Become a TFP Supporter Pool Math Forum Rules Pool School
Page 1 of 4 1234 LastLast
Results 1 to 20 of 64

Thread: This is why you bond your pool and equipment!

  1. Back To Top    #1
    Mod Squad JohnT's Avatar
    Join Date
    Apr 2007
    Location
    SW Indiana
    Posts
    9,089

    Exclamation This is why you bond your pool and equipment!

    TFP Moderator
    20K Gallon 20X36 Vinyl Inground
    Hayward S244T Sand Filter with 1HP Whisperflo Pump. Liquidator C-201 and Solar Heat

  2. Back To Top    #2

    Join Date
    Jun 2013
    Location
    Newcastle, Oklahoma
    Posts
    508

    Re: This is why you bond your pool and equipment!

    wow. so how do you bond it? its there kit to buy? also, if your pump was plugged into a GFCI outlet, and something shorted out that would cause an issue like electrified water, similar to that in the video, i would think it would trip the GFCI shutting power to pump off, and eliminating this issue. So wouldnt a GFCI outlet be enough?
    Partially buried Doughboy Desert Spring 16 x 32, sport pool, with 7 ft deep middle, 20,000 gallons, Hayward Powerflo Matrix 1.5 HP 2 speed pump, 250 lb sandfilter, 2 Doughboy skimmers and 2 returns. 2 cascade fountains.
    Taylor K-2006 kit. Zodiac Barracuda Ranger suction side cleaner.
    TFPC method and is crystal clear every day thanks to TFP!!!

  3. Back To Top    #3

    Join Date
    Dec 2012
    Location
    Manassas Park, VA
    Posts
    191

    Re: This is why you bond your pool and equipment!

    wow, that is horrifying. Thank you for sharing, I will be double checking my equipment tonight.
    25,000 gallon in ground white plaster- 1 1/2 HP Pentair SuperFlo pump - 60 sqft FNS DE filter (with FiberClear), 1999 Sundance Optima 850 hot tub.
    Manassas Park, VA

  4. Back To Top    #4

    Join Date
    Jul 2012
    Location
    Herndon, VA
    Posts
    419

    Re: This is why you bond your pool and equipment!

    ouch
    8,000 gallon, in ground, fiberglass pool with a cartridge filter.

  5. Back To Top    #5
    Isaac-1's Avatar
    Join Date
    May 2010
    Location
    SW Louisiana
    Posts
    6,711

    Re: This is why you bond your pool and equipment!

    Does anyone know the whole story yet, not just the simplified electricity BAD broadcast version?
    Indoor 20x40 35,000 gallon vinyl pool with 1.5 HP 2 speed Jandy FloPro pump, Hayward EC75 Perflex DE filter, 11 4x12 Techno-Solis solar panels w/ Aquasolar controller, Aquabot Turbo T Robot Cleaner. Also LMI metering chlorine dispenser pump and HotSpring Jetsetter
    I use and endorse TFtestKits TF-100 from http://tftestkits.net
    ~Remember TFP counts on your donations to keep this site ad free~

  6. Back To Top    #6
    Mod Squad JohnT's Avatar
    Join Date
    Apr 2007
    Location
    SW Indiana
    Posts
    9,089

    Re: This is why you bond your pool and equipment!

    Quote Originally Posted by gtnos View Post
    wow. so how do you bond it? its there kit to buy? also, if your pump was plugged into a GFCI outlet, and something shorted out that would cause an issue like electrified water, similar to that in the video, i would think it would trip the GFCI shutting power to pump off, and eliminating this issue. So wouldnt a GFCI outlet be enough?
    Bonding is primarily an issue with inground and metal AG pools. It consists of connecting all of the metal parts of and near the pool and the water itself together electrically.

    A GFCI won't necessarily help because the source of the electricity may be unrelated to the pool or your property. For example, a construction crew using a backhoe that contacts an overhead line could energize the ground and the current might flow through your pool.
    TFP Moderator
    20K Gallon 20X36 Vinyl Inground
    Hayward S244T Sand Filter with 1HP Whisperflo Pump. Liquidator C-201 and Solar Heat

  7. Back To Top    #7

    Join Date
    Jun 2013
    Location
    Newcastle, Oklahoma
    Posts
    508

    Re: This is why you bond your pool and equipment!

    Quote Originally Posted by JohnT View Post
    Bonding is primarily an issue with inground and metal AG pools. It consists of connecting all of the metal parts of and near the pool and the water itself together electrically.

