    Bonding Question

    I am ready to begin bonding my pool.

    Since it is a resin pool should I still connect a lug to the posts?

    I am going to make one of the 4 connections to the wall connector.

    I will have to do the water a little later when I get the plate in but will rough my wire up there in preperation.

    Is this overkill?

    Here is a pic.

    Screenshot_2014-05-30-16-50-23.jpg
    25,600 gallons
    33 Ft. 52 Inch AG buried 2 FT. Chlorine
    250 lb Sand Filter 2HP Hayward Pump

  2. Back To Top    #2

    Join Date
    May 2014
    Location
    Atoka, TN
    Posts
    26

    Re: Bonding Question

    Should this be moved to a different section? I don't want to keep 120 ft of #8 copper if I don't need it. I read where a section from the metal wall to the pump would suffice.

    25,600 gallons
    33 Ft. 52 Inch AG buried 2 FT. Chlorine
    250 lb Sand Filter 2HP Hayward Pump

  3. Back To Top    #3
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Bonding Question

    The wall isn't resin is it? I see what looks like a stainless steel panel, and if it is, it should be bonded at very least. I'd go ahead and run the loop around the pool and bond all the metal parts.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  4. Back To Top    #4

    Join Date
    May 2014
    Location
    Atoka, TN
    Posts
    26

    Re: Bonding Question

    Correct. The wall is not resin. Should I just tap into the the legs at 3 places? I am going to tap into that metal wall then to the motor. Should I run a rough end to the skimmer for future water bond?

    25,600 gallons
    33 Ft. 52 Inch AG buried 2 FT. Chlorine
    250 lb Sand Filter 2HP Hayward Pump

  5. Back To Top    #5
    Divin Dave's Avatar
    Join Date
    Oct 2013
    Location
    Longview, Texas
    Posts
    4,926

    Re: Bonding Question

    NEC code I believe calls for a minimum of bonding in 4 equally spaced spots around the pool. Or as close to equally spaced as you can get it
    Divin Dave,
    IG Vinyl, 15' x 30', 3 1/2' - 6' deep, Oval, ~15K gal, Intelliclor IC40, Intelliflo VS pump, Clean and Clear 420 Filter, auto-fill-disabled, Retrofit LED Color Light, Dolphin Nautilus Robot, TF100 Test Kit, Taylor K1766 Salt Test Kit, Tftestkit Pressure Gauge.
    www.tftestkits.net Experience- it's what's learned just after you needed it most !!

  6. Back To Top    #6
    pwrstrk's Avatar
    Join Date
    Aug 2012
    Location
    Elverson Pa.
    Posts
    4,758

    Re: Bonding Question

    Quote Originally Posted by Divin Dave View Post
    NEC code I believe calls for a minimum of bonding in 4 spaces around the pool. Dont quote me on that though.
    You are correct. That is the way my pool is bonded.
    Jeff
    24'x54" AG Morada RTR (by wilbar) 13'500 gal. Hayward Powerflo Matrix 1hp 2 speed. Hayward Perflex EC65 DE filter.

  7. Back To Top    #7
    Divin Dave's Avatar
    Join Date
    Oct 2013
    Location
    Longview, Texas
    Posts
    4,926

    Re: Bonding Question

    yup. I just googled it to make sure!

    MIne is grounded in 4 spots too

    Quote Originally Posted by pwrstrk View Post
    You are correct. That is the way my pool is bonded.
    Divin Dave,
    IG Vinyl, 15' x 30', 3 1/2' - 6' deep, Oval, ~15K gal, Intelliclor IC40, Intelliflo VS pump, Clean and Clear 420 Filter, auto-fill-disabled, Retrofit LED Color Light, Dolphin Nautilus Robot, TF100 Test Kit, Taylor K1766 Salt Test Kit, Tftestkit Pressure Gauge.
    www.tftestkits.net Experience- it's what's learned just after you needed it most !!

  8. Back To Top    #8

    Join Date
    May 2014
    Location
    Atoka, TN
    Posts
    26

    Re: Bonding Question

    That's what I am doing now. Did you guys tap into the legs? The 4th one will be on the metal wall connector. Do you guys have the water bonded. I don't have the hook up yet but can run the wire if it's needed.

    25,600 gallons
    33 Ft. 52 Inch AG buried 2 FT. Chlorine
    250 lb Sand Filter 2HP Hayward Pump

  9. Back To Top    #9

    Join Date
    Apr 2013
    Location
    Akron, NY
    Posts
    40

    Re: Bonding Question

    I have 4 legs bonded, the filter, and NY requires 9 sq in metal plate in the skimmer basket to bond the water. I sarcastically asked that since I am bonded with $250 Worth of copper if I could swim in an electrical storm. inspector didn't appreciate the comment.
    24 foot 54 inch AGP, 14.5k gallons, 1hp pump, 120 sq foot cartridge filter

  10. Back To Top    #10

    Join Date
    Mar 2014
    Location
    south central PA
    Posts
    112

    Re: Bonding Question

    We just had our resin pool done. Since the legs are all resin our electrician used a small lug nut (made specially for this bonding stuff I think?) that attached the copper wiring to the metal ring that holds the liner in place. Did that at 4-5 places around the pool.
    28 ft round ABG with ~6ft deep end, approx. 20,000 gal, 2 spd 2 HP pump, sand filter

  11. Back To Top    #11

    Join Date
    May 2014
    Location
    Atoka, TN
    Posts
    26

    Re: Bonding Question

    Pigeon. Anyway to get a pic of that?

    25,600 gallons
    33 Ft. 52 Inch AG buried 2 FT. Chlorine
    250 lb Sand Filter 2HP Hayward Pump

  12. Back To Top    #12

    Join Date
    Mar 2014
    Location
    south central PA
    Posts
    112

    Re: Bonding Question

    I'll take a picture tomorrow for you. If you google "bonding lug" you'll get an idea of the lug that was used.
    28 ft round ABG with ~6ft deep end, approx. 20,000 gal, 2 spd 2 HP pump, sand filter

  13. Back To Top    #13

    Join Date
    Jun 2013
    Location
    Newcastle, Oklahoma
    Posts
    508

    Re: Bonding Question

    here is how I did mine. Walls are steel, 8 of the supports are steel, the rest are resin. I lug connected all 8 supports using self tapping sheet metal screws in a ring around the pool that started and will stop at pump station. There I will tie into lug on pump, and attach the whole grid to a 3 ft grounding rod driven into the ground until only about 6 inches remain. Later I will add water bond through skimmer and tie to grid along with 2 connections to rebar in concrete decking tied to the grid.

    I started bonding before my pool was even finished being built since it is buried 3 ft and once walls are up I would have 12-15 inches of space in which to work in.



    Partially buried Doughboy Desert Spring 16 x 32, sport pool, with 7 ft deep middle, 20,000 gallons, Hayward Powerflo Matrix 1.5 HP 2 speed pump, 250 lb sandfilter, 2 Doughboy skimmers and 2 returns. 2 cascade fountains.
    Taylor K-2006 kit. Zodiac Barracuda Ranger suction side cleaner.
    TFPC method and is crystal clear every day thanks to TFP!!!

  14. Back To Top    #14

    Join Date
    May 2014
    Location
    Atoka, TN
    Posts
    26

    Re: Bonding Question

    I see. I attached lugs to 4 posts equally spaced. I'll take an up close pic tomorrow. The outside of the pool post I connected to has a coating, same as the wall but the post itself has a metal quality albeit thin. If I wasn't careful the tap screw wouldn't hold firm and I had to redo it. I want to make sure this bond is going to do the job. I didn't think you had to attach to a rod in the ground. I will have the circle and terminate at the pump lug.

    25,600 gallons
    33 Ft. 52 Inch AG buried 2 FT. Chlorine
    250 lb Sand Filter 2HP Hayward Pump

  15. Back To Top    #15
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Bonding Question

    You are not normally supposed to have a ground rod.

    The circle of wire should be 18" out from the water line and 4" to 6" below sub-grade.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  16. Back To Top    #16
    Divin Dave's Avatar
    Join Date
    Oct 2013
    Location
    Longview, Texas
    Posts
    4,926

    Re: Bonding Question

    You need to use some sandpaper and remove that coating. The bonding lug should be full metal to metal contact with the posts. As it is now, only tiny area on the side of the screw through the post has you actually bonded, and thats not enough.

    Quote Originally Posted by TommyD View Post
    I see. I attached lugs to 4 posts equally spaced. I'll take an up close pic tomorrow. The outside of the pool post I connected to has a coating,

    Sent from my SAMSUNG-SGH-I537 using Tapatalk
    Divin Dave,
    IG Vinyl, 15' x 30', 3 1/2' - 6' deep, Oval, ~15K gal, Intelliclor IC40, Intelliflo VS pump, Clean and Clear 420 Filter, auto-fill-disabled, Retrofit LED Color Light, Dolphin Nautilus Robot, TF100 Test Kit, Taylor K1766 Salt Test Kit, Tftestkit Pressure Gauge.
    www.tftestkits.net Experience- it's what's learned just after you needed it most !!