 15amps for the start up load.
Actually, 15A is the "FLA" or "full load amperage," which is what the motor consumes while running normally. Startup or "inrush" currents can be substantially higher. I don't know if the Intermatics need to be sized in consideration of startup current or not, but it's something to check.
 
A motor would never be sized to pull its FLA at normal running. It probably pulls 50 - 75% of FLA at normal running.

But you are correct about inrush currents, a 15 amp breaker would trip every time you tried to start the motor.
 

Enjoying this content?

Support TFP with a donation.

Give Support
Pflugerpool is correct, in that an electric motor will draw a little more than half of the FLA when running at or below it's rated load.

Inrush/starting current can be as much as 10x the FLA, for a very short time, as the motor spins up. this is why industrial motor fuses and breakers are "slow blow". This gives a small period of time where very high starting currents aren't going to do a lot of false trips on starting.

Household breakers can actually handle 5x the rated current for up to 10 seconds, but will trip instantaneously on a direct short.
 
Large current in rush occurs on high start up torque applications like a compressor. However, pool pumps have a very low start up torque so the load is near zero. The motor only needs to overcome the friction of the bearings but as the impeller spins up, load/torque increases with speed. So if you were to scope the current on a typical pool pump motor as it starts, the current increases on a cubic curve until the RPM is at full speed (~3450 RPM). But of course this happens very quickly. Remember that the maximum torque curve of an induction motor is not the same as the torque curve for centrifugal pump:

http://www.engineeringtoolbox.com/pumps-speed-torque-d_1114.html

Another good reference:

http://books.google.com/books?id=3R...epage&q=CEntrifugal Pump torque curve&f=false

There is however, still a short 1 cycle burst for the EMF build up but overall it is much shorter than a compressor.

Also, most pool pumps have an operating point that is well below FLA. The current draw on a pump increases from left to right on the pump head curve and peaks at just before pump run out. So that is why you should never use FLA as an indication of operational pump power draw.
 