    Hey guys, I think i already know the answer but why not. I have a 12 x 20 AGP being installed in about a week. Im thinking of getting a heater but my problem is my only available gas line is my BBQ line and its only 1/2". I was looking at the Hayward H-series 150K BTU, Do you think its possible to run it off the 1/2" pipe?

    Another possibly stupid question, is it possible to step up to 3/4" pipe from the BBQ line, Would that accomplish anything.

    Thanks

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Natural Gas Heater Question?

    Welcome to TFP!

    It all depends on the distance and the pressure. At standard pressure, a short run of 1/2" will work, but given typical yard dimensions you probably need something larger. We have 2" for our 60 foot run for a 200,000 BTU heater at standard pressure, but for our 40 foot run to a 300,000 btu generator at 2 psi we have 1/2".
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Natural Gas Heater Question?

    You most likely will need to have a larger line run from the meter. If you have a 1" line in the house (most likely do) then you could come off of that with the 3/4". I managed to get a 100,000 BTU to run on a line that is sized down to 3/8" ID but that is really pushing it. I clocked the meter and it is right at the 100,000 mark. What does the manual tell you to use? Stepping up from 1/2" to 3/4" won't do you any good as the flow will be controlled by the 1/2" line

  4. Back To Top    #4

    Join Date
    Feb 2014
    Location
    Staten Island, NY
    Posts
    4

    Re: Natural Gas Heater Question?

    Thanks for the replies. I figured it was too small. I'll most likely be going the solar heater route.
    Thanks guys

  5. Back To Top    #5
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Natural Gas Heater Question?

    Welcome to TFP!!!

    Please add your pool details to your signature and location to your profile as described HERE as it will help us help you.

    The solar heating possibilities between Alaska and Arizona are a little different ... being a little more specific than "United States" would help.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  6. Back To Top    #6

    Join Date
    Feb 2014
    Location
    Staten Island, NY
    Posts
    4

    Re: Natural Gas Heater Question?

    Sorry I updated the info ( I Think ) I was also looking at the Raypak 106K since its smaller and it has a 1/2" Gas Inlet on it already. Running a new line from the meter is not an option the way my house is situated.
    12' x 20' AGP Sunk 2 Feet Down
    Hayward EC-40 DE Filter
    1HP Hayward Matrix Pump
    Hard Plumbed

  7. Back To Top    #7
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Natural Gas Heater Question?

    Your BBQ supply does not sound like it was designed to handle that many more BTUs. You would need to know the pipe sizes and lengths all the way from the meter to be able to calculate if you have excess capacity available, but I doubt it.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  8. Back To Top    #8

    Join Date
    Feb 2014
    Location
    Staten Island, NY
    Posts
    4

    Re: Natural Gas Heater Question?

    The pipe runs are 3/4" from the meter to my kitchen stove which is probably like 20-25'. My BBQ line is tapped off that line in 1/2" pipe underground to my BBQ which is about another 35' from the stove. Then it would be about another 40' straight run to my Pool.
    12' x 20' AGP Sunk 2 Feet Down
    Hayward EC-40 DE Filter
    1HP Hayward Matrix Pump
    Hard Plumbed

  9. Back To Top    #9
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Natural Gas Heater Question?

    You would also need to know the BTU rating of your stove and BBQ. Pipes are generally sized assuming everything is running.

    I can not recall all the details how to do this sizing off the top of my head, but looking at a table your first 20' run of 3/4" pipe is only rated to ~192,000 BTUs .... likely your stove and BBQ are already exceeding that.

    A 60' run from the meter to the BBQ assuming all 1/2" is only rated to about 50,000 BTUs and your BBQ alone has is likely well above that.

    EDIT: This is a very conservative method of sizing.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  10. Back To Top    #10

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,434

    Re: Natural Gas Heater Question?

    The line won't support the heater.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  11. Back To Top    #11
    Pops37's Avatar
    Join Date
    May 2013
    Location
    North central TX (Tarrant County)
    Posts
    108

    Re: Natural Gas Heater Question?

    Howdy, here is a link to some nat gas calculations and pipe info. Good luck.... http://www.engineeringtoolbox.com/na...or-d_1042.html
    Gunite/plaster pool w/spa built 1983, 17,000 gal. (depth 3' x 6' x 3') (37' X 16' +spa, stairs & large in-pool bench seat). Arneson (now Hayward) pool vac (rebuilt 3 or 4 times over 30 years), 350k BTU (nat gas) XE heater (in need of a serious herbal cleansing lol), 2HP Marathon pump & filter basket, DE filter NSS-48, air pump for spa bubbles, one skimmer plus in-line filter Hayward CANISTER W560 to the pool vac. Re-plastered May 2013 reinforced quartz (Marbletite) Diamond Bright. Test kit: Taylor K-2006; Bleach