    Pentair MiniMax NT does not ignite - error E05

    The green lights go upto "HEATING"
    I can smell gas from exhaust after “HEATING” goes green for 2-3 sec. After 3 attempts, it shows Error E05.

    70V comes to my igniter. Should it be 120V?
    I also measured that the igniter has 100 Om resistance. Is it normal?

    Is it a false igniter or board?

    https://www.youtube.com/watch?v=GA4kcuO8X9g
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  2. Back To Top    #2

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: Pentair MiniMax NT does not ignite - error E05

    You should have 120 going to the ignitor. If you are really only seeing 70, then it sounds to me like the ignition control module is having issues. If the ignitor were an open, then it is faulty.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  3. Back To Top    #3

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Pentair MiniMax NT

    How to remove and clean burners?
    Is it right, the gas travel as red arrows on my picture? I just surprised that there is a lot of space between a burner orifice and a burning chamber (pink arrows).
    Do I need to rotate/remove a gas pipe (blue arrow) or 4 bolts (green arrow)?
    heater5.jpg
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  4. Back To Top    #4

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT

    Is it any way to reach and clean burners from the back of the heater?

    burnertray3.jpg
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  5. Back To Top    #5

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT

    This guy managed to open the back door. How??
    https://www.youtube.com/watch?v=17fQOcAB9v0
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  6. Back To Top    #6

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT does not ignite - error E05

    I took it out - hot red...
    http://youtu.be/z1GLfJeowPQ

    70V (whole scale set for 250V): http://youtu.be/DiV6lPj4R0A
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  7. Back To Top    #7

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Pentair MiniMax NT

    It looks to me that he took the whole heater apart. The amount of space between the orifices and burner tube is there to allow the gas and air to mix to the proper ratio to burn properly. Not sure on how those burners come out. It looks like you may need to remove the corroded plate above them at least. It may be possible that each tube can be raised up in the back ad slid out. Paul or one of the other guys that work on these may be along later to better advise.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  8. Back To Top    #8

    In the Industry

    duraleigh's Avatar
    Join Date
    Apr 2007
    Location
    Sebring, Florida
    Posts
    30,077

    Re: Pentair MiniMax NT does not ignite - error E05

    Pool123,

    It looks like you have two threads running simultaneously. That is very confusing to responders and your posts are likely not to get answered.
    Dave S.
    42k vinyl and concrete pool, 1.5hp pump, 140gpm filter
    TFTestkits , PoolMath , Pool School

  9. Back To Top    #9

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT does not ignite - error E05

    Hi Dave,
    This post is for the igniter problem. Another post is for burners cleaning.
    It looks that the igniter works. My guess that burners are dirty.
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  10. Back To Top    #10

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT

    The guy on this video: http://www.youtube.com/watch?v=VDf_i6q5GB4
    recommends to remove a main gas pipe and slide whole burner tray out.
    If it is the only way, then those engineers are not smart.
    I would try to remove an orifice and release the burner.

    Is it common practice, to use matches to check if an orifice runs a gas? It seems my heater release the gas at right time and shots down the valve if no flame. The igniter gets hot red at right time then turns off.
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  11. Back To Top    #11

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT

    Another great pool heater design: http://www.youtube.com/watch?v=YYZ1Yy42pmg
    I guess no way to take orifices off without taking almost whole heater apart.
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  12. Back To Top    #12

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: Pentair MiniMax NT

    Do you need to remove the burners for a particular reason? Is the unit burning bad? If you remove the plate above the burners, you can see pretty good inside to visually inspect the burners.

    - - - Updated - - -

    Quote Originally Posted by pool123 View Post
    This guy managed to open the back door. How??
    https://www.youtube.com/watch?v=17fQOcAB9v0
    The unit he is working on is an older Raypak from what it looks like. They are easy to get into.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  13. Back To Top    #13

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: Pentair MiniMax NT does not ignite - error E05

    That unit has an ignitor and a flame sensor.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  14. Back To Top    #14

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT

    ps0303,
    My heater does not burn. The igniter gets hot red, the gas valve clicks, I can smell gas for 2-3 sec, the gas valve clicks closed, the igniter goes off. All in right sequence.

    I think that orifices need to be clean. To remove them I will need to remove burners as well.


    Is it right that I need to remove the main gas pipe as on videos above, then get all burner tray out?
    No other way?
    What do I do after that? How to remove burners? Do I unscrew something on the back of the burner tray?

    What if I try to remove burner orifices without unscrewing some panel on the back of the burner tray?
    Will it work? Or the back panel removal on the burner tray is must?

    My main gas pipe has no way to hold a tool. And after years of rusting will be painful to remove it.



    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  15. Back To Top    #15

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: Pentair MiniMax NT

    Why do you think they need to be cleaned? With the correct wire, you can clean them without removing them. The best thing, if you haven't done so already, is to remove the plate above the burners and observe what happens when the unit lights up. Again, if your are having issues with it lighting and going out within 4 second, then you need to look at the flame sensor. Pulling burners and orifices is not always needed and more of a pain. Especially of the bolts that hold the burner tray in are rusted and you snap one off.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  16. Back To Top    #16

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT does not ignite - error E05

    Are you applying that a flame sensor could be faulty too? But there is no flame to start from.
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  17. Back To Top    #17

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: Pentair MiniMax NT does not ignite - error E05

    OK. Since you can see the ignitor glow then, do you hear or feel the gas valve click to open?
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  18. Back To Top    #18

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT

    What do you mean by "unit lights up"?
    I removed the panel. I could see the igniter gets hot red, I can smell a gas after the gas valve clicks, but no fire. Then the gas valve clicks off, no smell of gas after that. The same time the igniter does off. It repeats x3 times and gives an error E05.
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  19. Back To Top    #19

    Join Date
    May 2014
    Location
    Chicago
    Posts
    46

    Re: Pentair MiniMax NT does not ignite - error E05

    The igniter gets hot red, the gas valve clicks, I can smell gas for 2-3 sec, the gas valve clicks closed, the igniter goes off. All in right sequence.
    in-ground 20'000 gal; AK60431 cartridge filter x 4; Pentair MiniMax NT heater

  20. Back To Top    #20
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Pentair MiniMax NT does not ignite - error E05

    Topics merged. Please keep everything related to one project or problem together in one place.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot