    Jandy AquaPure 1400/Harward EcoStar SP3400VSP

    I recent had my Jandy single speed pump replaced with a EcoStar SP3400VSP.. The installer configure it so the Jandy Aquapure 1400 is always on and scheduled the pump to running for approx 6 hours a day @ various speeds. Is it ok to leave the Aquapure on all the time? My concerns is that it will decrease the life of the SWG.

    Thanks

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Jandy AquaPure 1400/Harward EcoStar SP3400VSP

    Welcome to TFP!

    It is not a lifetime issue, rather it is a safety issue. The SWG should turn it's self off any time there is no water flow. However if the flow sensor were to fail, which does happen, there would be an explosion hazard (the SWG produces explosive hydrogen gas when there is no water flow).

    The solution is to have either an automation system, or a current controlled relay, which turns off the SWG when the pump is not running.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3

    Join Date
    May 2014
    Location
    United States
    Posts
    2

    Re: Jandy AquaPure 1400/Harward EcoStar SP3400VSP

    Quote Originally Posted by JasonLion View Post
    Welcome to TFP!

    It is not a lifetime issue, rather it is a safety issue. The SWG should turn it's self off any time there is no water flow. However if the flow sensor were to fail, which does happen, there would be an explosion hazard (the SWG produces explosive hydrogen gas when there is no water flow).

    The solution is to have either an automation system, or a current controlled relay, which turns off the SWG when the pump is not running.
    Wow that does sound dangerous. What is your recommendation use a timer or current controlled relay? My dial timer is inline with the pump the installer just removed the start and stop pins. I can easy schedule it to turn on SWG and Pump (Need to check the pump manual on how to) or is the current control relay the better way to go.. Any input to product/model relay would help.

    Thanks for the quick response, I'm glad I found this forum..

    Chris

  4. Back To Top    #4
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Jandy AquaPure 1400/Harward EcoStar SP3400VSP

    Setting up a timer is the simplest approach, though you have to keep an eye on the timers and make sure they stay in sync. There are a couple of topics about using current controlled relays, for example here.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School