    Pool heater testing?

    Hey everyone,

    I purchased a house in the winter and am trying to tackle the pool it came with. I was told by the seller that the heater worked and the next door neighbor told me the people renting the house broke it without the seller knowing. So I don't know if it works or not. I plugged it in to see if it would even turn on and all the electrical seems to be working. Should I just hook it up to the gas line and a temporary hose, fire it up and see what happens? Following the manufactures instructions of course.

    Thank you!

    21'x52 AGP 11200 Gal
    TFPC Method

  2. Back To Top    #2

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Pool heater testing?

    I take it this is the Hayward 100,000 btu heater I saw in your other thread. It will need water flow thru it to work IF the pressure switch is still functional. As far as testing, that is the only way. Fire it up and see what happens. We can go from there then. These are pretty simple heaters as long as the pool chemistry stays normal. When you hook it up, check all of your connections with a soap solution for leaks. Actually in a pinch I have used spray bottle cleaners such as 409. If there is a leak, the bubbles will show.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  3. Back To Top    #3
    andyrob2215's Avatar
    Join Date
    May 2014
    Location
    Portage, Indiana
    Posts
    127

    Re: Pool heater testing?

    Thanks dan again!

    I have a soap solution I will use when I hook it up. After I test it I'll get back to you

    21'x52 AGP 11200 Gal
    TFPC Method

  4. Back To Top    #4
    andyrob2215's Avatar
    Join Date
    May 2014
    Location
    Portage, Indiana
    Posts
    127

    Re: Pool heater testing?

    Do you have any recommendations on how to get water flow through there temporarily or would I just have to hard plumb it all together then test it?

    21'x52 AGP 11200 Gal
    TFPC Method

  5. Back To Top    #5

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Pool heater testing?

    Just use the flex hoses that are there. You might have to get a section or two from the pool store for a temp hookup. I am not a big fan of those hoses either, especially on a heater output but for a test they should be fine. That heater is a fairly simple one as far as how it works, so it should be pretty easy to get running if something was goofed up on it.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  6. Back To Top    #6
    andyrob2215's Avatar
    Join Date
    May 2014
    Location
    Portage, Indiana
    Posts
    127

    Re: Pool heater testing?

    Ok sounds good I'll update when I'm done

    21'x52 AGP 11200 Gal
    TFPC Method

  7. Back To Top    #7
    andyrob2215's Avatar
    Join Date
    May 2014
    Location
    Portage, Indiana
    Posts
    127

    Re: Pool heater testing?

    Well it took longer than expected, but I got everything hooked up and last weekend got the heater put together and fired it up. And it worked! Pretty well actually.

    But... when I went to turn it on today it would not fire. It will turn on, then I think I hear the gas valve open but no flames or heat, then it kicks back off to "idle". It did this last weekend once and I took the cover off, reset the valve as stated on the instructions and it worked after that. I tried that this morning 3 times and no luck. Any suggestions?

    21' X 4' AGP 10400 GAL
    1.5 hp pump
    Sand filter
    no SWG
    TFPC method
    21'x52 AGP 11200 Gal
    TFPC Method

  8. Back To Top    #8

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Pool heater testing?

    The sequence of events for that heater are as follows...

    Call for heat (thermostat on)
    Fan starts and satisfies vacuum switch.
    spark igniter fires (slight buzzing sound)
    Gas valve opens (burners light)

    In order for this to happen, the pressure switch must also be satisfied. There are also two limit switches. These are all in series with the vacuum switch. You will need a volt/OHM meter to verify that each of the switches are working. There is also another chronic problem with certain eras of these units. The solder connections on the power in pins on the board tend to crack and fail. I have repaired several of these over the years.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  9. Back To Top    #9
    andyrob2215's Avatar
    Join Date
    May 2014
    Location
    Portage, Indiana
    Posts
    127

    Re: Pool heater testing?

    Once I turn the thermostat on, the blower turns on. About 10 seconds later, there is a slightly louder noise similar to the blower. It sounds like it "kicks" on but then goes away after a few seconds.

    I will try with the multi meter though. Thank you

    21' X 4' AGP 10400 GAL
    1.5 hp pump
    Sand filter
    no SWG
    TFPC method
    21'x52 AGP 11200 Gal
    TFPC Method

  10. Back To Top    #10

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Pool heater testing?

    Yeah, I would start checking the pressure switch and vacuum switch to ensure they are closing. There are also two limit switches in there but, I doubt they are causing the problem
    Make sure the hose to the vacuum switch is not cracked. Also check both ports where the hose hooks up to. They could be clogged up with debris. Also, make sure the exhaust port is clear.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  11. Back To Top    #11
    andyrob2215's Avatar
    Join Date
    May 2014
    Location
    Portage, Indiana
    Posts
    127

    Re: Pool heater testing?

    Well when I got home, I tried it again and it fired up on the first try.

    I'm happy it's working but worried about the unreliability. What could be the cause of it to do this? Everything seems to be working properly. I checked the lines, etc for debris and spider webs and blew it out with an air hose.

    Any suggestions?

    21' X 4' AGP 10400 GAL
    1.5 hp pump
    Sand filter
    no SWG
    TFPC method
    21'x52 AGP 11200 Gal