    Plumbing Head Loss Question - Tee or Elbow

    I'm doing some plumbing on my pool, and I'm curious if anyone can tell me if there will be a major difference in head loss between the following two configurations (ignore the periods).


    1.)................Pump
    .....................||
    .....................||
    Main Drains === Tee === Valve === Yard Drain


    2.)................Pump
    .....................||
    ....................Tee === Valve === Yard Drain
    .....................||
    Main Drains === Elbow

    In the first setup, the water to the pump has to make a sharp 90 degree turn while piling into the closed valve. In the second setup, the water makes a smooth 90 degree turn and then travels straight through the tee. Obviously, with the second setup I would never get the last couple of inches of water out of the pipe since the yard drain pipe level is above main drain pipe level by the height of the elbow and the tee. Thanks!

    TomU

  2. Back To Top    #2
    Mod Squad JohnT's Avatar
    Join Date
    Apr 2007
    Location
    SW Indiana
    Posts
    9,088

    Re: Plumbing Head Loss Question - Tee or Elbow

    Are you wanting to be able to drain the pool without the pump? I'm not sure of your goal, but the water in the pipes will always return to the level of the pool water as long as it can get air.

    Drawing 1 has one less fitting in the flow of the pumped water, so I'd choose it. I don't believe the area between the T and the valve will have much impact on the flow of water into the pump.
    TFP Moderator
    20K Gallon 20X36 Vinyl Inground
    Hayward S244T Sand Filter with 1HP Whisperflo Pump. Liquidator C-201 and Solar Heat

  3. Back To Top    #3

    Join Date
    May 2008
    Location
    Long Island, NY
    Posts
    151

    Re: Plumbing Head Loss Question - Tee or Elbow

    Pump to Main Drain:

    Setup 1:
    Tee-Branch - 8 equivalent feet of 1-1/2" pipe

    Setup 2
    Tee-Run: 2.7 equivalent feet of 1-1/2" pipe
    Elbow: 4 equivalent feet of 1-1/2" pipe

    Setup 2 would have 1.3 less equivalent feet of 1-1/2" pipe.

    Pump to the yard drain:

    Fitting loss is the same for both setups.

    For more on fitting friction loss see: http://www.lascofittings.com/supportcen ... ttings.asp

    Actual difference in head loss will depend upon pipe size and flow. 1.3' difference is not much. Example head loss @ 40 GPM in 1-1/2" pipe is only 9.54' (4.13 PSI) per 100' of pipe, so 1.3' of pipe is only 0.054 PSI...

    To calculate your actual loss here is a online friction loss calculator...

    http://www.lascofittings.com/supportcen ... ssCalc.asp
    Pool Details: 25,440 Gal IG Vinyl 21x40 Mountain Pond (Graphex)
    Filter: Hayward Micro-Clear DE (48 Sq Ft)
    Pump: Hayward SP2603VSP VS Super Pump
    SWG: Circupool Si45
    Cleaner: Pentair Kreepy Krauly Prowler 820

  4. Back To Top    #4

    Join Date
    Apr 2007
    Location
    Wyoming, Michigan
    Posts
    93

    Re: Plumbing Head Loss Question - Tee or Elbow

    Quote Originally Posted by JohnT
    Are you wanting to be able to drain the pool without the pump?
    Yes, or at least be able to lower the level if I want. I would only ever open that valve with the pump off. I'm thinking it would be handy if I need to lower the water level in the winter and already have the pump and related equipment winterized. This drain line is below the frost line. Here is more of the drawing.

    ..............................Returns
    .................................||
    ...................Pump === Filter => Waste Port
    .....................||.......................||
    .....................||.......................||
    Main Drains === Tee === Valve ====== Tee === Yard Drain

    It doesn't look like there is a big difference in flow restriction, but I wasn't sure since under normal conditions 1/2 of the tee in option 1 will be blocked (by the valve). This means its acting like an elbow, but possibly with much more turbulence. In option 2, there should be virtually no restriction through the Tee. There is no change in direction of the water through it and nothing sticking out that would create turbulence. FWIW, this is all 2" PVC.

    I guess the fundamental question is what is the difference in flow restriction between a 90 degree elbow and a tee with one end plugged? (Or how about between a schedule 40 tee [sharp bend] and a DWV tee [larger radius bend]?)



    [Edit]
    I should have followed that link first, I see some of this info is listed already....
    For those that didn't follow the link, here is the difference (for 2" PVC):
    - 90 degree direction change through Elbow = 6.0'
    - 90 degree direction change through Tee = 12.0'
    - Straight through a Tee = 4.3'

    So just analyzing the corner where the water is changing direction, option 1 would introduce 12.0' of additional head while option 2 would introduce 10.3' of additional head.

    Thanks for providing those links!
    [/Edit]

  5. Back To Top    #5
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,481

    Re: Plumbing Head Loss Question - Tee or Elbow

    The diameter of the pipe has much more of an impact on head loss than the fitting type. For a given plumbing system and flow rate, simply going from 1 1/2" pipe to 2" pipe will reduce the head loss by over 75%!!

    Also, as was pointed out a single fitting has very little impact on the over all plumbing head loss so if you really want to reduce head loss, increase the pipe diameter.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  6. Back To Top    #6

    Join Date
    Apr 2007
    Location
    Wyoming, Michigan
    Posts
    93

    Re: Plumbing Head Loss Question - Tee or Elbow

    Quote Originally Posted by mas985
    ...simply going from 1 1/2" pipe to 2" pipe will reduce the head loss by over 75%!!
    Most people don't appreciate the power of PI R Squared! A 2" pipe is 78% larger than a 1 1/2" pipe. Same idea with pool sizes. A 24' pool will hold 78% more water than an 18' pool (13,500 gallons vs. 7,600 gallons).

  7. Back To Top    #7

    Join Date
    May 2008
    Location
    Long Island, NY
    Posts
    151

    Re: Plumbing Head Loss Question - Tee or Elbow

    Quote Originally Posted by TomU
    Quote Originally Posted by JohnT
    option 1 would introduce 12.0' of additional head while option 2 would introduce 10.3' of additional head.
    [/Edit]
    Do not mix up equivlent feet of pipe with head loss. In order to calculate head loss of the pipe & fittings, you need to add up the feet of pipe to the total equivlent feet of pipe of the fittings. The first link gives you the equivalent feet of pipe for the fittings.

    option 1 would introduce 12' of pipe to the system not 12' of head.

    The 2nd link is where you calculate your head loss. Flow is critical to calculating head loss.

    1-1/2" vs 2" @ 40 GPM per 100' of pipe

    1-1/2" has 9.54' (4.31 PSI) loss per 100' of pipe
    2" has 2.79' (1.21 PSI) loss per 100' of pipe
    Pool Details: 25,440 Gal IG Vinyl 21x40 Mountain Pond (Graphex)
    Filter: Hayward Micro-Clear DE (48 Sq Ft)
    Pump: Hayward SP2603VSP VS Super Pump
    SWG: Circupool Si45
    Cleaner: Pentair Kreepy Krauly Prowler 820

  8. Back To Top    #8

    Join Date
    Apr 2007
    Location
    Wyoming, Michigan
    Posts
    93

    Re: Plumbing Head Loss Question - Tee or Elbow

    Thanks. I see what you mean.