    A GFCI won't necessarily help because the source of the electricity may be unrelated to the pool or your property. For example, a construction crew using a backhoe that contacts an overhead line could energize the ground and the current might flow through your pool.
    ahh, I see. So I need to bond my new partially buried AGP (Doughboy Desert Spring) that is going in tomorrow? I wont have any metal rails, ladder or steps though. Going with plastic wedding cake style steps and rails are resin.
    Partially buried Doughboy Desert Spring 16 x 32, sport pool, with 7 ft deep middle, 20,000 gallons, Hayward Powerflo Matrix 1.5 HP 2 speed pump, 250 lb sandfilter, 2 Doughboy skimmers and 2 returns. 2 cascade fountains.
    Taylor K-2006 kit. Zodiac Barracuda Ranger suction side cleaner.
    TFPC method and is crystal clear every day thanks to TFP!!!

  8. Back To Top    #8
    Mod Squad zea3's Avatar
    Join Date
    Jul 2009
    Location
    Houston, Texas
    Posts
    9,200

    Re: This is why you bond your pool and equipment!

    Yes, you should bond the pool.
    TFP Moderator
    Helpful links: TF Test Kits,TFP Pool School, PoolMath
    Vogue 21' round AG, Pentair 1 hp 2 speed pump, 36 sq ft DE filter, Hayward S180T 150# sand filter, Houston, Texas
    Love TFP? Become a
    TFP Supporter!

  9. Back To Top    #9

    TFP Guide

    AimeeH's Avatar
    Join Date
    Apr 2012
    Location
    Columbia SC
    Posts
    1,837

    Re: This is why you bond your pool and equipment!

    This news report states that having some non conductive material to touch may be helpful. I'm not sure I buy that. The pool needs to be bonded properly. We could feel the electricity when touching the cement and water at the came time.

    http://www.troublefreepool.com/threa...nd-around-pool

    I now know the pool NEEDS to be bonded properly. We are still struggling with this. It isn't code in our county to bond inground vinyl pool but is for gunite, etc.
    18*36*23 true "L" vinyl IG 29,000 gallons. SWG. TF-100 test kit.
    http://tftestkits.net/splash-page.html

  10. Back To Top    #10

    Join Date
    Sep 2007
    Location
    Shoreview, MN
    Posts
    11

    Re: This is why you bond your pool and equipment!

    What I heard was that it is helpful to have non-conductive safetly equipment, such as a hook, to help get someone out of the pool because you don't know what caused the problem in the first place.

    My electrical inspector was much more concerned with what I had done for bonding than he was with the wiring from the breaker panel in the basement. I find it hard to believe bonding isn't part of the NEC (National Electrical Code).
    18'x33' AG, 1.5 hp pump, 120 ft2 cartridge filter, BBB method

  11. Back To Top    #11

    steveg_nh's Avatar
    Join Date
    Oct 2013
    Location
    Southern NH
    Posts
    825

    Re: This is why you bond your pool and equipment!

    They said there were stray electrical wires in the water or something...

    - - - Updated - - -

    Bonding is absolutely part of the NEC.
    24'x40' 25k gal Imperial Mountain Pond IGP, full 28 mil VynAll Ocean Breakers liner. All Hayward system: 140k BTU HeatPro heat pump, 3/4HP single speed TriStar 2" Pump, DE6020 filter, AquaPlus Automation/Salt Chlorination, remote controls, ColorLogic 4.0 lighting. Polaris 280 w/PB4-60 BP. TF100 & K1766 test kits. Rinox Palazzo pavers and Spherik coping. Pool installed 9/2013, project completed 6/16/14.

  12. Back To Top    #12
    gtemkin's Avatar
    Join Date
    Jun 2008
    Location
    Seattle, WA
    Posts
    738

    Re: This is why you bond your pool and equipment!

    Quote Originally Posted by PoolPete View Post
    I find it hard to believe bonding isn't part of the NEC (National Electrical Code).
    It IS a part of the electrical code unless you're working to an antique version. Can you please explain where you got your information.
    21K gal 16' x 40' in-ground pool built 1959, old school with Jacuzzi bronze pump, American Products 24" Sand Filter & Americana Multiport valve, Jandy Lite2 millivolt heater, Coverstar cover, and classic Kreepy Krauly.

  13. Back To Top    #13

    Join Date
    Feb 2012
    Location
    Maryland
    Posts
    400

    Re: This is why you bond your pool and equipment!

    As the story mentioned, the water was electrified with no issues. Only when she touched the metal, she became the path of least resistance and all the current flowed through her. With bond wire, all the current in the water should follow the path of least resistance, that being the copper #8 wire, and should flow out there.

    I would think a situation like this had to be extreme. Like a live wire physically IN the water. Stray voltage in the ground around the pool seems would cause a tingle or jolt but not full paralysis like was shown here. The way the gentlemen had to physically break her from the rail looked like how one would break someone from a live wire.
    DIY 18x36 IG Vinyl Rectangle with 2 foot radius; Steel Walls. 8' steps w/t 2 step jets; 2 MD, 1 Skimmer, 2 returns; Hayward Pro Series 24 Inch 300# Sand Pool ; Hayward color logic 4.0 LED light; 2" PVC pipe 4 Jandy Valves, Hayward PL-P-4, SWCG

  14. Back To Top    #14
    Divin Dave's Avatar
    Join Date
    Oct 2013
    Location
    Longview, Texas
    Posts
    4,926

    Re: This is why you bond your pool and equipment!

    A bond on a pool is required by the National Electric Code. Is a serious safety consideration.

    Bonding consists of running a continuous copper wire all the way around the pool and making a connection between every metal part of the pool and equipment to that wire. SOme places even require the water to be bonded.
    Look up the code for Bonding for specifics.
    If you look at your pump, timer and other metal equipment and you see a bare copper wire connecting them all togehter, then it's bonded.

    Almost every single thing, Person, animal, car, trees, plants carpet etc is energized. We and everything else all have electrically charged particles as part of our makeup.

    If the electrical potential is equal, then we all are in haromony with each other. WHen the potentials become unequal is where the problem comes in. A perfect example of this is rubbing your feet on the carpet and then touching the door knob. When you scoot your feet on the carpet, your electrical potential changes. The electrical discharge or spark when you tough the doorknob, is the result of the electrical potential difference of you and the door knob being equalized.

    The most vivid example of electical potential..... is when the hair on your arms stand up and your skin tingles when a thunderstorm is approaching. Its not the potential of you changing such as in the static electricity example above. Insead you are feeling the effect of the atmospheres potential changing that makes the hair stand up on your arm. When atmosphere potential finally gets to a breaking point, an electrostatic discharge takes place. Its called Lightning.

    That copper wire all around the pool provides an electrical field that maintains the same electrical potential of everything around the pool so that a electrostatic discharge (getting shocked) does not occur.

    And no. This does not mean you can stay in the pool with lightning flashing all around !
    Divin Dave,
    IG Vinyl, 15' x 30', 3 1/2' - 6' deep, Oval, ~15K gal, Intelliclor IC40, Intelliflo VS pump, Clean and Clear 420 Filter, auto-fill-disabled, Retrofit LED Color Light, Dolphin Nautilus Robot, TF100 Test Kit, Taylor K1766 Salt Test Kit, Tftestkit Pressure Gauge.
    www.tftestkits.net Experience- it's what's learned just after you needed it most !!

  15. Back To Top    #15

    Wow! Improper bond...

    http://www.liveleak.com/view?i=22f_1400791833

    I know that a negative was improperly connected but wouldn't a properly bonded pool prevent this?
    15 K gal/gunnite, 600 gal attached SPA, Hayward: ProLogic, ColorLogic LED, Super II pumps, 400k BTU heater, StarClear cartridge filter for, SwimClear cartridge filter . Pentaire: booster

    http://www.troublefreepool.com/detai...l?hilit=corpus

  16. Back To Top    #16


    TFP Guide

    bmoreswim's Avatar
    Join Date
    Jul 2012
    Location
    Central MD
    Posts
    3,294

    Re: Wow! Improper bond...

    Double wow. Nothing to add electrically, but geez, wow.
    18'x38' Rectangle (3'-8 1/2' deep w/ diving board) - 27K gal. w/ gray plaster
    Hayward equipment (cartridge filter, 2-speed pump, SWCG, automation) View Our Build
    Coverstar automatic pool cover | StoneMakers concrete retaining wall and decking
    Spring 2013 Build | Dolphin Active 20 robot cleaner | Support TFP!

  17. Back To Top    #17
    Mod Squad JohnT's Avatar
    Join Date
    Apr 2007
    Location
    SW Indiana
    Posts
    9,089

    Re: Wow! Improper bond...

    Quote Originally Posted by savela View Post
    http://www.liveleak.com/view?i=22f_1400791833

    I know that a negative was improperly connected but wouldn't a properly bonded pool prevent this?
    It should prevent it.
    TFP Moderator
    20K Gallon 20X36 Vinyl Inground
    Hayward S244T Sand Filter with 1HP Whisperflo Pump. Liquidator C-201 and Solar Heat

  18. Back To Top    #18

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: This is why you bond your pool and equipment!

    Quote Originally Posted by PoolPete View Post
    I find it hard to believe bonding isn't part of the NEC (National Electrical Code).
    Article 680 of the NEC if very explicit on pool bonding
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  19. Back To Top    #19

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Wow! Improper bond...

    The comment in the video about the voltage seeking ground in this case was not entirely correct. Electricity, contrary to what we are all taught in school, does not seek ground. It seeks it's source. The earth being a big resistor does not allow for the flow of electricity very well.

    The anomaly you saw in the video was two different electrical potentials trying to equalize. To understand electrical potential, you need to watch this video. https://www.youtube.com/watch?v=SkFH8lLvKZ0 The man sitting on the helicopter and the helicopter itself are in the air at one electrical potential. when they approach the power line, which is at a different potential, there is a clear danger. The probe the man uses is connected to the chassis of the helicopter and when he reaches out with it equalizes the potential differential and the clamp he puts on the wire ensures it stays the same.

    In the pool, when a person reached out to grab the railing, they were acting like the probe. They were completing a path between two different potentials. The amount of current flow was not great enough to kill them but, surly it was enough to cause some discomfort and even slight paralysis.

    The interesting study here is the metal railing in the pool water and connected to the deck. Several years ago this was thought to be a good water bond to the bonding grid. This did not seem to be the case here. I would have liked to test that pool right after this happened. I am going to surmise that there was no potential difference between the water and the railing in the direct vicinity of the railing but, there was voltage gradients throughout the pool.

    Someone mentioned why a GFCI did not trip or if there was even one present. It is entirely possible there was a GFCI present on the circuit (I doubt it though). If you look at the chart I posted below...


    1mA Perception Level
    4-6 mA UL 943 Class A GFCI Trip Level
    10mA Let-Go Threshold
    15mA Muscles “Freeze” in 50% of the Population
    30mA IEC RCD Standards Breathing Difficult, Fibrillation in children
    50 mA - 4 Amps Fibrillation
    4 AMPERES AND OVER Heart Paralysis, Serious Tissue and Organ Burning


    You will see that the UL listed current threshold to trip a GFCI is 4-6 mA. If you are subject to that much current you will feel it. I was shocked one time while plugging in an extension cord. It was enough to cause me to get a little weak in the knees and let go of the cord. When I realized what had happened I figured the GFCI must have tripped after the event. It did not. The current I felt must have been below the trip threshold for the GFCI but it was still enough to startle me.

    Someone also mentioned that the electricity that is sometimes referred to as stray voltage as coming from, say, a construction site or bad underground wire. While these can be sources, one has to realize that voltage potential gradients are around us everywhere. Most gradients are so slight that when you touch something the equalizing difference is so slight that you don't feel it.

    About 5 years ago. I had to fix a bonding issue at a pool. it was an above ground pool and when they were standing on the ground in a certain area of the pool there was a voltage difference measurable between the water and the ground. If you touched the water while standing in your bare feet it would hit you pretty hard. A little harder than a static shock when you touch a door knob (two potentials equalizing) I found that the installer did the 4 connection points wrong and that they were all at one end of the pool. The owners thought that the power line that was running along the back of the property was the culprit. I could not convince them otherwise until an event happened that gave me the opportunity. We had a major power outage. The type which the entire town/county is out. Knowing I had to move fast I went over there and disconnected the bonding grid. I then measured the voltage difference between the water and ground and showed them the reading. It was actually higher than it was before. Knowing that the power line at the rear of the property was the one feeding the neighborhood I was sure there was no power flow at that time. I reconnected the bond and the voltage differential went almost to zero.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  20. Back To Top    #20
    Pysiek's Avatar
    Join Date
    Apr 2012
    Location
    Frankfort , Illinois
    Posts
    419

    Re: This is why you bond your pool and equipment!

    Is it possible that they replace a pump and connect ground or neutral to the same plug that the bonding was connected to? And that is why this happened?
    30'x54" Quest Above Ground Round Pool , About 21,000 Gallons , Hayward Perflex EC50 D.E. Filter System 1.5HP Power-Flo Pump , TF-100 Test Kit , Two Hayward Main Drains on the Bottom , Hayward CL200 In-Line Above-Ground Chlorinator.
    77"x77"x21.5" Hot Tub

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •