    Jandi LXI heater error msg

    Hi Guys, Newby Here. This is my problem. I have a Jandy Model #LXI25N that the access door blow open during a bad wind and rainstorm. the pool pump was on so when I went outside to shut the pump down I noticed the PIB board had shorted out. This was last fall and I have waited until now to repair the damage. when I assessed the damage I also found the PDB board was destroyed also. I ordered both parts and installed them. With my downloaded troubleshooting Guide I checked my voltage all the way to the Black wire (L) on the PDB.... 110 volts. Everything is good but still no fan and (CHECK IGN CONTROL) error is still coming up. I am testing with the pump on and heater request on. I pulled the fan motor and it looks brand new. No visible signs or smell of damage. (Heater is less than 2 years old very clean inside, and little usage)
    Here is what have i have tried so far. As my post indicates...almost everything including voltage to and from transformer, air pressure switch, water pressure switch, high limits ETC, but these are all startup stages that come after FAN START right? I have also pulled the wires going to the igniter and it tested 72.4 ohms. Also I safely discharged the capacitor on the motor and on the ohm meter it spiked up high and slowly went to o how do I bench test the motor? 5 wires are confusing. I do know the system is 220 volts ac

  2. Back To Top    #2

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Jandi LXI heater error msg

    Just looking at the schematic for that unit...If it is wired to 240 then you should have 240 volts at the F1 & F2 terminals on the ignition control board (black wire, blue wire) Next to that there is a 24 volt terminal that comes from the transformer (red wire). Check that from that terminal to the ground wire on the board (yellow wire)

    I also see a note on the sheet about a selector for the 120 to 240 conversion. Verify that that is in the correct orientation. Here is a copy from the manual.....

    Converting the Heater for a 120V Power
    Source
    To convert the LXi heater to 120 Volt, 60 Hz AC requires
    reversal of the voltage selector board on the power
    distribution board. The following procedure should be
    performed before the heater is connected to a power
    source:
    1. Identify the power distribution board on the
    heater. It is located to the right of the ignition
    control on the raceway. See Figure 22.
    2. Cut the plastic wire tie that is holding the voltage
    selector board in place and discard the wire
    tie. Unplug the voltage selector board from the
    receptacle. See Figure 23.
    3. Rotate the voltage selector board 180 and reinsert
    it into the receptacle so that the hole in the board
    is not visible. Be sure that the board is securely
    seated in the receptacle.


    On the ignition control board, look for power from the L1 and L2 terminals. These look to be the output for the motor.

  3. Back To Top    #3
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    Yes, I have voltage to my blower motor plug at the PDB board. just no fan power. I am tying to determine if the motor and or capacitor is bad B4 I buy the new one at $400. Both the PIB and the PDB board have been replaced because they were fried My PDB is set to 240 vac just bas the old one was.

    - - - Updated - - -

    L1 and L2 at the ignition control and the PDB board both are hot at 110 vac also

    - - - Updated - - -

    I have been told the bench test on the motor is a multi step process

    - - - Updated - - -

    With 5 wires on the fan motor I want to be careful

  4. Back To Top    #4

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Jandi LXI heater error msg

    Quote Originally Posted by wedgeiron View Post
    Yes, I have voltage to my blower motor plug at the PDB board. just no fan power. I am tying to determine if the motor and or capacitor is bad B4 I buy the new one at $400. Both the PIB and the PDB board have been replaced because they were fried My PDB is set to 240 vac just bas the old one was.

    - - - Updated - - -

    L1 and L2 at the ignition control and the PDB board both are hot at 110 vac also
    Does each terminal have 120 or do they have 120 when probed across them. The schematics I see do not show the power output for the motor


    Quote Originally Posted by wedgeiron View Post
    - - - Updated - - -

    I have been told the bench test on the motor is a multi step process

    - - - Updated - - -

    With 5 wires on the fan motor I want to be careful
    . From the schematic I see that the leads go back to some sort of junction and then to the motor.

    The problem with testing the motor is that without seeing it and how it is hooked up it is hard to tell what wire(s) are being used. Generaly the white is the neutral and one of the colors is the other leg. The different colors are for different speed configurations. If you have access to the wire connections where the motor plugs in you can test for voltage there to ensure the motor is at least getting power. You may have a motor shop in your area that could check out the motor for you.

  5. Back To Top    #5
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    and I have 26.2 vac at the red wire (both ends) Fuse is good. the motor is already pulled from heater. I have been told that the fan has different speeds as needed during startup.

  6. Back To Top    #6
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    can not find a shop that will test a pool heater fan motor

    - - - Updated - - -

    thanks for the assist

  7. Back To Top    #7

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Jandi LXI heater error msg

    Yes the fan runs two different speeds. I would have used an amp meter to see if the motor, before being removed, was drawing anything.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  8. Back To Top    #8
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    I am getting voltage to the Fan plug....already discharged the Capacitor and did an ohm test on that....it spiked up and slowly went to infinity. so it looks like a new Motor. hard to believe the storm did that much damage.

    - - - Updated - - -

    If the pump had not been on I would not have this much damage because there is no power to heater unless the pump is on.

  9. Back To Top    #9
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    Everything I have checked so far is telling me the IGNITION CONTROL is good (i hope)

  10. Back To Top    #10

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Jandi LXI heater error msg

    Even though items are not turned on and there is a power issue, it can still run thru equipment. If it were a power surge it can take out lots of things unless you have some sort of power surge protection.

    Good luck on the motor and hopefully that is the only thing damaged in the heater.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  11. Back To Top    #11
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    I had another person just now have me unplug F1 and F2 from the IGNITION CONTROL.....jump them together.....turn power back on and the fan came on?? he then told me I had a bad IGNITION CONTROL.....why would I have 110 at Fi AND F2 in the first place and no fan??

    - - - Updated - - -

    this was his TOP SECRET fan BENCH TEST TRICK?

  12. Back To Top    #12

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Jandi LXI heater error msg

    The capacitor is in microfarad. So you need an amp meter to read correctly. If you have power at the F1/F2 and the motor runs when jumped, I might suspect the capacitor. Of course I would just throw one on and see. It is cheaper to get that then a motor.

    BTW, I don't like the Jandy units.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  13. Back To Top    #13
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    Who would sell those?
    I was told by my secret agent to take an OHMS test....BTW, I don't like the Jandy units now either

  14. Back To Top    #14

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Jandi LXI heater error msg

    AC supply places carry the capacitors. Other than that, internet search.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  15. Back To Top    #15

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Jandi LXI heater error msg

    Quote Originally Posted by wedgeiron View Post
    I had another person just now have me unplug F1 and F2 from the IGNITION CONTROL.....jump them together.....turn power back on and the fan came on?? he then told me I had a bad IGNITION CONTROL.....why would I have 110 at Fi AND F2 in the first place and no fan??

    - - - Updated - - -

    this was his TOP SECRET fan BENCH TEST TRICK?
    Just looked at a better schematic for this and see that the F1 and F2 seem to be tied directly to the 15 pin plug at the connection box. It seems like the F1 and F2 are some kind of switching loop for the fan. The drawing does not show which pins are jumpered together on the plug, but I suspect some of them are. This is why you are seeing 120 on those terminals.

    With this, I too suspect you have a bad ign control. What ever relay inside the ign control box controls that is not turning on for some reason. Have you verified continuity thru all safety switches?

  16. Back To Top    #16
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    I downloaded this this PDF (lxi trouble shooting guide) (it will show up as the first search item) on a GOOGLE search and followed the guide on pages 6 & 7 for the LXI and it checked out.....but you know you might have something there. if the motor runs on 240 it would take a relay to send both F1 and F2 110vac to the motor at the same time to make it 220vac.....I wondered at the time when I was troubleshooting the IGNITION CONTROL how the motor was getting the 220vac.....I am going to run the complete check again......thanks....Google that guide and see if you can see your point Thanks
    It is a pretty good guide........http://www.victormfg.com/_build/docs...tingGuides.pdf

  17. Back To Top    #17
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    POST note............when I call for heat I can hear a relay click in the IGNITION CONTROL?? but that does not mean it is working

  18. Back To Top    #18
    wedgeiron's Avatar
    Join Date
    May 2014
    Location
    Las Vegas Nv.
    Posts
    21

    Re: Jandi LXI heater error msg

    The capacitor was completely discharged when I first started testing because of not being used for 6 months....would that prevent fan motor start?

  19. Back To Top    #19

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Jandi LXI heater error msg

    Here is a link to the schematic I was looking at.... http://edc.poolsupplyworld.com/wpdf/...ter-manual.pdf It is on page 7. Not ascolorful as the one you linked to but, shows the 15 pin molded plug that I assume yours has. Have you unplugged it and checked for a broken/missing pin or corrosion in there?

  20. Back To Top    #20

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Jandi LXI heater error msg

    Quote Originally Posted by wedgeiron View Post
    I downloaded this this PDF (lxi trouble shooting guide) (it will show up as the first search item) on a GOOGLE search and followed the guide on pages 6 & 7 for the LXI and it checked out.....but you know you might have something there. if the motor runs on 240 it would take a relay to send both F1 and F2 110vac to the motor at the same time to make it 220vac.....I wondered at the time when I was troubleshooting the IGNITION CONTROL how the motor was getting the 220vac.....I am going to run the complete check again......thanks....Google that guide and see if you can see your point Thanks
    It is a pretty good guide........http://www.victormfg.com/_build/docs...tingGuides.pdf

    It does not look like the motor receives 240. I was just re-reading thru this and noted something. You stated in a previous post... I had another person just now have me unplug F1 and F2 from the IGNITION CONTROL.....jump them together. Are you sure it was the F1 and F2?
    This should have caused a dead short between the two legs of the 240 and tripped a breaker. Was it maybe the L1 and L2 wires?

    Just wondering...what is the power reading on the L1 and L2 terminals when the wires are unhooked