    Power problems

    recently had a hayward 3200vsp installed to replace a 1hp jandy stealth. Since installing the new pump the gfci in my basement keeps tripping randomly. I recall this only happening once last year, but since replacing the pump it happens regularly. It doesn't trip while priming or running at high speed. Seems to trip only when running at 1000 or 1725 rpm. *‎ My programming is 7-7 at 1725 and then 7-7 at 1000. *

    When we first turned on the power it tripped right away because a wire was bent too much. Now, it runs fine for hours or multiple days between trips. * I've jiggled the wire while the pump is running but this didn't do anything. *

    The pump is on a dedicated 15A breaker in my sub panel connected to a 30A gfci inside. There is also a switch between the pump and breaker (from the old pump). *One interesting thing was when it was first installed, I turned off the switch when leaving for work and when I returned the gfci was tripped. * Nothing else would have been on, just power was on. *‎

    I thought it might be one of my other breakers in the sub panel, so yesterday I had just the pump and heater powered and it tripped. Heater wasn't on, it only had power for its clock. So far today, it's only the pump but it hasn't tripped (yet). *

    Could it be the pump? Or heater? * ‎ Maybe it's just a faulty gfci in my main panel. * No breakers or wires have been changed yet. I'm worried the constant loss of power may cause damage, especially if my heater was running when it happens. * *I don't think it's load related as I've had the pump running at 2500rpm and heater on for over 8 hours simultaneously with now issue. Again, only happens when no one is there to see it!

    Any ideas?‎
    77000L (20500 gallon) vinyl in-ground chlorine double roman pool, 35'x17', Hayward SP3200VSP, Jandy Lite2 LJ400N heater, Hayward S244TC filter, *deleted* Hayward chlorinator, Taylor CK1004FAS+CYA

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Power problems

    You can't feed a sub-panel with a GFCI breaker. Things exactly like what you describe, or worse, happen.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3

    Join Date
    Jun 2013
    Location
    GTA, Toronto, Ontario
    Posts
    119

    Re: Power problems

    JasonLion - sub panel may not be exactly what it is called. But if I understand you correctly, I should replace the 1 gfci in my main panel with a regular breaker and then put in 3 gfci breakers in my outside "sub" panel? Any technical reason or just experience? My electrician didn't say anything about it.

    The pool is about 8 years old (second owner) and that's how I got it.
    77000L (20500 gallon) vinyl in-ground chlorine double roman pool, 35'x17', Hayward SP3200VSP, Jandy Lite2 LJ400N heater, Hayward S244TC filter, *deleted* Hayward chlorinator, Taylor CK1004FAS+CYA

  4. Back To Top    #4

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Power problems

    Assuming that the 30 amp breaker in the main panel is a double pole breaker, I am surprised that you have not had problems in the past with it. You said that the panel with the 15 amp breaker is not a sub panel. Not sure what else it would be. Can you confirm that the breaker feeding all of this (30 amp) is indeed a double pole or is it a single pole. If it is a double pole, the reason it is tripping, is it is sensing a load imbalance across both poles and thinks that it is a current leak, thus tripping.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  5. Back To Top    #5

    Join Date
    Jun 2013
    Location
    GTA, Toronto, Ontario
    Posts
    119

    Re: Power problems

    I just double checked, the main panel is a double 30 (so 60, no?). Outside, the pump is on a double 15A (only 1 lever but double for 240v) and the heater and outside outlets are all on separate 15A singles. (sorry, don't know the technical terms).

    This morning, with only the pump breaker on (again, it's a double wide 15A) the gfci in the basement is tripped.

    I will try to post pictures in an hour or so
    77000L (20500 gallon) vinyl in-ground chlorine double roman pool, 35'x17', Hayward SP3200VSP, Jandy Lite2 LJ400N heater, Hayward S244TC filter, *deleted* Hayward chlorinator, Taylor CK1004FAS+CYA

  6. Back To Top    #6

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Power problems

    Quote Originally Posted by benjydog View Post
    I just double checked, the main panel is a double 30 (so 60, no?).
    Nope, 30 amps




    Quote Originally Posted by benjydog View Post
    Outside, the pump is on a double 15A (only 1 lever but double for 240v) and the heater and outside outlets are all on separate 15A singles. (sorry, don't know the technical terms).

    This morning, with only the pump breaker on (again, it's a double wide 15A) the gfci in the basement is tripped.

    I will try to post pictures in an hour or so
    Remove the 30 amp GFCI in the basement and install a regular 30 amp breaker. Install the GFCI protection in the box that has the breakers that control everything outside. GFCI's do not like to be feeding other GFCI's. Sometimes they work fine, other times they do not.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  7. Back To Top    #7

    Join Date
    Jun 2013
    Location
    GTA, Toronto, Ontario
    Posts
    119

    Re: Power problems

    Thanks. I will talk to my electrician tonight. Here are the pictures i was talking about.

    outside.jpg

    - - - Updated - - -

    inside.jpg

    Sorry for the size, it wouldnt allow me to go bigger.
    77000L (20500 gallon) vinyl in-ground chlorine double roman pool, 35'x17', Hayward SP3200VSP, Jandy Lite2 LJ400N heater, Hayward S244TC filter, *deleted* Hayward chlorinator, Taylor CK1004FAS+CYA

  8. Back To Top    #8

    Join Date
    Jun 2013
    Location
    GTA, Toronto, Ontario
    Posts
    119

    Re: Power problems

    Update;

    so after some head scratching we found a way to make the breaker trip Ondemand. After replacing the on/off switch between the pump and breaker and that not working we replaced the gfci in my basement. No problems since. Expensive fix, but problem is gone!
    77000L (20500 gallon) vinyl in-ground chlorine double roman pool, 35'x17', Hayward SP3200VSP, Jandy Lite2 LJ400N heater, Hayward S244TC filter, *deleted* Hayward chlorinator, Taylor CK1004FAS+CYA