Thread: Aqua Plus Filter VSP Comm Error

  1. Back To Top    #1

    Join Date
    Jun 2014
    Gulf Breeze/Florida

    Aqua Plus Filter VSP Comm Error

    We have a new pool and are just learning about the system. We have an aqua plus and are getting a "Filter VSP Comm Error". I cannot find anywhere how to fix this. Any help would be appreciated.

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Silver Spring, MD

    Re: Aqua Plus Filter VSP Comm Error

    Welcome to TFP!

    That error message means the automation system is setup to expect a Hayward variable speed pump connected over a data connection, but no pump responds on the data connection. Either the data connection is not properly connected, or the pump does not have power, or there is a hardware error of some kind in the communications circuit on one end or the other. Start by checking the data cable is properly connected at both ends and is not cut anywhere.